<html><body bgcolor="#FFFFFF"><div>Annoyingly, I also find the PLR data is the hardest to get. I would also assume that Part Load performance is dependent on conditions such as water entering and leaving temps just as the full load table describes. But the PLR table is not built up like that. It is simply a multiplier to the full load table.</div><div><br></div><div>How do you go about requesting this data from a manufacturer? <br><br>Sent from my iPhone</div><div><br>On 13.03.2013, at 16:19, David BRADLEY <<a href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>> wrote:<br><br></div><div></div><blockquote type="cite"><div>
Dear Yeo,<br>
The sample file Samp_C.dat contains full load data for the chiller
and in our experience, at full load, most chiller performance data
looks about the same regardless of the type of compressor. The other
file (Samp_PLR.dat) contains the part load data (the unloading data)
and that does change from one type of compressor to another.
Unfortunately, I do not recall what kind of chiller was used to
develop the sample PLR data. I am fairly certain that it was not a
reciprocating compressor and that it was either a screw or a rotary.<br>
Kind regards,<br>
David<br>
<br>
<br>
<div class="moz-cite-prefix">On 3/12/2013 21:58, #YEO KEAT KEE#
wrote:<br>
</div>
<blockquote cite="mid:E509F3B2D62E8945873C2ADAE6F1BAD364036DF2@SINPRD0111MB391.apcprd01.prod.exchangelabs.com" type="cite">
<style><!--
/* Font Definitions */
@font-face
{font-family:SimSun;
panose-1:2 1 6 0 3 1 1 1 1 1;}
@font-face
{font-family:SimSun;
panose-1:2 1 6 0 3 1 1 1 1 1;}
@font-face
{font-family:Calibri;
panose-1:2 15 5 2 2 2 4 3 2 4;}
@font-face
{font-family:Tahoma;
panose-1:2 11 6 4 3 5 4 4 2 4;}
@font-face
{font-family:"\@SimSun";
panose-1:2 1 6 0 3 1 1 1 1 1;}
@font-face
{font-family:Consolas;
panose-1:2 11 6 9 2 2 4 3 2 4;}
/* Style Definitions */
p.MsoNormal, li.MsoNormal, div.MsoNormal
{margin:0cm;
margin-bottom:.0001pt;
font-size:12.0pt;
font-family:"Times New Roman","serif";
color:black;}
a:link, span.MsoHyperlink
{mso-style-priority:99;
color:blue;
text-decoration:underline;}
a:visited, span.MsoHyperlinkFollowed
{mso-style-priority:99;
color:purple;
text-decoration:underline;}
p
{mso-style-priority:99;
mso-margin-top-alt:auto;
margin-right:0cm;
mso-margin-bottom-alt:auto;
margin-left:0cm;
font-size:12.0pt;
font-family:"Times New Roman","serif";
color:black;}
pre
{mso-style-priority:99;
mso-style-link:"HTML Preformatted Char";
margin:0cm;
margin-bottom:.0001pt;
font-size:10.0pt;
font-family:"Courier New";
color:black;}
p.MsoAcetate, li.MsoAcetate, div.MsoAcetate
{mso-style-priority:99;
mso-style-link:"Balloon Text Char";
margin:0cm;
margin-bottom:.0001pt;
font-size:8.0pt;
font-family:"Tahoma","sans-serif";
color:black;}
span.HTMLPreformattedChar
{mso-style-name:"HTML Preformatted Char";
mso-style-priority:99;
mso-style-link:"HTML Preformatted";
font-family:Consolas;
color:black;}
span.EmailStyle20
{mso-style-type:personal;
font-family:"Calibri","sans-serif";
color:#1F497D;}
span.EmailStyle21
{mso-style-type:personal-reply;
font-family:"Calibri","sans-serif";
color:#1F497D;}
span.BalloonTextChar
{mso-style-name:"Balloon Text Char";
mso-style-priority:99;
mso-style-link:"Balloon Text";
font-family:"Tahoma","sans-serif";
color:black;}
.MsoChpDefault
{mso-style-type:export-only;
font-size:10.0pt;}
@page WordSection1
{size:612.0pt 792.0pt;
margin:72.0pt 90.0pt 72.0pt 90.0pt;}
div.WordSection1
{page:WordSection1;}
--></style><!--[if gte mso 9]><xml>
<o:shapedefaults v:ext="edit" spidmax="1026" />
</xml><![endif]--><!--[if gte mso 9]><xml>
<o:shapelayout v:ext="edit">
<o:idmap v:ext="edit" data="1" />
</o:shapelayout></xml><![endif]-->
<div class="WordSection1">
<p class="MsoNormal"><span style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D">Dear
</span><span style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D">All</span><span style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D">,
<o:p></o:p></span></p>
<p class="MsoNormal"><span style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D"><o:p> </o:p></span></p>
<p class="MsoNormal"><span style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D">I
am just wondering , when
</span><span style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D">David</span><span style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D">
mentioned that the normalized performance curves of the
water cooled chillers look about the same, does it refer to
a specific type of water cooled chiller, i.e. Centrifugals,
Screws or</span><span style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D">
does it refer to
</span><span style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D">the
normalized performance curves of
</span><span style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D">all
</span><span style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D">water
cooled chillers
</span><span style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D">in</span><span style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D">
genera</span><span style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D">l,
</span><span style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D">regardless
of the type.
