    Nipaporn,<br>
      If you want a heating controller (ie a controller that turns
    equipment on when the room temperature falls below 26.5C and allows
    it to stay on until room temperature reaches 27.5C) then set the
    first input to the middle of your set point temperature range (27C).
    The second input will be the temperature that you are monitoring
    (the room temperature). The fifth input (upper dead band) would be
    set to 0.5C and the sixth input (lower dead band) would be set to
    -0.5C.<br>
    <br>
      If you want a cooling controller (ie a controller that turns
    equipment on when the room temperature rises above 27.5C and allows
    it to stay on until room temperature falls to 26.5C) then set the <i>second</i>
    input to the middle of your set point temperature range (27C). The <i>first
    </i>input will be the temperature that you are monitoring (the room
    temperature). The fifth input (upper dead band) would be set to 0.5C
    and the sixth input (lower dead band) would be set to -0.5C.<br>
    <br>
    Kind regards,<br>
     David<br>
    <br>
    <br>
    <div class="moz-cite-prefix">On 5/14/2013 23:22, Nipaporn Nutprasert
      wrote:<br>
    </div>
    <blockquote cite="mid:COL126-W13B8D75562E112ECE8029F85A20@phx.gbl"
      type="cite">
      <style><!--
.hmmessage P
{
margin:0px;
padding:0px
}
body.hmmessage
{
font-size: 12pt;
font-family:Calibri
}
--></style>
      <div dir="ltr">Hi TRNSYS users, <br>
        I need some help about differential controller(Type2b). I would
        like to control temperature in the room within 26.5-27.5oC. How
        can I define the upper/lower deadbands (Upper input temperature
        Th, Lower input temperatureTl, Monitoring temperature Tin, Upper
        dead band dT, Lower dead band dT)to monitor the room temperature
        to gain simple ON/OFF control.<br>
         <br>
        Thank you in advance.<br>
        Nipaporn<br>
      </div>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <br>
      <pre wrap="">_______________________________________________
TRNSYS-users mailing list
<a class="moz-txt-link-abbreviated" href="mailto:TRNSYS-users@cae.wisc.edu">TRNSYS-users@cae.wisc.edu</a>
<a class="moz-txt-link-freetext" href="https://mailman.cae.wisc.edu/listinfo/trnsys-users">https://mailman.cae.wisc.edu/listinfo/trnsys-users</a>
</pre>
    </blockquote>
    <br>
    <pre class="moz-signature" cols="72">-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI  53703 USA

P:+1.608.274.2577
F:+1.608.278.1475
<a class="moz-txt-link-abbreviated" href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>

<a class="moz-txt-link-freetext" href="http://www.tess-inc.com">http://www.tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.trnsys.com">http://www.trnsys.com</a></pre>
  </body>
</html>