    Tom,<br>
      Good job decreasing the time step and making sure that the zone
    capacitance was reasonable! <br>
     <br>
      Almost all of the controller components in TRNSYS (and in fact
    controllers in real life) have a deadband around the setpoint. In
    cooling mode, if the set point is 21C, the cooling system might not
    start until the temperature reached 21.5C and then it would continue
    to operate until the zone temperature got down to 20.5C (or
    something like that). Controllers (again both in TRNSYS and in the
    real world) also often implement some form of a limit on the number
    of oscillations that they may go through in a period of time.
    Unfortunately, it is not possible to implement either a limit on
    controller state changes or a thermostat dead band using equations.
    You may be able to implement a dead band in Excel but it won't be
    easy. There is an outside air reset controller (which basically does
    the same as your adaptive temperature control) in the TESS Controls
    Library (Type1250). If you do not have that component then I would
    recommend that you use a Type2 (the instance in the Studio that is
    labeled Aquastat: Cooling Mode: Type2-AquastatC) within your
    equation to provide yourself with a dead band and a limit on
    state-changes.  <br>
    <br>
    <div class="moz-cite-prefix">On 5/6/2013 05:40, Tom B wrote:<br>
    </div>
    <blockquote cite="mid:DUB119-W328279BB506625458E5448A2B90@phx.gbl"
      type="cite">
      <style><!--
.hmmessage P
{
margin:0px;
padding:0px
}
body.hmmessage
{
font-size: 12pt;
font-family:Calibri
}
--></style>
      <div dir="ltr">Dear Marcello,<br>
         <br>
        you're absolutely right about this, the formula was
        unnecessarily complicated. I deleted this variable and the
        number of convergence errors decreased indeed, but unfortunately
        did not go away completely. <br>
         <br>
        I also tried looking at it from a different point of view.
        According to the list file, the convergence errors occur between
        Type 56 and type 62 (calling Excel) which are part of the loop.
        Type 62 components outside the loop do not give any problems. Is
        there something that makes Type 62 inadequate for loops? And if
        so, could I adjust some value or component order to make sure
        that I can use Type 62 in a loop?<br>
         <br>
        Kind regards,<br>
         <br>
        Tom<br>
         <br>
        <div>
          <hr id="stopSpelling">From:
          <a class="moz-txt-link-abbreviated" href="mailto:marcello.caciolo@cofelyaxima-gdfsuez.com">marcello.caciolo@cofelyaxima-gdfsuez.com</a><br>
          To: <a class="moz-txt-link-abbreviated" href="mailto:trnsys-users@cae.wisc.edu">trnsys-users@cae.wisc.edu</a><br>
          Date: Mon, 6 May 2013 12:03:57 +0200<br>
          Subject: Re: [TRNSYS-users] Convergence errors with adaptive
          temperature limits<br>
          <br>
          <style><!--
.ExternalClass .ecxshape {
}
--></style>
          <style><!--
.ExternalClass p.ecxMsoNormal, .ExternalClass li.ecxMsoNormal, .ExternalClass div.ecxMsoNormal {
font-size:12.0pt;
font-family:"Times New Roman","serif";
}

.ExternalClass a:link, .ExternalClass span.ecxMsoHyperlink {
color:blue;
text-decoration:underline;
}

.ExternalClass span.ecxMsoHyperlinkFollowed {
color:purple;
text-decoration:underline;
}

.ExternalClass p {
font-size:12.0pt;
font-family:"Times New Roman","serif";
}

.ExternalClass p.ecxMsoAcetate, .ExternalClass li.ecxMsoAcetate, .ExternalClass div.ecxMsoAcetate {
font-size:8.0pt;
font-family:"Tahoma","sans-serif";
}

.ExternalClass p.ecxmsonormal, .ExternalClass li.ecxmsonormal, .ExternalClass div.ecxmsonormal {
font-size:12.0pt;
font-family:"Times New Roman","serif";
}

.ExternalClass p.ecxmsoacetate, .ExternalClass li.ecxmsoacetate, .ExternalClass div.ecxmsoacetate {
font-size:12.0pt;
font-family:"Times New Roman","serif";
}

