    Tobias,<br>
      The maximum heating rate is a parameter in Type60. Parameters, by
    definition, are read once at the beginning of the simulation and
    then are not updated. They are time independent. If you need a tank
    model in which the input heating rate is variable, I would recommend
    using Type534 in the TESS Storage Tank library.<br>
    <br>
      The Type20 data files are described (although not very completely)
    in the 05-MathematicalReference manual. I assume that you are using
    Trnsys16; please be aware that Type20 was removed from Trnsys17
    because it models a very specific (rather unusual) kind of heat pump
    that can use either water or air on its source side, because it can
    only operate in heating mode, and because it has some built-in
    control algorithms that cannot be modified. A preferable heat pump
    model may be found in the TESS HVAC library.<br>
    Best,<br>
     David<br>
    <br>
    <br>
    <div class="moz-cite-prefix">On 6/17/2013 03:53, Tobias Tag wrote:<br>
    </div>
    <blockquote
cite="mid:CADACZCJzczk1jdG=H+cHuDEiHTrxYYYNTKtkZJmqccqOrJUkgw@mail.gmail.com"
      type="cite">
      <div dir="ltr">Dear TRNSYS-User,<br>
        <br>
        i have two problems with TRNSYS 17.<br>
        <br>
        1. I´m trying to make the maximum heating rate of an element (of
        Type 60c)  depending on the power produced by PV in three steps.
        Shold look like that:<br>
        <br>
         <br>
            If 1.5kW < PV-Power < 3kW  then heating rate = 1.5 kW<br>
        <br>
            else if 3kW < PV-Power < 4.5kW then heating rate = 3kW<br>
            <br>
            else if PV-Power > 4.5kW then heating rate = 4.5kW <br>
        <br>
        <br>
        I´ve set the heating rate as a String variable which shold get
        the value from a equation. but i don´t know how to update the
        equation in every time step of the simulation.<br>
        <br>
        2. Does anybody know what the external files of type 20 (dual
        source heat pump) are? Unfortunatly ther is no example in the
        TRNSYS-Examples folder.<br>
        <br>
        <br>
        Kind regards<br>
        <br>
        Tobias <br>
      </div>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <br>
      <pre wrap="">_______________________________________________
TRNSYS-users mailing list
<a class="moz-txt-link-abbreviated" href="mailto:TRNSYS-users@cae.wisc.edu">TRNSYS-users@cae.wisc.edu</a>
<a class="moz-txt-link-freetext" href="https://mailman.cae.wisc.edu/listinfo/trnsys-users">https://mailman.cae.wisc.edu/listinfo/trnsys-users</a>
</pre>
    </blockquote>
    <br>
    <pre class="moz-signature" cols="72">-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI  53703 USA

P:+1.608.274.2577
F:+1.608.278.1475
<a class="moz-txt-link-abbreviated" href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>

<a class="moz-txt-link-freetext" href="http://www.tess-inc.com">http://www.tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.trnsys.com">http://www.trnsys.com</a></pre>
  </body>
</html>