<html><body bgcolor="#FFFFFF"><div>Annoyingly, I also find the PLR data is the hardest to get. I would also assume that Part Load performance is dependent on conditions such as water entering and leaving temps just as the full load table describes. But the PLR table is not built up like that. It is simply a multiplier to the full load table.</div><div><br></div><div>How do you go about requesting this data from a manufacturer? <br><br>Sent from my iPhone</div><div><br>On 13.03.2013, at 16:19, David BRADLEY <<a href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>> wrote:<br><br></div><div></div><blockquote type="cite"><div>
    Dear Yeo,<br>
      The sample file Samp_C.dat contains full load data for the chiller
    and in our experience, at full load, most chiller performance data
    looks about the same regardless of the type of compressor. The other
    file (Samp_PLR.dat) contains the part load data (the unloading data)
    and that does change from one type of compressor to another.
    Unfortunately, I do not recall what kind of chiller was used to
    develop the sample PLR data. I am fairly certain that it was not a
    reciprocating compressor and that it was either a screw or a rotary.<br>
    Kind regards,<br>
     David<br>
    <br>
    <br>
    <div class="moz-cite-prefix">On 3/12/2013 21:58, #YEO KEAT KEE#
      wrote:<br>
    </div>
    <blockquote cite="mid:E509F3B2D62E8945873C2ADAE6F1BAD364036DF2@SINPRD0111MB391.apcprd01.prod.exchangelabs.com" type="cite">
      
      
      <style><!--
/* Font Definitions */
@font-face
        {font-family:SimSun;
        panose-1:2 1 6 0 3 1 1 1 1 1;}
@font-face
        {font-family:SimSun;
        panose-1:2 1 6 0 3 1 1 1 1 1;}
@font-face
        {font-family:Calibri;
        panose-1:2 15 5 2 2 2 4 3 2 4;}
@font-face
        {font-family:Tahoma;
        panose-1:2 11 6 4 3 5 4 4 2 4;}
@font-face
        {font-family:"\@SimSun";
        panose-1:2 1 6 0 3 1 1 1 1 1;}
@font-face
        {font-family:Consolas;
        panose-1:2 11 6 9 2 2 4 3 2 4;}
/* Style Definitions */
p.MsoNormal, li.MsoNormal, div.MsoNormal
        {margin:0cm;
        margin-bottom:.0001pt;
        font-size:12.0pt;
        font-family:"Times New Roman","serif";
        color:black;}
a:link, span.MsoHyperlink
        {mso-style-priority:99;
        color:blue;
        text-decoration:underline;}
a:visited, span.MsoHyperlinkFollowed
        {mso-style-priority:99;
        color:purple;
        text-decoration:underline;}
p
        {mso-style-priority:99;
        mso-margin-top-alt:auto;
        margin-right:0cm;
        mso-margin-bottom-alt:auto;
        margin-left:0cm;
        font-size:12.0pt;
        font-family:"Times New Roman","serif";
        color:black;}
pre
        {mso-style-priority:99;
        mso-style-link:"HTML Preformatted Char";
        margin:0cm;
        margin-bottom:.0001pt;
        font-size:10.0pt;
        font-family:"Courier New";
        color:black;}
p.MsoAcetate, li.MsoAcetate, div.MsoAcetate
        {mso-style-priority:99;
        mso-style-link:"Balloon Text Char";
        margin:0cm;
        margin-bottom:.0001pt;
        font-size:8.0pt;
        font-family:"Tahoma","sans-serif";
        color:black;}
span.HTMLPreformattedChar
        {mso-style-name:"HTML Preformatted Char";
        mso-style-priority:99;
        mso-style-link:"HTML Preformatted";
        font-family:Consolas;
        color:black;}
span.EmailStyle20
        {mso-style-type:personal;
        font-family:"Calibri","sans-serif";
        color:#1F497D;}
span.EmailStyle21
        {mso-style-type:personal-reply;
        font-family:"Calibri","sans-serif";
        color:#1F497D;}
span.BalloonTextChar
        {mso-style-name:"Balloon Text Char";
        mso-style-priority:99;
        mso-style-link:"Balloon Text";
        font-family:"Tahoma","sans-serif";
        color:black;}
.MsoChpDefault
        {mso-style-type:export-only;
        font-size:10.0pt;}
@page WordSection1
        {size:612.0pt 792.0pt;
        margin:72.0pt 90.0pt 72.0pt 90.0pt;}
div.WordSection1
        {page:WordSection1;}
--></style><!--[if gte mso 9]><xml>
<o:shapedefaults v:ext="edit" spidmax="1026" />
</xml><![endif]--><!--[if gte mso 9]><xml>
<o:shapelayout v:ext="edit">
<o:idmap v:ext="edit" data="1" />
</o:shapelayout></xml><![endif]-->
      <div class="WordSection1">
        <p class="MsoNormal"><span style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D">Dear
          </span><span style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D">All</span><span style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D">,
            <o:p></o:p></span></p>
        <p class="MsoNormal"><span style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D"><o:p> </o:p></span></p>