.ExternalClass p.ecxmsochpdefault, .ExternalClass li.ecxmsochpdefault, .ExternalClass div.ecxmsochpdefault {
font-size:12.0pt;
font-family:"Times New Roman","serif";
}

.ExternalClass span.ecxmsohyperlink {
}

.ExternalClass span.ecxmsohyperlinkfollowed {
}

.ExternalClass span.ecxemailstyle19 {
}

.ExternalClass span.ecxtextedebullescar {
}

.ExternalClass p.ecxmsonormal1, .ExternalClass li.ecxmsonormal1, .ExternalClass div.ecxmsonormal1 {
font-size:12.0pt;
font-family:"Times New Roman","serif";
}

.ExternalClass span.ecxmsohyperlink1 {
color:blue;
text-decoration:underline;
}

.ExternalClass span.ecxmsohyperlinkfollowed1 {
color:purple;
text-decoration:underline;
}

.ExternalClass p.ecxmsoacetate1, .ExternalClass li.ecxmsoacetate1, .ExternalClass div.ecxmsoacetate1 {
font-size:8.0pt;
font-family:"Tahoma","sans-serif";
}

.ExternalClass span.ecxemailstyle191 {
font-family:"Calibri","sans-serif";
color:#1F497D;
}

.ExternalClass span.ecxtextedebullescar1 {
font-family:"Tahoma","sans-serif";
}

.ExternalClass p.ecxmsochpdefault1, .ExternalClass li.ecxmsochpdefault1, .ExternalClass div.ecxmsochpdefault1 {
font-size:10.0pt;
font-family:"Times New Roman","serif";
}

.ExternalClass span.ecxTextedebullesCar {
font-family:"Tahoma","sans-serif";
}

.ExternalClass span.ecxEmailStyle35 {
font-family:"Calibri","sans-serif";
color:#1F497D;
}

