<!DOCTYPE html PUBLIC "-//W3C//DTD XHTML 1.0 Transitional//EN">
<html><body>
<p>Dear Raksit,</p>
<p> </p>
<p>I have a couple of comments about this. First of all, it is difficult to see the exact error without seeing the listing (*.lst) file. Also, when converting humidity ratio to %RH, simply use the Type33 component which calls the Pyschrometric subroutine to calculate the moist air properties. However, I would recommend that you simply use Type642 diverter from the TESS Hydronics Library which has a %RH input.</p>
<p> </p>
<p>Best regards,</p>
<p> </p>
<p>Matt Duffy</p>
<p> </p>
<p>On 2013-03-15 03:33, Raksit Pattanapitoon wrote:</p>
<blockquote type="cite" style="padding-left:5px; border-left:#1010ff 2px solid; margin-left:5px; width:100%"><!-- html ignored --><!-- head ignored --><!-- meta ignored -->
<div dir="ltr">
<div>Dear all,</div>
<div>I have been running into this error message:</div>
<strong>TRNSYS Message 25 : Error in determining the unit number specified in an EQUATION. To reference an OUTPUT in a TRNSYS EQUATION, both the UNIT number and OUTPUT number must be enclosed by square brackets and separated by a comma. For example [1,2]</strong>
<div><strong><br /></strong></div>
<div>I think this probably comes from the Equation I use to convert between humidity ratio and %RH (if the error message means something else please let me know). The conversion is necessary because the moist air flow mixer (type 11c) and moist air tee-piece (type 11g) that I'm using need humidity ratio as input/output but my TRNBuild component outputs %RH. Even though I use Equation to change the value, the unit is not changed and thus I am still connecting %RH output to humidity ratio input which causes the error. Does anyone know a way around this?</div>
<div>Thank you for your help in advance!</div>
<div>Best,</div>
<div>Raksit</div>
<div>-- <br />Raksit Pattanapitoon<br />
<div>Cornell University Mechanical Engineering </div>
<div>B.S. 2012, M.Eng. 2013</div>
</div>
</div>
</blockquote>
</body></html>