        <p class="MsoNormal"><span style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D">I
            am just wondering , when
          </span><span style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D">David</span><span style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D">
            mentioned that the normalized performance curves of the
            water cooled chillers look about the same, does it refer to
            a specific type of water cooled chiller, i.e. Centrifugals,
            Screws or</span><span style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D">
            does it  refer to
          </span><span style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D">the
            normalized performance curves of
          </span><span style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D">all
          </span><span style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D">water
            cooled chillers
          </span><span style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D">in</span><span style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D">
            genera</span><span style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D">l,
          </span><span style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D">regardless
            of the type.
          </span><span style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D"><o:p></o:p></span></p>
        <p class="MsoNormal"><span style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D"><o:p> </o:p></span></p>
        <p class="MsoNormal"><span style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D">I
            am using TRNSYS 16, and attached
          </span><span style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D">is</span><span style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D">
            the performance file that are default with the program, does
            the relationship described in this file applies to all types
            of water cooled chiller ? If not, is it possible to find out
            what kind of chiller does it describe ?
            <o:p></o:p></span></p>
        <p class="MsoNormal"><span style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D"><o:p> </o:p></span></p>
        <p class="MsoNormal"><span style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D">Best
            Regards<o:p></o:p></span></p>
        <p class="MsoNormal"><span style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D">Yeo<o:p></o:p></span></p>
        <div>
          <div style="border:none;border-top:solid #B5C4DF
            1.0pt;padding:3.0pt 0cm 0cm 0cm">
            <p class="MsoNormal"><b><span style="font-size:10.0pt;font-family:"Tahoma","sans-serif";color:windowtext" lang="EN-US">From:</span></b><span style="font-size:10.0pt;font-family:"Tahoma","sans-serif";color:windowtext" lang="EN-US"> David BRADLEY [<a moz-do-not-send="true" href="mailto:d.bradley@tess-inc.com"><a href="mailto:d.bradley@tess-inc.com">mailto:d.bradley@tess-inc.com</a></a>]
                <br>
                <b>Sent:</b> Saturday, 16 February, 2013 1:11 AM<br>
                <b>To:</b> Jean Marais<br>
                <b>Cc:</b> #YEO KEAT KEE#; <a moz-do-not-send="true" href="mailto:trnsys-users@cae.wisc.edu"><a href="mailto:trnsys-users@cae.wisc.edu">trnsys-users@cae.wisc.edu</a></a><br>
                <b>Subject:</b> Re: [TRNSYS-users] Type 666 Chiller
                Queries<o:p></o:p></span></p>
          </div>
        </div>
        <p class="MsoNormal"><o:p> </o:p></p>
        <p class="MsoNormal" style="margin-bottom:12.0pt">Dear Yeo,<br>
          Jean's responses are all quite accurate. I wanted to add a
          little bit to the discussion in the hopes that it might make
          your life a little easier. Some years ago, we participated in
          a research project in which we were looking at whether the
          performance of certain pieces of HVAC equipment can
          effectively be normalized. In other words you look at the COP
          and capacity of a device at a particular combination of inlet
          conditions and then divide the COP and the capacity by the
          rated COP and capacity for the device. Then you plot the
          normalized performance over the entire operation range of the
          equipment and you do the same for the same piece of equipment
          from other manufacturers and of other rated capacities. It
          turns out that some kinds of equipment (particularly single
          stage heat pumps and both air and <span style="color:red">water
            cooled chillers) normalize very well meaning that their
            normalized performance curves all look about the same</span>.