.ExternalClass .ecxMsoChpDefault {
font-size:10.0pt;
}

.ExternalClass div.ecxWordSection1 {
}

--></style>
          <div class="ecxWordSection1">
            <p class="ecxMsoNormal"><span style="color: rgb(31, 73,
                125); font-family:
                "Calibri","sans-serif"; font-size:
                11pt;">Dear Tom, </span></p>
            <p class="ecxMsoNormal"><span style="color: rgb(31, 73,
                125); font-family:
                "Calibri","sans-serif"; font-size:
                11pt;"> </span></p>
            <p class="ecxMsoNormal"><span style="color: rgb(31, 73,
                125); font-family:
                "Calibri","sans-serif"; font-size:
                11pt;" lang="EN-US">Actually you are right, I
                misunderstood your question and gave you the same
                equation you used.</span></p>
            <p class="ecxMsoNormal"><span style="color: rgb(31, 73,
                125); font-family:
                "Calibri","sans-serif"; font-size:
                11pt;" lang="EN-US"> </span></p>
            <p class="ecxMsoNormal"><span style="color: rgb(31, 73,
                125); font-family:
                "Calibri","sans-serif"; font-size:
                11pt;" lang="EN-US">As a second guess, I would say that
                your problem is in the definition of the variable
                “cooling need”. If I well understand, you compute
                cooling need by using the actual temperature calculated
                by type 56 and comparing it to your target temperature.
                This could be the reason of the bad behavior of your
                simulation and it is not necessary. Indeed, if your
                actual temperature is lower (in the case of cooling) of
                the target temperature, cooling need is zero anyway.</span></p>
            <p class="ecxMsoNormal"><span style="color: rgb(31, 73,
                125); font-family:
                "Calibri","sans-serif"; font-size:
                11pt;" lang="EN-US"> </span></p>
            <p class="ecxMsoNormal"><span style="color: rgb(31, 73,
                125); font-family:
                "Calibri","sans-serif"; font-size:
                11pt;" lang="EN-US">Try to remove this variable and
                rerun the simulation.</span></p>
            <p class="ecxMsoNormal"><span style="color: rgb(31, 73,
                125); font-family:
                "Calibri","sans-serif"; font-size:
                11pt;" lang="EN-US"> </span></p>
            <p class="ecxMsoNormal"><span style="color: rgb(31, 73,
                125); font-family:
                "Calibri","sans-serif"; font-size:
                11pt;" lang="EN-US">Hope this helps.</span></p>
            <p class="ecxMsoNormal"><span style="color: rgb(31, 73,
                125); font-family:
                "Calibri","sans-serif"; font-size:
                11pt;" lang="EN-US"> </span></p>
            <p class="ecxMsoNormal"><span style="color: rgb(31, 73,
                125); font-family:
                "Calibri","sans-serif"; font-size:
                11pt;" lang="EN-US">Best regards,</span><span
                style="color: rgb(31, 73, 125); font-family:
                "Calibri","sans-serif"; font-size:
                11pt;"></span></p>
            <p class="ecxMsoNormal"><b><span style="color: rgb(88, 89,
                  91); font-family:
                  "Tahoma","sans-serif"; font-size:
                  11pt;">Marcello Caciolo</span></b><span style="color:
                rgb(88, 89, 91); font-family:
                "Tahoma","sans-serif"; font-size:
                11pt;"><br>
              </span><span style="color: rgb(88, 89, 91); font-family:
                "Tahoma","sans-serif"; font-size:
                9pt;">Responsable Outils et Méthodes d'Analyse
                Energétique</span><span style="color: rgb(88, 89, 91);
                font-family: "Tahoma","sans-serif";
                font-size: 11pt;"></span></p>
            <p class="ecxMsoNormal"><span style="color: gray;
                font-family: "Arial","sans-serif";
                font-size: 10pt;"><img id="ecxImage_x0020_1"
                  alt="cid:image003.jpg@01CD4E08.954D04D0"
                  src="cid:part1.00050503.08090007@tess-inc.com"
                  width="170" height="62"><br>
                <b><br>
                </b>Cellule Efficacité Energétique et Environnementale -
                Pôle Projets et Réalisations<br>
                46 Boulevard de la Prairie au Duc<br>
                BP 40119 - 44201 Nantes Cedex 02</span><span
                style="color: rgb(31, 73, 125); font-family:
                "Tahoma","sans-serif"; font-size:
                9pt;"><br>
              </span><span style="color: gray; font-family:
                "Arial","sans-serif"; font-size:
                10pt;">Tél.: +33 02 40 41 06 57</span><span
                style="color: rgb(31, 73, 125); font-family:
                "Tahoma","sans-serif"; font-size:
                9pt;"><br>
                <a moz-do-not-send="true"
                  href="mailto:prenom.nom@aximaseitha-gdfsuez.com"><span
                    style="color: blue;">marcello.caciolo@cofelyaxima-gdfsuez.com</span></a></span><span
                style="color: gray; font-family:
                "Arial","sans-serif"; font-size:
                10pt;"></span></p>
            <p class="ecxMsoNormal"><span style="color: rgb(51, 153,
                102); font-family: Webdings; font-size: 11pt;">P</span><span
