    Jean,<br>
      The model looks at the full load performance file and determines
    the chiller's nominal capacity (its rated capacity as adjusted by
    the current entering conditions) and its nominal COP (rated COP
    adjusted by the current entering conditions). It then determines how
    much energy the chiller is required to produce and determines PLR =
    qRequired/NominalCapacity. The model then goes looking in the PLR
    file to see what the fraction of full load power is. In a way, the
    model makes use of the kind of data that is available but you are
    quite right in pointing out that the PLR table given by
    manufacturers isn't entirely correct; part load performance isn't as
    simple as a multiplier on full load performance. The only way I have
    found to get that data from the manufacturer is to ask them to
    generate a whole lot of performance points for different entering
    conditions and for different loading conditions, then to assemble a
    full performance map. Often manufacturers are willing to let you
    have access to their selection software for a limited time so that
    you can generate points yourself.<br>
    Best,<br>
     David<br>
    <br>
    <br>
    <div class="moz-cite-prefix">On 3/14/2013 00:23,
      <a class="moz-txt-link-abbreviated" href="mailto:jeannieboef@gmail.com">jeannieboef@gmail.com</a> wrote:<br>
    </div>
    <blockquote
      cite="mid:C7136333-CB93-489D-98EC-43E4DF728A1F@gmail.com"
      type="cite">
      <div>Annoyingly, I also find the PLR data is the hardest to get. I
        would also assume that Part Load performance is dependent on
        conditions such as water entering and leaving temps just as the
        full load table describes. But the PLR table is not built up
        like that. It is simply a multiplier to the full load table.</div>
      <div><br>
      </div>
      <div>How do you go about requesting this data from a
        manufacturer? <br>
        <br>
        Sent from my iPhone</div>
      <div><br>
        On 13.03.2013, at 16:19, David BRADLEY <<a
          moz-do-not-send="true" href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>>
        wrote:<br>
        <br>
      </div>
      <blockquote type="cite">
        <div> Dear Yeo,<br>
            The sample file Samp_C.dat contains full load data for the
          chiller and in our experience, at full load, most chiller
          performance data looks about the same regardless of the type
          of compressor. The other file (Samp_PLR.dat) contains the part
          load data (the unloading data) and that does change from one
          type of compressor to another. Unfortunately, I do not recall
          what kind of chiller was used to develop the sample PLR data.
          I am fairly certain that it was not a reciprocating compressor
          and that it was either a screw or a rotary.<br>
          Kind regards,<br>
           David<br>
          <br>
          <br>
          <div class="moz-cite-prefix">On 3/12/2013 21:58, #YEO KEAT
            KEE# wrote:<br>
          </div>
          <blockquote
cite="mid:E509F3B2D62E8945873C2ADAE6F1BAD364036DF2@SINPRD0111MB391.apcprd01.prod.exchangelabs.com"
            type="cite">
            <style><!--
/* Font Definitions */
@font-face
        {font-family:SimSun;
        panose-1:2 1 6 0 3 1 1 1 1 1;}
@font-face
        {font-family:SimSun;
        panose-1:2 1 6 0 3 1 1 1 1 1;}
@font-face
        {font-family:Calibri;
        panose-1:2 15 5 2 2 2 4 3 2 4;}
@font-face
        {font-family:Tahoma;
        panose-1:2 11 6 4 3 5 4 4 2 4;}
@font-face
        {font-family:"\@SimSun";
        panose-1:2 1 6 0 3 1 1 1 1 1;}
@font-face
        {font-family:Consolas;
        panose-1:2 11 6 9 2 2 4 3 2 4;}
/* Style Definitions */
p.MsoNormal, li.MsoNormal, div.MsoNormal
        {margin:0cm;
        margin-bottom:.0001pt;
        font-size:12.0pt;
        font-family:"Times New Roman","serif";
        color:black;}
a:link, span.MsoHyperlink
        {mso-style-priority:99;
        color:blue;
        text-decoration:underline;}
a:visited, span.MsoHyperlinkFollowed
        {mso-style-priority:99;
        color:purple;
        text-decoration:underline;}
p
        {mso-style-priority:99;
        mso-margin-top-alt:auto;
        margin-right:0cm;
        mso-margin-bottom-alt:auto;
        margin-left:0cm;
        font-size:12.0pt;
        font-family:"Times New Roman","serif";
        color:black;}
pre
        {mso-style-priority:99;
        mso-style-link:"HTML Preformatted Char";
        margin:0cm;
        margin-bottom:.0001pt;
        font-size:10.0pt;
        font-family:"Courier New";
        color:black;}
p.MsoAcetate, li.MsoAcetate, div.MsoAcetate
        {mso-style-priority:99;
        mso-style-link:"Balloon Text Char";
        margin:0cm;
        margin-bottom:.0001pt;
        font-size:8.0pt;
        font-family:"Tahoma","sans-serif";
        color:black;}
span.HTMLPreformattedChar
        {mso-style-name:"HTML Preformatted Char";
        mso-style-priority:99;
        mso-style-link:"HTML Preformatted";
        font-family:Consolas;
        color:black;}
span.EmailStyle20
        {mso-style-type:personal;
        font-family:"Calibri","sans-serif";
        color:#1F497D;}
span.EmailStyle21
        {mso-style-type:personal-reply;
        font-family:"Calibri","sans-serif";
        color:#1F497D;}
span.BalloonTextChar
        {mso-style-name:"Balloon Text Char";
        mso-style-priority:99;
        mso-style-link:"Balloon Text";
        font-family:"Tahoma","sans-serif";
        color:black;}
.MsoChpDefault
        {mso-style-type:export-only;
        font-size:10.0pt;}
@page WordSection1
        {size:612.0pt 792.0pt;
        margin:72.0pt 90.0pt 72.0pt 90.0pt;}
div.WordSection1
        {page:WordSection1;}
--></style><!--[if gte mso 9]><xml>
<o:shapedefaults v:ext="edit" spidmax="1026" />
</xml><![endif]--><!--[if gte mso 9]><xml>
<o:shapelayout v:ext="edit">
<o:idmap v:ext="edit" data="1" />
</o:shapelayout></xml><![endif]-->
            <div class="WordSection1">
              <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D">Dear

