<html>
  <head>
    <meta content="text/html; charset=ISO-8859-1"
      http-equiv="Content-Type">
  </head>
  <body text="#000000" bgcolor="#FFFFFF">
    Youcef,<br>
      Normally, an electric grid is treated as an infinite source/sink
    of power because the amount of power that is contributed by the PV
    is negligible in comparison to the power of the grid. In small scale
    applications, I would recommend that you use Type188 (AC bus bar).
    The component is a very simple energy balance of power sources and
    power loads and it assumes that the devices on the grid are all
    voltage regulated. The actual voltage and frequency of the grid
    doesn't really matter in this case because the size of the TRNSYS
    time step is very large in comparison to the time constant of the
    grid. TRNSYS time steps are on the order of 1 to 5 minutes so the AC
    grid just looks like a steady state process.<br>
    Regards,<br>
     David<br>
    <br>
    <br>
    <br>
    <div class="moz-cite-prefix">On 5/5/2013 07:10, youcef benmoulai
      wrote:<br>
    </div>
    <blockquote
cite="mid:CAA3jsrbFvbNmdJEZqSg-k4qiffdZJ3N2sA8_chQF1V48hBqkaA@mail.gmail.com"
      type="cite">
      <div dir="ltr">
        <div>
          <div>BONJOUR A TOUS<br>
          </div>
          j ai besoin de produit 220v et 50hz a mon reseaux electrique
          ....quel composant il faut utiliser???<br>
          <br>
        </div>
        merci <br clear="all">
        <div>
          <div>
            <div><br>
              -- <br>
              Benmoulai Youcef
            </div>
          </div>
        </div>
      </div>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <br>
      <pre wrap="">_______________________________________________
TRNSYS-users mailing list
<a class="moz-txt-link-abbreviated" href="mailto:TRNSYS-users@cae.wisc.edu">TRNSYS-users@cae.wisc.edu</a>
<a class="moz-txt-link-freetext" href="https://mailman.cae.wisc.edu/listinfo/trnsys-users">https://mailman.cae.wisc.edu/listinfo/trnsys-users</a>
</pre>
    </blockquote>
    <br>
    <pre class="moz-signature" cols="72">-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI  53703 USA

P:+1.608.274.2577
F:+1.608.278.1475
<a class="moz-txt-link-abbreviated" href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>

<a class="moz-txt-link-freetext" href="http://www.tess-inc.com">http://www.tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.trnsys.com">http://www.trnsys.com</a></pre>
  </body>
</html>