                style="color: rgb(51, 153, 102); font-family: Webdings;
                font-size: 10pt;"> </span><b><span style="color:
                  rgb(51, 153, 102); font-family:
                  "Arial","sans-serif"; font-size:
                  7.5pt;">Pensez à l'environnement avant d'imprimer ce
                  message</span></b><span style="color: rgb(31, 73,
                125); font-family:
                "Calibri","sans-serif"; font-size:
                11pt;"></span></p>
            <p class="ecxMsoNormal"><span style="color: rgb(31, 73,
                125); font-family:
                "Calibri","sans-serif"; font-size:
                11pt;"> </span></p>
            <p class="ecxMsoNormal"><span style="color: rgb(31, 73,
                125); font-family:
                "Calibri","sans-serif"; font-size:
                11pt;"> </span></p>
            <p class="ecxMsoNormal"><span style="color: rgb(31, 73,
                125); font-family:
                "Calibri","sans-serif"; font-size:
                11pt;"> </span></p>
            <div>
              <div style="border-width: 1pt medium medium; border-style:
                solid none none; border-color: rgb(181, 196, 223)
                currentColor currentColor; padding: 3pt 0cm 0cm;">
                <p class="ecxMsoNormal"><b><span style="font-family:
                      "Tahoma","sans-serif";
                      font-size: 10pt;">De :</span></b><span
                    style="font-family:
                    "Tahoma","sans-serif";
                    font-size: 10pt;"> <a class="moz-txt-link-abbreviated" href="mailto:trnsys-users-bounces@cae.wisc.edu">trnsys-users-bounces@cae.wisc.edu</a>
                    [<a class="moz-txt-link-freetext" href="mailto:trnsys-users-bounces@cae.wisc.edu">mailto:trnsys-users-bounces@cae.wisc.edu</a>] <b>De la
                      part de</b> Tom B<br>
                    <b>Envoyé :</b> lundi 6 mai 2013 11:53<br>
                    <b>À :</b> TRNSYS users mailing list at the Solar
                    Energy Lab, UW-Madison<br>
                    <b>Objet :</b> Re: [TRNSYS-users] Convergence errors
                    with adaptive temperature limits</span></p>
              </div>
            </div>
            <p class="ecxMsoNormal"> </p>
            <div>
              <p class="ecxMsoNormal"><span style="font-family:
                  "Calibri","sans-serif";">Dear
                  Marcello,<br>
                   <br>
                  First of all, thank you very much for your response,
                  it is much appreciated. I tried your formula as well,
                  but I'm afraid this is not the problem, because it
                  still gives the same errors. This may be because the
                  formula is in fact the same, just written down
                  differently (because the part between brackets is
                  reversed, the plus turns into a minus). I hope you or
                  someone else may have another suggestion.<br>
                   <br>
                  Kind regards,<br>
                   <br>
                  Tom<br>
                   </span></p>
              <div>
                <div style="text-align: center;" class="ecxMsoNormal"
                  align="center"><span style="font-family:
                    "Calibri","sans-serif";">
                    <hr id="ecxstopSpelling" size="2" width="100%"
                      align="center"></span></div>
                <p class="ecxMsoNormal"><span style="font-family:
                    "Calibri","sans-serif";">From: <a
                      moz-do-not-send="true"
                      href="mailto:marcello.caciolo@cofelyaxima-gdfsuez.com">marcello.caciolo@cofelyaxima-gdfsuez.com</a><br>
                    To: <a moz-do-not-send="true"
                      href="mailto:trnsys-users@cae.wisc.edu">trnsys-users@cae.wisc.edu</a><br>
                    Date: Mon, 6 May 2013 10:50:59 +0200<br>
                    Subject: Re: [TRNSYS-users] Convergence errors with
                    adaptive temperature limits</span></p>
                <div>
                  <p class="ecxMsoNormal"><span style="color: rgb(31,
                      73, 125); font-family:
                      "Calibri","sans-serif";
                      font-size: 11pt;" lang="EN-US">Dear Tom,</span><span
                      style="font-family:
                      "Calibri","sans-serif";"></span></p>
                  <p class="ecxMsoNormal"><span style="color: rgb(31,
                      73, 125); font-family:
                      "Calibri","sans-serif";
                      font-size: 11pt;" lang="EN-US"> </span><span
                      style="font-family:
                      "Calibri","sans-serif";"></span></p>
                  <p class="ecxMsoNormal"><span style="color: rgb(31,
                      73, 125); font-family:
                      "Calibri","sans-serif";
                      font-size: 11pt;" lang="EN-US">I think that your
                      problem is in the definition of the cooling
                      temperature. It should read : </span><span
                      style="font-family:
                      "Calibri","sans-serif";"></span></p>
                  <p class="ecxMsoNormal"><span style="color: rgb(31,
                      73, 125); font-family:
                      "Calibri","sans-serif";
                      font-size: 11pt;" lang="EN-US"> </span><span
                      style="font-family:
                      "Calibri","sans-serif";"></span></p>
                  <p class="ecxMsoNormal"><span style="font-family:
                      "Calibri","sans-serif";"
                      lang="EN-US">T_Cool_On = 30 -
                      Cooling_need*Cooling_schedule*(30 -
                      Target_temperature)</span><span
                      style="font-family:
                      "Calibri","sans-serif";"></span></p>
                  <p class="ecxMsoNormal"><span style="font-family:
                      "Calibri","sans-serif";"
                      lang="EN-US"> </span><span style="font-family:
                      "Calibri","sans-serif";"></span></p>
                  <p class="ecxMsoNormal"><span style="font-family:
                      "Calibri","sans-serif";"
                      lang="EN-US">In this way, cooling temperature is
                      30 when cooling need and/or cooling schedule are
                      zero, and your target temperature when both
                      cooling need and cooling schedule are 1.</span><span
                      style="font-family:
                      "Calibri","sans-serif";"></span></p>
                  <p class="ecxMsoNormal"><span style="font-family:
                      "Calibri","sans-serif";"
                      lang="EN-US"> </span><span style="font-family:
                      "Calibri","sans-serif";"></span></p>
                  <p class="ecxMsoNormal"><span style="font-family:
                      "Calibri","sans-serif";"
                      lang="EN-US">Hope this helps.</span><span
                      style="font-family:
                      "Calibri","sans-serif";"></span></p>
                  <p class="ecxMsoNormal"><span style="font-family:
                      "Calibri","sans-serif";"
                      lang="EN-US"> </span><span style="font-family:
                      "Calibri","sans-serif";"></span></p>
                  <p class="ecxMsoNormal"><span style="font-family:
                      "Calibri","sans-serif";"
                      lang="EN-US">Best regards,</span><span
                      style="font-family:
                      "Calibri","sans-serif";"></span></p>
                  <p class="ecxMsoNormal"><b><span style="color: rgb(88,
                        89, 91); font-family:
                        "Tahoma","sans-serif";
                        font-size: 11pt;">Marcello Caciolo</span></b><span
                      style="color: rgb(88, 89, 91); font-family:
                      "Tahoma","sans-serif";
                      font-size: 11pt;"><br>
                    </span><span style="color: rgb(88, 89, 91);
                      font-family:
                      "Tahoma","sans-serif";
                      font-size: 9pt;">Responsable Outils et Méthodes
                      d'Analyse Energétique</span><span
                      style="font-family:
                      "Calibri","sans-serif";"></span></p>
                  <p class="ecxMsoNormal"><span style="color: gray;
                      font-family:
                      "Arial","sans-serif";
                      font-size: 10pt;"><img moz-do-not-send="true"
                        id="ecxImage_x0020_1"
                        alt="cid:image003.jpg@01CD4E08.954D04D0"
                        src="http://image001.jpg@01CE4A51.6BE59EE0"
                        width="170" height="62" border="0"><br>
                      <b><br>
                      </b>Cellule Efficacité Energétique et
                      Environnementale - Pôle Projets et Réalisations<br>
                      46 Boulevard de la Prairie au Duc<br>
                      BP 40119 - 44201 Nantes Cedex 02</span><span
                      style="color: rgb(31, 73, 125); font-family:
                      "Tahoma","sans-serif";
                      font-size: 9pt;"><br>
                    </span><span style="color: gray; font-family:
                      "Arial","sans-serif";
                      font-size: 10pt;">Tél.: +33 02 40 41 06 57</span><span
                      style="color: rgb(31, 73, 125); font-family:
                      "Tahoma","sans-serif";
                      font-size: 9pt;"><br>
                      <a moz-do-not-send="true"
                        href="mailto:prenom.nom@aximaseitha-gdfsuez.com">marcello.caciolo@cofelyaxima-gdfsuez.com</a></span><span
                      style="font-family:
                      "Calibri","sans-serif";"></span></p>
                  <p class="ecxMsoNormal"><span style="color: rgb(51,
                      153, 102); font-family: Webdings; font-size:
                      11pt;">P</span><span style="color: rgb(51, 153,
                      102); font-family: Webdings; font-size: 10pt;"> </span><b><span
                        style="color: rgb(51, 153, 102); font-family:
                        "Arial","sans-serif";
                        font-size: 7.5pt;">Pensez à l'environnement
                        avant d'imprimer ce message</span></b><span
                      style="font-family:
                      "Calibri","sans-serif";"></span></p>
                  <p class="ecxMsoNormal"><span style="color: rgb(31,
                      73, 125); font-family:
                      "Calibri","sans-serif";
                      font-size: 11pt;"> </span><span
                      style="font-family:
                      "Calibri","sans-serif";"></span></p>
                  <p class="ecxMsoNormal"><span style="color: rgb(31,
                      73, 125); font-family:
                      "Calibri","sans-serif";
                      font-size: 11pt;"> </span><span
                      style="font-family:
                      "Calibri","sans-serif";"></span></p>
                  <p class="ecxMsoNormal"><span style="color: rgb(31,
                      73, 125); font-family:
                      "Calibri","sans-serif";
                      font-size: 11pt;"> </span><span
                      style="font-family:
                      "Calibri","sans-serif";"></span></p>
                  <div>
                    <div style="border-width: 1pt medium medium;
                      border-style: solid none none; border-color:
                      currentColor; padding: 3pt 0cm 0cm;">
                      <p class="ecxMsoNormal"><b><span
                            style="font-family:
                            "Tahoma","sans-serif";
                            font-size: 10pt;">De :</span></b><span
                          style="font-family:
                          "Tahoma","sans-serif";
                          font-size: 10pt;"> <a moz-do-not-send="true"
href="mailto:trnsys-users-bounces@cae.wisc.edu">trnsys-users-bounces@cae.wisc.edu</a>
                          [<a moz-do-not-send="true"
                            href="mailto:trnsys-users-bounces@cae.wisc.edu">mailto:trnsys-users-bounces@cae.wisc.edu</a>]
                          <b>De la part de</b> Tom B<br>
                          <b>Envoyé :</b> samedi 4 mai 2013 13:39<br>
                          <b>À :</b> <a moz-do-not-send="true"
                            href="mailto:trnsys-users@cae.wisc.edu">trnsys-users@cae.wisc.edu</a><br>
                          <b>Objet :</b> [TRNSYS-users] Convergence
                          errors with adaptive temperature limits</span><span
                          style="font-family:
                          "Calibri","sans-serif";"></span></p>
                    </div>
                  </div>
                  <p class="ecxMsoNormal"><span style="font-family:
                      "Calibri","sans-serif";"> </span></p>
                  <div>
                    <div>
                      <p class="ecxMsoNormal"><span style="font-family:
                          "Calibri","sans-serif";">Dear
                          all,<br>
                           <br>
                          In short, I'm facing a problem in which I
                          would like to use a formula for cooling which
                          works perfectly for heating, but gives
                          convergence errors when I apply it to my
                          cooling temperature. It occurs when I'm using
                          adaptive temperature limits in an energy
                          calculation to find the efficiency of a
                          certain shading device. I tried increasing the
                          thermal capacitance to 5*1.2*1.007*roomvolume,
                          the moisture capacitance to 7, I've used time
                          steps varying from 5 minutes to 1 hour, but
                          nothing works. Eventually this results in a
                          fatal error, or if I increase the Limits
                          drastically it only slows down my simulation
                          enormously. I'm using Trnsys 17 by the way.<br>
                           <br>
                          <strong><span style="font-family:
                              "Calibri","sans-serif";">Problem
                              description</span></strong></span></p>
                    </div>
                    <div>
                      <p class="ecxMsoNormal"><span style="font-family:
                          "Calibri","sans-serif";">I've
                          used a 4199.1 kJ/h for both heating and
                          cooling, so given a floor area of 19.44m2 that
                          would be 60W/m2. I've included a file of a
                          project where I isolated this adaptive
                          temperature limit and heating/cooling
                          schedule, so without any shading. One of them
                          shows the situation when there are no
                          convergence errors, but T_Cool_On remains zero
                          degrees, and the other one where in my mind
                          the formula is correct, but convergence errors
                          occur.</span></p>
                    </div>
                    <div>
                      <p class="ecxMsoNormal"><span style="font-family:
                          "Calibri","sans-serif";"> </span></p>
                    </div>
                    <div>
                      <p class="ecxMsoNormal"><span style="font-family:
                          "Calibri","sans-serif";">I
                          think I found where the problem occurs, but I
                          don't know what I'm doing wrong. I use a loop
                          from type 56 to an equation, in which the
                          acceptable indoor temperature depends on the
                          outside temperature (people tollerate higher
                          temperatures if it's warm outside as well),
                          and is compared to the actual indoor
                          temperature to see whether the cooling/heating
                          should be on or off. This goes to another
                          equation to incorporate the annual occupancy