                </span><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D">All</span><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D">,
                  <o:p></o:p></span></p>
              <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D"><o:p> </o:p></span></p>
              <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D">I
                  am just wondering , when </span><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D">David</span><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D">
                  mentioned that the normalized performance curves of
                  the water cooled chillers look about the same, does it
                  refer to a specific type of water cooled chiller, i.e.
                  Centrifugals, Screws or</span><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D">
                  does it  refer to </span><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D">the

                  normalized performance curves of </span><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D">all

                </span><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D">water

                  cooled chillers </span><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D">in</span><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D">
                  genera</span><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D">l,

                </span><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D">regardless

                  of the type. </span><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D"><o:p></o:p></span></p>
              <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D"><o:p> </o:p></span></p>
              <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D">I
                  am using TRNSYS 16, and attached </span><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D">is</span><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D">
                  the performance file that are default with the
                  program, does the relationship described in this file
                  applies to all types of water cooled chiller ? If not,
                  is it possible to find out what kind of chiller does
                  it describe ? <o:p></o:p></span></p>
              <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D"><o:p> </o:p></span></p>
              <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D">Best

                  Regards<o:p></o:p></span></p>
              <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D">Yeo<o:p></o:p></span></p>
              <div>
                <div style="border:none;border-top:solid #B5C4DF
                  1.0pt;padding:3.0pt 0cm 0cm 0cm">
                  <p class="MsoNormal"><b><span
style="font-size:10.0pt;font-family:"Tahoma","sans-serif";color:windowtext"
                        lang="EN-US">From:</span></b><span
style="font-size:10.0pt;font-family:"Tahoma","sans-serif";color:windowtext"
                      lang="EN-US"> David BRADLEY [<a
                        moz-do-not-send="true"
                        href="mailto:d.bradley@tess-inc.com">mailto:d.bradley@tess-inc.com</a>]
                      <br>
                      <b>Sent:</b> Saturday, 16 February, 2013 1:11 AM<br>
                      <b>To:</b> Jean Marais<br>
                      <b>Cc:</b> #YEO KEAT KEE#; <a
                        moz-do-not-send="true"
                        href="mailto:trnsys-users@cae.wisc.edu">trnsys-users@cae.wisc.edu</a><br>
                      <b>Subject:</b> Re: [TRNSYS-users] Type 666
                      Chiller Queries<o:p></o:p></span></p>
                </div>
              </div>
              <p class="MsoNormal"><o:p> </o:p></p>
              <p class="MsoNormal" style="margin-bottom:12.0pt">Dear
                Yeo,<br>
                Jean's responses are all quite accurate. I wanted to add
                a little bit to the discussion in the hopes that it
                might make your life a little easier. Some years ago, we
                participated in a research project in which we were
                looking at whether the performance of certain pieces of
                HVAC equipment can effectively be normalized. In other
                words you look at the COP and capacity of a device at a
                particular combination of inlet conditions and then
                divide the COP and the capacity by the rated COP and
                capacity for the device. Then you plot the normalized
                performance over the entire operation range of the
                equipment and you do the same for the same piece of
                equipment from other manufacturers and of other rated
                capacities. It turns out that some kinds of equipment
                (particularly single stage heat pumps and both air and <span
                  style="color:red">water cooled chillers) normalize
                  very well meaning that their normalized performance
                  curves all look about the same</span>. Unloading (part
                load ratio) curves can look a bit different but they
                begin to look similar again if you first sort them by
                compressor type (screw, rotary, etc.). Other pieces of
                equipment do not look the same at all if you normalize
                them (absorption chillers are a good example). <br>
                <br>
                  The lesson in all this is that if you have a specific
                chiller, it is best to get the manufacturer's data for
                that chiller and to create a data file from it. If,
                however, you just need a generic chiller, you can use
                the default performance curves in the \Trnsys17\Tess
                Models\SampleCatalogData\ directory and set the rated
                capacity and COP parameters in the Type; you will be
                quite close in your performance estimates.<br>
                <br>
                  One other note; make sure that the rated capacity and
                COP that you enter for parameters are at the same
                conditions to which the external data file is
                normalized. In other words, if the data file is
                normalized to a 5C oulet chilled water temperature and a
                16C inlet cooling water temperature then make sure that
                the capacity and COP that you enter as the rated values
                are at those same conditions. <br>
                Best,<br>
                 David<br>
                  <o:p></o:p></p>
              <div>
                <p class="MsoNormal">On 2/15/2013 07:10, Jean Marais
                  wrote:<o:p></o:p></p>
              </div>
              <blockquote style="margin-top:5.0pt;margin-bottom:5.0pt">
                <p class="MsoNormal" style="margin-bottom:12.0pt">Wow.
                  You stated these questions so well that I can only
                  think that you did so already knowing the answeres.<br>
                  1. You can't. You need a comprehensive data set from
                  your chiller supplier, specifying a matrix of COPs at
                  different water temperatures on supply and return side
                  as well as condenser supply and return side.<br>
                  2. This will be clear in the data set. It is very
                  possible.<br>
                  3. There is no mathematical thermal corrolation. It is
                  chiller dependant. It is a different data set.<br>
                  4. Yes. You'll need data at all the points where your
                  chiller may operate at. For example if you don't have
                  data for the chiller performance at less than 20% of
                  full rated capacity, then the simulation will issue a
                  warning when your chiller model is required to output
                  results at these conditions (most chillers will turn
                  off below 20% demand).<br>
                  5. Correct.<br>
                  I stand corrected on any points.<o:p></o:p></p>
                <div>
                  <p class="MsoNormal">On 15 February 2013 10:36, #YEO
                    KEAT KEE# <<a moz-do-not-send="true"
                      href="mailto:YEOK0031@e.ntu.edu.sg">YEOK0031@e.ntu.edu.sg</a>>

