<p>I am not clear on what you are trying to accomplish with your model.</p>
<p>If you are trying to model a tank in an environment with a constant temperature, you can just set the environmental temperature inputs to the tank model to a constant 55C. </p>
<p>Type 6 is intended to model the heating of a fluid stream and not the air surrounding a tank.</p>
<p>Regards,</p>
<p>Tim</p>
<div>
<pre>---
Timothy P. McDowell
Executive Vice President
Thermal Energy System Specialists, LLC
22 N Carroll St, Suite 370
Madison, WI 53703
608-274-2577</pre>
</div>
<p>On 2013-04-10 12:17, Rajaa Badaoui wrote:</p>
<blockquote type="cite" style="padding-left:5px; border-left:#1010ff 2px solid; margin-left:5px; width:100%"><!-- html ignored --><!-- head ignored --><!-- meta ignored -->
<div dir="ltr">
<div>
<div>
<div>
<div>
<div>
<div>
<div>
<div>
<div>
<div>Hi everybody,<br /><br /></div>
I'm stuck with trying to control the outside temperature of a stratified storage tank (type534) with the controller type2b and the auxiliary heater type6.</div>
When i first connect only the auxiliary heater to the tank, the auxiliary heater was ON only when there was a flow stream.</div>
Then i connected a controller to maintain the auxiliary heater even if there is no flowrate. the outside storage tank temperature has to be always at 55°C.</div>
But sometimes the outside temperature of the tank is lower than 55°C.</div>
I think i put a sufficient maximum heating rate in the type6.</div>
I connected the tank nodal temperature to the lower input temperature of the controller</div>
<div>I set the upper input temperature of the controller to 55°C<br /><br /></div>
Can somebody help me to understand why i can't maintain the outside temperature at 55°C?<br /><br /></div>
I'll be grateful for any advice<br /><br /></div>
Thanks in advance<br /><br /></div>
Rajaa</div>