                          schedule for heating and cooling, which is
                          then lead back to type 56. <br>
                           </span></p>
                    </div>
                    <div>
                      <p class="ecxMsoNormal"><strong><span
                            style="font-family:
                            "Calibri","sans-serif";">Heating
                            goes fine, cooling becomes a problem</span></strong><span
                          style="font-family:
                          "Calibri","sans-serif";"><br>
                          Strangely enough, I use similar formulas for
                          heating and cooling, and while heating does
                          not give any problems, the cooling does. This
                          is what I use:<br>
                           <br>
                          T_Heat_On =
                          Heating_need*Heating_schedule*(Target_temperature
                          - 15) + 15 --> 'need' and 'schedule' give
                          either a 0 or 1, and in this way the heating
                          goes on either when the indoor temperature
                          drops below the target temperature while the
                          building is occupied, or when the temperature
                          drops below 15 degrees at any time.<br>
                           <br>
                          T_Cool_On =
                          Cooling_need*Cooling_schedule*(Target_temperature
                          - 30) + 30 --> I tried to do the same for
                          cooling, so it would cool when it would become
                          too hot, or when the temperature would rise
                          above 30 degrees when the building is
                          unoccupied. Strangely enough, this only works
                          when I leave out the maximum of 30 degrees (so
                          T_Cool_On =
                          Cooling_need*Cooling_schedule*Target_temperature),
                          but if I'm not mistaking, this means that at
                          times when the building is not occupied or no
                          cooling is needed, the T_Cool_On is equal to
                          0, meaning that the heating and cooling start
                          to compete with each other because the cooling
                          'wants' a lower temperature than the heating.</span></p>
                    </div>
                    <div>
                      <p class="ecxMsoNormal"><span style="font-family:
                          "Calibri","sans-serif";"> </span></p>
                    </div>
                    <div>
                      <p class="ecxMsoNormal"><span style="font-family:
                          "Calibri","sans-serif";">Could
                          someone please tell me what might cause this
                          convergence error, and possibly also how to
                          solve this? Thank you very much in advance!</span></p>
                    </div>
                    <div>
                      <p class="ecxMsoNormal"><span style="font-family:
                          "Calibri","sans-serif";"> </span></p>
                    </div>
                    <div>
                      <p class="ecxMsoNormal"><span style="font-family:
                          "Calibri","sans-serif";">Kind
                          regards, Tom<br>
                           </span></p>
                    </div>
                  </div>
                </div>
                <p class="ecxMsoNormal"><span style="font-family:
                    "Calibri","sans-serif";"><br>
                    _______________________________________________
                    TRNSYS-users mailing list <a moz-do-not-send="true"
                      href="mailto:TRNSYS-users@cae.wisc.edu">TRNSYS-users@cae.wisc.edu</a>
                    <a moz-do-not-send="true"
                      href="https://mailman.cae.wisc.edu/listinfo/trnsys-users"
                      target="_blank">https://mailman.cae.wisc.edu/listinfo/trnsys-users</a></span></p>
              </div>
            </div>
          </div>
          <br>
          _______________________________________________
          TRNSYS-users mailing list
          <a class="moz-txt-link-abbreviated" href="mailto:TRNSYS-users@cae.wisc.edu">TRNSYS-users@cae.wisc.edu</a>
          <a class="moz-txt-link-freetext" href="https://mailman.cae.wisc.edu/listinfo/trnsys-users">https://mailman.cae.wisc.edu/listinfo/trnsys-users</a></div>
      </div>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <br>
      <pre wrap="">_______________________________________________
TRNSYS-users mailing list
<a class="moz-txt-link-abbreviated" href="mailto:TRNSYS-users@cae.wisc.edu">TRNSYS-users@cae.wisc.edu</a>
<a class="moz-txt-link-freetext" href="https://mailman.cae.wisc.edu/listinfo/trnsys-users">https://mailman.cae.wisc.edu/listinfo/trnsys-users</a>
</pre>
    </blockquote>
    <br>
    <pre class="moz-signature" cols="72">-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI  53703 USA

P:+1.608.274.2577
F:+1.608.278.1475
<a class="moz-txt-link-abbreviated" href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>

<a class="moz-txt-link-freetext" href="http://www.tess-inc.com">http://www.tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.trnsys.com">http://www.trnsys.com</a></pre>
  </body>
</html>