          Unloading (part load ratio) curves can look a bit different
          but they begin to look similar again if you first sort them by
          compressor type (screw, rotary, etc.). Other pieces of
          equipment do not look the same at all if you normalize them
          (absorption chillers are a good example).
          <br>
          <br>
            The lesson in all this is that if you have a specific
          chiller, it is best to get the manufacturer's data for that
          chiller and to create a data file from it. If, however, you
          just need a generic chiller, you can use the default
          performance curves in the \Trnsys17\Tess
          Models\SampleCatalogData\ directory and set the rated capacity
          and COP parameters in the Type; you will be quite close in
          your performance estimates.<br>
          <br>
            One other note; make sure that the rated capacity and COP
          that you enter for parameters are at the same conditions to
          which the external data file is normalized. In other words, if
          the data file is normalized to a 5C oulet chilled water
          temperature and a 16C inlet cooling water temperature then
          make sure that the capacity and COP that you enter as the
          rated values are at those same conditions.
          <br>
          Best,<br>
           David<br>
            <o:p></o:p></p>
        <div>
          <p class="MsoNormal">On 2/15/2013 07:10, Jean Marais wrote:<o:p></o:p></p>
        </div>
        <blockquote style="margin-top:5.0pt;margin-bottom:5.0pt">
          <p class="MsoNormal" style="margin-bottom:12.0pt">Wow. You
            stated these questions so well that I can only think that
            you did so already knowing the answeres.<br>
            1. You can't. You need a comprehensive data set from your
            chiller supplier, specifying a matrix of COPs at different
            water temperatures on supply and return side as well as
            condenser supply and return side.<br>
            2. This will be clear in the data set. It is very possible.<br>
            3. There is no mathematical thermal corrolation. It is
            chiller dependant. It is a different data set.<br>
            4. Yes. You'll need data at all the points where your
            chiller may operate at. For example if you don't have data
            for the chiller performance at less than 20% of full rated
            capacity, then the simulation will issue a warning when your
            chiller model is required to output results at these
            conditions (most chillers will turn off below 20% demand).<br>
            5. Correct.<br>
            I stand corrected on any points.<o:p></o:p></p>
          <div>
            <p class="MsoNormal">On 15 February 2013 10:36, #YEO KEAT
              KEE# <<a moz-do-not-send="true" href="mailto:YEOK0031@e.ntu.edu.sg" target="_blank"><a href="mailto:YEOK0031@e.ntu.edu.sg">YEOK0031@e.ntu.edu.sg</a></a>>
              wrote:<o:p></o:p></p>
            <div>
              <div>
                <p class="MsoNormal" style="mso-margin-top-alt:auto;mso-margin-bottom-alt:auto"><span lang="EN-US">Dear Fellow Trnsys Users</span><o:p></o:p></p>
                <p class="MsoNormal" style="mso-margin-top-alt:auto;mso-margin-bottom-alt:auto"><span lang="EN-US">I am a new user to Trnsys and is
                    modeling a water cooled chiller system using type
                    666 as the chiller.</span><o:p></o:p></p>
                <p class="MsoNormal" style="mso-margin-top-alt:auto;mso-margin-bottom-alt:auto"><span lang="EN-US">I understand that if I want to model a
                    specific chiller model in the system, I will have to