                    wrote:<o:p></o:p></p>
                  <div>
                    <div>
                      <p class="MsoNormal"
                        style="mso-margin-top-alt:auto;mso-margin-bottom-alt:auto"><span
                          lang="EN-US">Dear Fellow Trnsys Users</span><o:p></o:p></p>
                      <p class="MsoNormal"
                        style="mso-margin-top-alt:auto;mso-margin-bottom-alt:auto"><span
                          lang="EN-US">I am a new user to Trnsys and is
                          modeling a water cooled chiller system using
                          type 666 as the chiller.</span><o:p></o:p></p>
                      <p class="MsoNormal"
                        style="mso-margin-top-alt:auto;mso-margin-bottom-alt:auto"><span
                          lang="EN-US">I understand that if I want to
                          model a specific chiller model in the system,
                          I will have to make changes to the chiller
                          performance data file and the part load
                          performance data file.</span><o:p></o:p></p>
                      <p class="MsoNormal"
                        style="mso-margin-top-alt:auto;mso-margin-bottom-alt:auto"><span
                          lang="EN-US">In the chiller performance data
                          file, I see that there the capacity ratio and
                          the COP ratio being defined as 1 at 7C Outlet
                          CHWT 30C INLET CWT.</span><o:p></o:p></p>
                      <p class="MsoNormal"
                        style="mso-margin-top-alt:auto;mso-margin-bottom-alt:auto"><span
                          lang="EN-US">1.</span><span
                          style="font-size:7.0pt" lang="EN-US">       </span><span
                          lang="EN-US">If I only have the performance
                          data of the chiller at  6.7C Outlet CHWT 29.4C
                          INLET CWT, how can I make use of this data to
                          input it into the chiller performance data
                          file?</span><o:p></o:p></p>
                      <p><span lang="EN-US">2.</span><span
                          style="font-size:7.0pt" lang="EN-US">       </span>
                        <span lang="EN-US">Must the capacity ratio and
                          the COP ratio being defined as 1 at 7C Outlet
                          CHWT 30C INLET CWT, or can it be defined as 1
                          at other  Outlet CHWT and Inlet CWT ?</span><o:p></o:p></p>
                      <p><span lang="EN-US">3.</span><span
                          style="font-size:7.0pt" lang="EN-US">       </span>
                        <span lang="EN-US">How does the part load ratio
                          data of the chiller relate to the different
                          Capacity Ratio and COP ratio ?</span><o:p></o:p></p>
                      <p><span lang="EN-US">4.</span><span
                          style="font-size:7.0pt" lang="EN-US">       </span>
                        <span lang="EN-US">In the parameter tab of the
                          type 666 chiller, it is stated that “The
                          capacity of the machine at its rated condition
                          (typically 30 C (85 F) inlet cooling water
                          temperature and 7 C (44 F) chilled water set
                          point temperature)The data file associated
                          with this model should be consistent with this
                          rating conditions.” . Does it mean that I have
                          to include the chiller performance at 7C
                          chilled water set point and 30C inlet cooling
                          water temperature in the chiller performance
                          data file ?</span><o:p></o:p></p>
                      <p><span lang="EN-US">5.</span><span
                          style="font-size:7.0pt" lang="EN-US">       </span>
