    Laplace,<br>
      I am not sure that TRNSYS is the correct tool to use in this case
    and I might steer you towards something like EES (Engineering
    Equation Solver) instead. The heat exchanger components in TRNSYS
    that might be the basis for your evaporator and condenser are quasi
    steady state models meaning that they do not account for the thermal
    capacitance of the heat exchanger material or the fluid. They also
    ignore short term transient behaviors that may be important to your
    modeling. Lastly, they assume that the working fluid does not change
    phase. I think you would probably have to write models for all the
    various parts of the chiller. If there is an advantage to writing
    such models then of course you can do so but be careful in
    connecting components that have been designed to model very short
    term transients with components that have been designed for use with
    longer time steps.<br>
    <br>
      EES is a more pure equation solver than TRNSYS, especially in that
    it can solve simultaneous equations. It is not too challenging to
    write the equations that govern the refrigeration process and EES
    has got a number of built-in functions that will return the
    thermodynamic properties of a lot of refrigerants.<br>
    Best,<br>
     David<br>
    <br>
    <br>
    <div class="moz-cite-prefix">On 8/25/2013 13:06, Laplace Bessel
      wrote:<br>
    </div>
    <blockquote
      cite="mid:1377453989.66143.YahooMailNeo@web141504.mail.bf1.yahoo.com"
      type="cite">
      <div style="color:#000; background-color:#fff; font-family:times
        new roman, new york, times, serif;font-size:12pt">Hello trnsys
        users,<br>
        Does anyone know how to model a chiller as its components i.e.
        evaporator, condenser, compressor in Trnsys? Any pointers would
        be very appreciated.<br>
        <br>
        Laplace<br>
        <div><br>
        </div>
      </div>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <br>
      <pre wrap="">_______________________________________________
TRNSYS-users mailing list
<a class="moz-txt-link-abbreviated" href="mailto:TRNSYS-users@cae.wisc.edu">TRNSYS-users@cae.wisc.edu</a>
<a class="moz-txt-link-freetext" href="https://mailman.cae.wisc.edu/listinfo/trnsys-users">https://mailman.cae.wisc.edu/listinfo/trnsys-users</a>
</pre>
    </blockquote>
    <br>
    <pre class="moz-signature" cols="72">-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI  53703 USA
P:+1.608.274.2577
F:+1.608.278.1475
<a class="moz-txt-link-abbreviated" href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.tess-inc.com">http://www.tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.trnsys.com">http://www.trnsys.com</a></pre>
  </body>
</html>