                    make changes to the chiller performance data file
                    and the part load performance data file.</span><o:p></o:p></p>
                <p class="MsoNormal" style="mso-margin-top-alt:auto;mso-margin-bottom-alt:auto"><span lang="EN-US">In the chiller performance data file, I
                    see that there the capacity ratio and the COP ratio
                    being defined as 1 at 7C Outlet CHWT 30C INLET CWT.</span><o:p></o:p></p>
                <p class="MsoNormal" style="mso-margin-top-alt:auto;mso-margin-bottom-alt:auto"><span lang="EN-US">1.</span><span style="font-size:7.0pt" lang="EN-US">      
                  </span><span lang="EN-US">If I only have the
                    performance data of the chiller at  6.7C Outlet CHWT
                    29.4C INLET CWT, how can I make use of this data to
                    input it into the chiller performance data file?</span><o:p></o:p></p>
                <p><span lang="EN-US">2.</span><span style="font-size:7.0pt" lang="EN-US">       </span>
                  <span lang="EN-US">Must the capacity ratio and the COP
                    ratio being defined as 1 at 7C Outlet CHWT 30C INLET
                    CWT, or can it be defined as 1 at other  Outlet CHWT
                    and Inlet CWT ?</span><o:p></o:p></p>
                <p><span lang="EN-US">3.</span><span style="font-size:7.0pt" lang="EN-US">       </span>
                  <span lang="EN-US">How does the part load ratio data
                    of the chiller relate to the different Capacity
                    Ratio and COP ratio ?</span><o:p></o:p></p>
                <p><span lang="EN-US">4.</span><span style="font-size:7.0pt" lang="EN-US">       </span>
                  <span lang="EN-US">In the parameter tab of the type
                    666 chiller, it is stated that “The capacity of the
                    machine at its rated condition (typically 30 C (85
                    F) inlet cooling water temperature and 7 C (44 F)
                    chilled water set point temperature)The data file
                    associated with this model should be consistent with
                    this rating conditions.” . Does it mean that I have
                    to include the chiller performance at 7C chilled
                    water set point and 30C inlet cooling water
                    temperature in the chiller performance data file ?</span><o:p></o:p></p>
                <p><span lang="EN-US">5.</span><span style="font-size:7.0pt" lang="EN-US">       </span>
                  <span lang="EN-US">In the chiller performance data
                    file, it is observed that the chiller capacity ratio
                    can be more than 1.  Does this means that the
                    chiller current capacity is higher than the rated
                    capacity?</span><o:p></o:p></p>
                <p><span lang="EN-US">Can anyone kindly advice on the
                    above mentioned queries ?</span><o:p></o:p></p>
                <p class="MsoNormal" style="mso-margin-top-alt:auto;mso-margin-bottom-alt:auto"><span lang="EN-US"> Thank You !</span><o:p></o:p></p>
                <p class="MsoNormal" style="mso-margin-top-alt:auto;mso-margin-bottom-alt:auto"><span lang="EN-US"> Best Regards</span><o:p></o:p></p>
                <p class="MsoNormal" style="mso-margin-top-alt:auto;mso-margin-bottom-alt:auto"><span lang="EN-US">KK Yeo</span><o:p></o:p></p>
                <p><span lang="EN-US"> </span><o:p></o:p></p>
              </div>
            </div>
            <p class="MsoNormal" style="margin-bottom:12.0pt"><br>
              _______________________________________________<br>