                        <span lang="EN-US">In the chiller performance
                          data file, it is observed that the chiller
                          capacity ratio can be more than 1.  Does this
                          means that the chiller current capacity is
                          higher than the rated capacity?</span><o:p></o:p></p>
                      <p><span lang="EN-US">Can anyone kindly advice on
                          the above mentioned queries ?</span><o:p></o:p></p>
                      <p class="MsoNormal"
                        style="mso-margin-top-alt:auto;mso-margin-bottom-alt:auto"><span
                          lang="EN-US"> Thank You !</span><o:p></o:p></p>
                      <p class="MsoNormal"
                        style="mso-margin-top-alt:auto;mso-margin-bottom-alt:auto"><span
                          lang="EN-US"> Best Regards</span><o:p></o:p></p>
                      <p class="MsoNormal"
                        style="mso-margin-top-alt:auto;mso-margin-bottom-alt:auto"><span
                          lang="EN-US">KK Yeo</span><o:p></o:p></p>
                      <p><span lang="EN-US"> </span><o:p></o:p></p>
                    </div>
                  </div>
                  <p class="MsoNormal" style="margin-bottom:12.0pt"><br>
                    _______________________________________________<br>
                    TRNSYS-users mailing list<br>
                    <a moz-do-not-send="true"
                      href="mailto:TRNSYS-users@cae.wisc.edu">TRNSYS-users@cae.wisc.edu</a><br>
                    <a moz-do-not-send="true"
                      href="https://mailman.cae.wisc.edu/listinfo/trnsys-users">https://mailman.cae.wisc.edu/listinfo/trnsys-users</a><o:p></o:p></p>
                </div>
                <p class="MsoNormal" style="margin-bottom:12.0pt"><br>
                  <br>
                  <br>
                  <o:p></o:p></p>
                <pre>_______________________________________________<o:p></o:p></pre>
                <pre>TRNSYS-users mailing list<o:p></o:p></pre>
                <pre><a moz-do-not-send="true" href="mailto:TRNSYS-users@cae.wisc.edu">TRNSYS-users@cae.wisc.edu</a><o:p></o:p></pre>
                <pre><a moz-do-not-send="true" href="https://mailman.cae.wisc.edu/listinfo/trnsys-users">https://mailman.cae.wisc.edu/listinfo/trnsys-users</a><o:p></o:p></pre>
              </blockquote>
              <p class="MsoNormal" style="margin-bottom:12.0pt"><o:p> </o:p></p>
              <pre>-- <o:p></o:p></pre>
              <pre>***************************<o:p></o:p></pre>
              <pre>David BRADLEY<o:p></o:p></pre>
              <pre>Principal<o:p></o:p></pre>
              <pre>Thermal Energy Systems Specialists, LLC<o:p></o:p></pre>
              <pre>22 North Carroll Street - suite 370<o:p></o:p></pre>
              <pre>Madison, WI  53703 USA<o:p></o:p></pre>
              <pre><o:p> </o:p></pre>
              <pre>P:+1.608.274.2577<o:p></o:p></pre>
              <pre>F:+1.608.278.1475<o:p></o:p></pre>
              <pre><a moz-do-not-send="true" href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a><o:p></o:p></pre>
              <pre><o:p> </o:p></pre>
              <pre><a moz-do-not-send="true" href="http://www.tess-inc.com">http://www.tess-inc.com</a><o:p></o:p></pre>
              <pre><a moz-do-not-send="true" href="http://www.trnsys.com">http://www.trnsys.com</a><o:p></o:p></pre>
            </div>
            <br>
            <fieldset class="mimeAttachmentHeader"></fieldset>
            <br>
            <pre wrap="">_______________________________________________
TRNSYS-users mailing list
<a moz-do-not-send="true" href="mailto:TRNSYS-users@cae.wisc.edu">TRNSYS-users@cae.wisc.edu</a>
<a moz-do-not-send="true" href="https://mailman.cae.wisc.edu/listinfo/trnsys-users">https://mailman.cae.wisc.edu/listinfo/trnsys-users</a>
</pre>
          </blockquote>
          <br>
          <pre class="moz-signature" cols="72">-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI  53703 USA

