    <p>Marco,</p>
    <p>  We did indeed change the behavior of Type11 with Trnsys17 back
      to what it had been long ago. The issue at hand is that when there
      is no flow through the diverter, what should the output values be
      set to (specifically the outlet temperatures)? Some claim that the
      output value should be set to the input value when there is no
      flow. Others would prefer the last calculated value of the output
      to be held until flow starts. This causes issues if controls are
      based on the outlet conditions of the diverters. There is not
      really a correct answer; it is just a matter of the assumption
      that you wish to make when writing the model. Our reasoning was
      that the temperature of the diverter should go to the inlet
      temperature so that there is not a temperature difference across
      the diverter under no-flow. </p>
    <p>  If you are seeing a dramatic change in energy between the two
      versions, that is an indication that your controls are not
      operating the same between the two. Usually, systems that exhibit
      this behavior are systems that are low on thermal capacitance
      (i.e. there aren't enough pipes modeled in the various hydronics).
      Low- or no-capacitance hydronic loops react unrealistically
      quickly to control decisions and can become unstable. I would be
      curious to know whether you see the same energy differences
      between the v16 and v17 simulation if you add piping to your flow
      network.</p>
    Kind regards,
    <p> David<br>
      <br>
    </p>
    <div class="moz-cite-prefix">On 4/30/2013 10:48, Marco Noro wrote:<br>
    </div>
    <blockquote cite="mid:002a01ce45ba$35de0760$a19a1620$@noro@unipd.it"
      type="cite">
      <meta http-equiv="Content-Type" content="text/html;
        charset=ISO-8859-1">
      <meta name="Generator" content="Microsoft Word 12 (filtered
        medium)">
      <style><!--
/* Font Definitions */
@font-face
        {font-family:"Cambria Math";
        panose-1:2 4 5 3 5 4 6 3 2 4;}
@font-face
        {font-family:Cambria;
        panose-1:2 4 5 3 5 4 6 3 2 4;}
@font-face
        {font-family:Calibri;
        panose-1:2 15 5 2 2 2 4 3 2 4;}
@font-face
        {font-family:Verdana;
        panose-1:2 11 6 4 3 5 4 4 2 4;}
/* Style Definitions */
p.MsoNormal, li.MsoNormal, div.MsoNormal
        {margin:0cm;
        margin-bottom:.0001pt;
        font-size:11.0pt;
        font-family:"Calibri","sans-serif";}
a:link, span.MsoHyperlink
        {mso-style-priority:99;
        color:blue;
        text-decoration:underline;}
a:visited, span.MsoHyperlinkFollowed
        {mso-style-priority:99;
        color:purple;
        text-decoration:underline;}
span.StileMessaggioDiPostaElettronica17
        {mso-style-type:personal-compose;
        font-family:"Calibri","sans-serif";
        color:windowtext;}
.MsoChpDefault
        {mso-style-type:export-only;}
@page WordSection1
        {size:612.0pt 792.0pt;
        margin:70.85pt 2.0cm 2.0cm 2.0cm;}
div.WordSection1
        {page:WordSection1;}
--></style><!--[if gte mso 9]><xml>
<o:shapedefaults v:ext="edit" spidmax="1026" />
</xml><![endif]--><!--[if gte mso 9]><xml>
<o:shapelayout v:ext="edit">
<o:idmap v:ext="edit" data="1" />
</o:shapelayout></xml><![endif]-->
      <div class="WordSection1">
        <p class="MsoNormal"><span lang="EN-US">Dear Trnsys-users,<o:p></o:p></span></p>
        <p class="MsoNormal"><span lang="EN-US">I have opened a .tpf
            project that I had built and run in Trnsys 16 with the new
            release Trnsys 17.<o:p></o:p></span></p>
        <p class="MsoNormal"><span lang="EN-US">With my great surprise,
            the energy balances (it is a solar cooling plant) of the
            same project with the two Trnsys releases are very very
            different.<o:p></o:p></span></p>
        <p class="MsoNormal"><span lang="EN-US">I realized that the mass
            flows are different, and in particular I think that type 11
            behaves in a different way in trnsys 16 and 17.<o:p></o:p></span></p>
        <p class="MsoNormal"><span lang="EN-US">The problem is that in
            my project a have a lot of diverter, mixer, ecc., so: how
            can I solve this problem? That is, the same project should
            behave in the same way!<o:p></o:p></span></p>
        <p class="MsoNormal"><span lang="EN-US">I add that the problem
            could be also (or) in type 2 behaviour in the two trnsys
            releases…<o:p></o:p></span></p>
        <p class="MsoNormal"><span lang="EN-US">Thank you for your