</span><span style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D"><o:p></o:p></span></p>
<p class="MsoNormal"><span style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D"><o:p> </o:p></span></p>
<p class="MsoNormal"><span style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D">I
am using TRNSYS 16, and attached
</span><span style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D">is</span><span style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D">
the performance file that are default with the program, does
the relationship described in this file applies to all types
of water cooled chiller ? If not, is it possible to find out
what kind of chiller does it describe ?
<o:p></o:p></span></p>
<p class="MsoNormal"><span style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D"><o:p> </o:p></span></p>
<p class="MsoNormal"><span style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D">Best
Regards<o:p></o:p></span></p>
<p class="MsoNormal"><span style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D">Yeo<o:p></o:p></span></p>
<div>
<div style="border:none;border-top:solid #B5C4DF
1.0pt;padding:3.0pt 0cm 0cm 0cm">
<p class="MsoNormal"><b><span style="font-size:10.0pt;font-family:"Tahoma","sans-serif";color:windowtext" lang="EN-US">From:</span></b><span style="font-size:10.0pt;font-family:"Tahoma","sans-serif";color:windowtext" lang="EN-US"> David BRADLEY [<a moz-do-not-send="true" href="mailto:d.bradley@tess-inc.com"><a href="mailto:d.bradley@tess-inc.com">mailto:d.bradley@tess-inc.com</a></a>]
<br>
<b>Sent:</b> Saturday, 16 February, 2013 1:11 AM<br>
<b>To:</b> Jean Marais<br>
<b>Cc:</b> #YEO KEAT KEE#; <a moz-do-not-send="true" href="mailto:trnsys-users@cae.wisc.edu"><a href="mailto:trnsys-users@cae.wisc.edu">trnsys-users@cae.wisc.edu</a></a><br>
<b>Subject:</b> Re: [TRNSYS-users] Type 666 Chiller
Queries<o:p></o:p></span></p>
</div>
</div>
<p class="MsoNormal"><o:p> </o:p></p>
<p class="MsoNormal" style="margin-bottom:12.0pt">Dear Yeo,<br>
Jean's responses are all quite accurate. I wanted to add a
little bit to the discussion in the hopes that it might make
your life a little easier. Some years ago, we participated in
a research project in which we were looking at whether the
performance of certain pieces of HVAC equipment can
effectively be normalized. In other words you look at the COP
and capacity of a device at a particular combination of inlet
conditions and then divide the COP and the capacity by the
rated COP and capacity for the device. Then you plot the
normalized performance over the entire operation range of the
equipment and you do the same for the same piece of equipment
from other manufacturers and of other rated capacities. It
turns out that some kinds of equipment (particularly single
stage heat pumps and both air and <span style="color:red">water
cooled chillers) normalize very well meaning that their
normalized performance curves all look about the same</span>.
Unloading (part load ratio) curves can look a bit different
but they begin to look similar again if you first sort them by
compressor type (screw, rotary, etc.). Other pieces of
equipment do not look the same at all if you normalize them
(absorption chillers are a good example).
<br>
<br>
The lesson in all this is that if you have a specific
chiller, it is best to get the manufacturer's data for that
chiller and to create a data file from it. If, however, you
just need a generic chiller, you can use the default
performance curves in the \Trnsys17\Tess
Models\SampleCatalogData\ directory and set the rated capacity
and COP parameters in the Type; you will be quite close in
your performance estimates.<br>
<br>
One other note; make sure that the rated capacity and COP
that you enter for parameters are at the same conditions to
which the external data file is normalized. In other words, if
the data file is normalized to a 5C oulet chilled water
temperature and a 16C inlet cooling water temperature then
make sure that the capacity and COP that you enter as the
rated values are at those same conditions.