P:+1.608.274.2577
F:+1.608.278.1475
<a moz-do-not-send="true" href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>

<a moz-do-not-send="true" href="http://www.tess-inc.com">http://www.tess-inc.com</a>
<a moz-do-not-send="true" href="http://www.trnsys.com">http://www.trnsys.com</a></pre>
        </div>
      </blockquote>
      <blockquote type="cite">
        <div><span>_______________________________________________</span><br>
          <span>TRNSYS-users mailing list</span><br>
          <span><a moz-do-not-send="true"
              href="mailto:TRNSYS-users@cae.wisc.edu">TRNSYS-users@cae.wisc.edu</a></span><br>
          <span><a moz-do-not-send="true"
              href="https://mailman.cae.wisc.edu/listinfo/trnsys-users">https://mailman.cae.wisc.edu/listinfo/trnsys-users</a></span><br>
        </div>
      </blockquote>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <br>
      <pre wrap="">_______________________________________________
TRNSYS-users mailing list
<a class="moz-txt-link-abbreviated" href="mailto:TRNSYS-users@cae.wisc.edu">TRNSYS-users@cae.wisc.edu</a>
<a class="moz-txt-link-freetext" href="https://mailman.cae.wisc.edu/listinfo/trnsys-users">https://mailman.cae.wisc.edu/listinfo/trnsys-users</a>
</pre>
    </blockquote>
    <br>
    <pre class="moz-signature" cols="72">-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI  53703 USA

P:+1.608.274.2577
F:+1.608.278.1475
<a class="moz-txt-link-abbreviated" href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>

<a class="moz-txt-link-freetext" href="http://www.tess-inc.com">http://www.tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.trnsys.com">http://www.trnsys.com</a></pre>
  </body>
</html>