            cooperation!<o:p></o:p></span></p>
        <p class="MsoNormal">Best regards<o:p></o:p></p>
        <p class="MsoNormal">Marco Noro<o:p></o:p></p>
        <p class="MsoNormal"><o:p> </o:p></p>
        <p class="MsoNormal"><o:p> </o:p></p>
        <p class="MsoNormal"><i><span
              style="font-family:"Cambria","serif";color:#0070C0"><o:p> </o:p></span></i></p>
        <p class="MsoNormal"><i><span
              style="font-family:"Cambria","serif";color:#0070C0">***************************************</span></i><i><span
style="font-family:"Cambria","serif";color:#0070C0"><o:p></o:p></span></i></p>
        <p class="MsoNormal"><span
            style="font-family:"Cambria","serif";color:#0070C0">Marco
            Noro, PhD<o:p></o:p></span></p>
        <p class="MsoNormal"><span
            style="font-family:"Cambria","serif";color:#0070C0"
            lang="EN-US">Assistant Professor in Applied Physics<o:p></o:p></span></p>
        <p class="MsoNormal"><i><span
              style="font-family:"Cambria","serif";color:#0070C0"
              lang="EN-US">Department of Management and Engineering
              (DTG)  -  University of Padova<o:p></o:p></span></i></p>
        <p class="MsoNormal"><i><span
              style="font-family:"Cambria","serif";color:#0070C0">stradella
              San Nicola, 3  -  36100  Vicenza  (VI)  -  Italy<o:p></o:p></span></i></p>
        <p class="MsoNormal"><i><span
              style="font-family:"Cambria","serif";color:#0070C0">tel.  
              +390444 998704    -    fax   +390444 998884<o:p></o:p></span></i></p>
        <p class="MsoNormal"><i><span
              style="font-family:"Cambria","serif";color:#0070C0">e-mail  
            </span></i><span
            style="font-family:"Cambria","serif";color:#0070C0"><a
              moz-do-not-send="true" href="mailto:marco.noro@unipd.it"><span
                style="color:blue">marco.noro@unipd.it</span></a></span><u><span
style="font-family:"Cambria","serif";color:#002060"><o:p></o:p></span></u></p>
        <p class="MsoNormal"><span
            style="font-family:"Cambria","serif";color:#002060">               
            <u><a moz-do-not-send="true"
                href="mailto:noro@gest.unipd.it"><span
                  style="color:blue">noro@gest.unipd.it</span></a><o:p></o:p></u></span></p>
        <p class="MsoNormal"><i><span
              style="font-family:"Cambria","serif";color:#0070C0">PEC</span></i>       
          <u><span
              style="font-family:"Cambria","serif";color:blue"
              lang="EN"><a moz-do-not-send="true"
                href="mailto:marco.noro-7002@postacertificata.gov.it"><span
                  style="color:blue" lang="IT">marco.noro-7002@postacertificata.gov.it</span></a></span></u><span
style="font-family:"Verdana","sans-serif""><o:p></o:p></span></p>
        <p class="MsoNormal"><i><span
              style="font-family:"Cambria","serif";color:#4F81BD">web       
            </span></i><u><span
              style="font-family:"Cambria","serif";color:#002060"><a
                moz-do-not-send="true"
                href="http://sites.google.com/site/marconoro03/"><span
                  style="color:blue">http://sites.google.com/site/marconoro03/</span></a><o:p></o:p></span></u></p>
        <p class="MsoNormal"><i><span
              style="font-family:"Cambria","serif";color:#0070C0">skype    
            </span></i><span
            style="font-family:"Cambria","serif";color:blue">nereo3</span><span
style="font-family:"Cambria","serif";color:#002060"><o:p></o:p></span></p>
        <p class="MsoNormal"><o:p> </o:p></p>
        <p class="MsoNormal"><o:p> </o:p></p>
        <p class="MsoNormal"><o:p> </o:p></p>
        <p class="MsoNormal"><o:p> </o:p></p>
      </div>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <br>
      <pre wrap="">_______________________________________________
TRNSYS-users mailing list
<a class="moz-txt-link-abbreviated" href="mailto:TRNSYS-users@cae.wisc.edu">TRNSYS-users@cae.wisc.edu</a>
<a class="moz-txt-link-freetext" href="https://mailman.cae.wisc.edu/listinfo/trnsys-users">https://mailman.cae.wisc.edu/listinfo/trnsys-users</a>
</pre>
    </blockquote>
    <br>
    <pre class="moz-signature" cols="72">-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI  53703 USA

P:+1.608.274.2577
F:+1.608.278.1475
<a class="moz-txt-link-abbreviated" href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>

<a class="moz-txt-link-freetext" href="http://www.tess-inc.com">http://www.tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.trnsys.com">http://www.trnsys.com</a></pre>
  </body>
</html>