<br>
Best,<br>
David<br>
<o:p></o:p></p>
<div>
<p class="MsoNormal">On 2/15/2013 07:10, Jean Marais wrote:<o:p></o:p></p>
</div>
<blockquote style="margin-top:5.0pt;margin-bottom:5.0pt">
<p class="MsoNormal" style="margin-bottom:12.0pt">Wow. You
stated these questions so well that I can only think that
you did so already knowing the answeres.<br>
1. You can't. You need a comprehensive data set from your
chiller supplier, specifying a matrix of COPs at different
water temperatures on supply and return side as well as
condenser supply and return side.<br>
2. This will be clear in the data set. It is very possible.<br>
3. There is no mathematical thermal corrolation. It is
chiller dependant. It is a different data set.<br>
4. Yes. You'll need data at all the points where your
chiller may operate at. For example if you don't have data
for the chiller performance at less than 20% of full rated
capacity, then the simulation will issue a warning when your
chiller model is required to output results at these
conditions (most chillers will turn off below 20% demand).<br>
5. Correct.<br>
I stand corrected on any points.<o:p></o:p></p>
<div>
<p class="MsoNormal">On 15 February 2013 10:36, #YEO KEAT
KEE# <<a moz-do-not-send="true" href="mailto:YEOK0031@e.ntu.edu.sg" target="_blank"><a href="mailto:YEOK0031@e.ntu.edu.sg">YEOK0031@e.ntu.edu.sg</a></a>>
wrote:<o:p></o:p></p>
<div>
<div>
<p class="MsoNormal" style="mso-margin-top-alt:auto;mso-margin-bottom-alt:auto"><span lang="EN-US">Dear Fellow Trnsys Users</span><o:p></o:p></p>
<p class="MsoNormal" style="mso-margin-top-alt:auto;mso-margin-bottom-alt:auto"><span lang="EN-US">I am a new user to Trnsys and is
modeling a water cooled chiller system using type
666 as the chiller.</span><o:p></o:p></p>
<p class="MsoNormal" style="mso-margin-top-alt:auto;mso-margin-bottom-alt:auto"><span lang="EN-US">I understand that if I want to model a
specific chiller model in the system, I will have to
make changes to the chiller performance data file
and the part load performance data file.</span><o:p></o:p></p>
<p class="MsoNormal" style="mso-margin-top-alt:auto;mso-margin-bottom-alt:auto"><span lang="EN-US">In the chiller performance data file, I
see that there the capacity ratio and the COP ratio
being defined as 1 at 7C Outlet CHWT 30C INLET CWT.</span><o:p></o:p></p>
<p class="MsoNormal" style="mso-margin-top-alt:auto;mso-margin-bottom-alt:auto"><span lang="EN-US">1.</span><span style="font-size:7.0pt" lang="EN-US">
</span><span lang="EN-US">If I only have the
performance data of the chiller at 6.7C Outlet CHWT
29.4C INLET CWT, how can I make use of this data to
input it into the chiller performance data file?</span><o:p></o:p></p>
<p><span lang="EN-US">2.</span><span style="font-size:7.0pt" lang="EN-US"> </span>
<span lang="EN-US">Must the capacity ratio and the COP
ratio being defined as 1 at 7C Outlet CHWT 30C INLET
CWT, or can it be defined as 1 at other Outlet CHWT
and Inlet CWT ?</span><o:p></o:p></p>
<p><span lang="EN-US">3.</span><span style="font-size:7.0pt" lang="EN-US"> </span>
<span lang="EN-US">How does the part load ratio data
of the chiller relate to the different Capacity
Ratio and COP ratio ?</span><o:p></o:p></p>
<p><span lang="EN-US">4.</span><span style="font-size:7.0pt" lang="EN-US"> </span>
<span lang="EN-US">In the parameter tab of the type
666 chiller, it is stated that “The capacity of the
machine at its rated condition (typically 30 C (85
F) inlet cooling water temperature and 7 C (44 F)
chilled water set point temperature)The data file
associated with this model should be consistent with
this rating conditions.” . Does it mean that I have
to include the chiller performance at 7C chilled
water set point and 30C inlet cooling water
temperature in the chiller performance data file ?</span><o:p></o:p></p>
<p><span lang="EN-US">5.</span><span style="font-size:7.0pt" lang="EN-US"> </span>
<span lang="EN-US">In the chiller performance data
file, it is observed that the chiller capacity ratio
can be more than 1. Does this means that the
chiller current capacity is higher than the rated
capacity?</span><o:p></o:p></p>