              TRNSYS-users mailing list<br>
              <a moz-do-not-send="true" href="mailto:TRNSYS-users@cae.wisc.edu"><a href="mailto:TRNSYS-users@cae.wisc.edu">TRNSYS-users@cae.wisc.edu</a></a><br>
              <a moz-do-not-send="true" href="https://mailman.cae.wisc.edu/listinfo/trnsys-users" target="_blank"><a href="https://mailman.cae.wisc.edu/listinfo/trnsys-users">https://mailman.cae.wisc.edu/listinfo/trnsys-users</a></a><o:p></o:p></p>
          </div>
          <p class="MsoNormal" style="margin-bottom:12.0pt"><br>
            <br>
            <br>
            <o:p></o:p></p>
          <pre>_______________________________________________<o:p></o:p></pre>
          <pre>TRNSYS-users mailing list<o:p></o:p></pre>
          <pre><a moz-do-not-send="true" href="mailto:TRNSYS-users@cae.wisc.edu"><a href="mailto:TRNSYS-users@cae.wisc.edu">TRNSYS-users@cae.wisc.edu</a></a><o:p></o:p></pre>
          <pre><a moz-do-not-send="true" href="https://mailman.cae.wisc.edu/listinfo/trnsys-users"><a href="https://mailman.cae.wisc.edu/listinfo/trnsys-users">https://mailman.cae.wisc.edu/listinfo/trnsys-users</a></a><o:p></o:p></pre>
        </blockquote>
        <p class="MsoNormal" style="margin-bottom:12.0pt"><o:p> </o:p></p>
        <pre>-- <o:p></o:p></pre>
        <pre>***************************<o:p></o:p></pre>
        <pre>David BRADLEY<o:p></o:p></pre>
        <pre>Principal<o:p></o:p></pre>
        <pre>Thermal Energy Systems Specialists, LLC<o:p></o:p></pre>
        <pre>22 North Carroll Street - suite 370<o:p></o:p></pre>
        <pre>Madison, WI  53703 USA<o:p></o:p></pre>
        <pre><o:p> </o:p></pre>
        <pre>P:+1.608.274.2577<o:p></o:p></pre>
        <pre>F:+1.608.278.1475<o:p></o:p></pre>
        <pre><a moz-do-not-send="true" href="mailto:d.bradley@tess-inc.com"><a href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a></a><o:p></o:p></pre>
        <pre><o:p> </o:p></pre>
        <pre><a moz-do-not-send="true" href="http://www.tess-inc.com"><a href="http://www.tess-inc.com">http://www.tess-inc.com</a></a><o:p></o:p></pre>
        <pre><a moz-do-not-send="true" href="http://www.trnsys.com"><a href="http://www.trnsys.com">http://www.trnsys.com</a></a><o:p></o:p></pre>
      </div>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <br>
      <pre wrap="">_______________________________________________
TRNSYS-users mailing list
<a class="moz-txt-link-abbreviated" href="mailto:TRNSYS-users@cae.wisc.edu"><a href="mailto:TRNSYS-users@cae.wisc.edu">TRNSYS-users@cae.wisc.edu</a></a>
<a class="moz-txt-link-freetext" href="https://mailman.cae.wisc.edu/listinfo/trnsys-users"><a href="https://mailman.cae.wisc.edu/listinfo/trnsys-users">https://mailman.cae.wisc.edu/listinfo/trnsys-users</a></a>
</pre>
    </blockquote>
    <br>
    <pre class="moz-signature" cols="72">-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI  53703 USA

P:+1.608.274.2577
F:+1.608.278.1475
<a class="moz-txt-link-abbreviated" href="mailto:d.bradley@tess-inc.com"><a href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a></a>

<a class="moz-txt-link-freetext" href="http://www.tess-inc.com"><a href="http://www.tess-inc.com">http://www.tess-inc.com</a></a>
<a class="moz-txt-link-freetext" href="http://www.trnsys.com"><a href="http://www.trnsys.com">http://www.trnsys.com</a></a></pre>
  

</div></blockquote><blockquote type="cite"><div><span>_______________________________________________</span><br><span>TRNSYS-users mailing list</span><br><span><a href="mailto:TRNSYS-users@cae.wisc.edu">TRNSYS-users@cae.wisc.edu</a></span><br><span><a href="https://mailman.cae.wisc.edu/listinfo/trnsys-users">https://mailman.cae.wisc.edu/listinfo/trnsys-users</a></span><br></div></blockquote></body></html>