<p><span lang="EN-US">Can anyone kindly advice on the
above mentioned queries ?</span><o:p></o:p></p>
<p class="MsoNormal" style="mso-margin-top-alt:auto;mso-margin-bottom-alt:auto"><span lang="EN-US"> Thank You !</span><o:p></o:p></p>
<p class="MsoNormal" style="mso-margin-top-alt:auto;mso-margin-bottom-alt:auto"><span lang="EN-US"> Best Regards</span><o:p></o:p></p>
<p class="MsoNormal" style="mso-margin-top-alt:auto;mso-margin-bottom-alt:auto"><span lang="EN-US">KK Yeo</span><o:p></o:p></p>
<p><span lang="EN-US"> </span><o:p></o:p></p>
</div>
</div>
<p class="MsoNormal" style="margin-bottom:12.0pt"><br>
_______________________________________________<br>
TRNSYS-users mailing list<br>
<a moz-do-not-send="true" href="mailto:TRNSYS-users@cae.wisc.edu"><a href="mailto:TRNSYS-users@cae.wisc.edu">TRNSYS-users@cae.wisc.edu</a></a><br>
<a moz-do-not-send="true" href="https://mailman.cae.wisc.edu/listinfo/trnsys-users" target="_blank"><a href="https://mailman.cae.wisc.edu/listinfo/trnsys-users">https://mailman.cae.wisc.edu/listinfo/trnsys-users</a></a><o:p></o:p></p>
</div>
<p class="MsoNormal" style="margin-bottom:12.0pt"><br>
<br>
<br>
<o:p></o:p></p>
<pre>_______________________________________________<o:p></o:p></pre>
<pre>TRNSYS-users mailing list<o:p></o:p></pre>
<pre><a moz-do-not-send="true" href="mailto:TRNSYS-users@cae.wisc.edu"><a href="mailto:TRNSYS-users@cae.wisc.edu">TRNSYS-users@cae.wisc.edu</a></a><o:p></o:p></pre>
<pre><a moz-do-not-send="true" href="https://mailman.cae.wisc.edu/listinfo/trnsys-users"><a href="https://mailman.cae.wisc.edu/listinfo/trnsys-users">https://mailman.cae.wisc.edu/listinfo/trnsys-users</a></a><o:p></o:p></pre>
</blockquote>
<p class="MsoNormal" style="margin-bottom:12.0pt"><o:p> </o:p></p>
<pre>-- <o:p></o:p></pre>
<pre>***************************<o:p></o:p></pre>
<pre>David BRADLEY<o:p></o:p></pre>
<pre>Principal<o:p></o:p></pre>
<pre>Thermal Energy Systems Specialists, LLC<o:p></o:p></pre>
<pre>22 North Carroll Street - suite 370<o:p></o:p></pre>
<pre>Madison, WI 53703 USA<o:p></o:p></pre>
<pre><o:p> </o:p></pre>
<pre>P:+1.608.274.2577<o:p></o:p></pre>
<pre>F:+1.608.278.1475<o:p></o:p></pre>
<pre><a moz-do-not-send="true" href="mailto:d.bradley@tess-inc.com"><a href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a></a><o:p></o:p></pre>
<pre><o:p> </o:p></pre>
<pre><a moz-do-not-send="true" href="http://www.tess-inc.com"><a href="http://www.tess-inc.com">http://www.tess-inc.com</a></a><o:p></o:p></pre>
<pre><a moz-do-not-send="true" href="http://www.trnsys.com"><a href="http://www.trnsys.com">http://www.trnsys.com</a></a><o:p></o:p></pre>
</div>
<br>
<fieldset class="mimeAttachmentHeader"></fieldset>
<br>
<pre wrap="">_______________________________________________
TRNSYS-users mailing list
<a class="moz-txt-link-abbreviated" href="mailto:TRNSYS-users@cae.wisc.edu"><a href="mailto:TRNSYS-users@cae.wisc.edu">TRNSYS-users@cae.wisc.edu</a></a>
<a class="moz-txt-link-freetext" href="https://mailman.cae.wisc.edu/listinfo/trnsys-users"><a href="https://mailman.cae.wisc.edu/listinfo/trnsys-users">https://mailman.cae.wisc.edu/listinfo/trnsys-users</a></a>
</pre>
</blockquote>
<br>
<pre class="moz-signature" cols="72">--
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI 53703 USA
P:+1.608.274.2577
F:+1.608.278.1475
<a class="moz-txt-link-abbreviated" href="mailto:d.bradley@tess-inc.com"><a href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a></a>
<a class="moz-txt-link-freetext" href="http://www.tess-inc.com"><a href="http://www.tess-inc.com">http://www.tess-inc.com</a></a>
<a class="moz-txt-link-freetext" href="http://www.trnsys.com"><a href="http://www.trnsys.com">http://www.trnsys.com</a></a></pre>
</div></blockquote><blockquote type="cite"><div><span>_______________________________________________</span><br><span>TRNSYS-users mailing list</span><br><span><a href="mailto:TRNSYS-users@cae.wisc.edu">TRNSYS-users@cae.wisc.edu</a></span><br><span><a href="https://mailman.cae.wisc.edu/listinfo/trnsys-users">https://mailman.cae.wisc.edu/listinfo/trnsys-users</a></span><br></div></blockquote></body></html>