    Simon,<br>
      There aren't any heat pump models in the current standard library.
    The TESS HVAC Library has a number of different models available but
    they all use the same basic computation methodology and read
    performance from an external data file. Which heat pump model you
    use depends on which heat pump technology you have (single stage
    air-to-air, multi stage water (source) to air, variable speed air
    (source) to water, etc.).  If you can be more specific about what
    kind of heat pump you want to use, I can suggest a specific Type for
    you.<br>
    <br>
      You will find one difference in heat pump components in that some
    are "normalized" and some are not. The non-normalized components
    require that the machine's capacity and COP be entered into the
    external performance data files for a number of different operating
    conditions. The normalized versions take the machine's rated
    capacity and COP as parameters while the external performance files
    contain ratios of capacity at a particular operating condition to
    the rated capacity (and ratios of COP at the operating condition to
    the rated COP). <br>
    <br>
    Kind regards,<br>
     David<br>
    <br>
    <br>
    <br>
    <div class="moz-cite-prefix">On 3/12/2013 10:04, Simon Janse wrote:<br>
    </div>
    <blockquote
cite="mid:trinity-96a345db-a0ac-48dc-af3f-c79623a7e920-1363100644098@3capp-gmx-bs05"
      type="cite">
      <div style="font-family: Verdana;font-size: 12.0px;">
        <div>Hey TrnSys-community,<br>
        </div>
        <div><br>
        </div>
        <div>which types would you recommend (Standard, Standard TESS
          and Non-Standard TESS)  to use for simulating differnt heat
          pumps. <br>
        </div>
        <div>Thank you very much for your help.<br>
        </div>
        <div><br>
        </div>
        <div>Best regards<br>
        </div>
        <div>Simon <br>
        </div>
      </div>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <br>
      <pre wrap="">_______________________________________________
TRNSYS-users mailing list
<a class="moz-txt-link-abbreviated" href="mailto:TRNSYS-users@cae.wisc.edu">TRNSYS-users@cae.wisc.edu</a>
<a class="moz-txt-link-freetext" href="https://mailman.cae.wisc.edu/listinfo/trnsys-users">https://mailman.cae.wisc.edu/listinfo/trnsys-users</a>
</pre>
    </blockquote>
    <br>
    <pre class="moz-signature" cols="72">-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI  53703 USA

P:+1.608.274.2577
F:+1.608.278.1475
<a class="moz-txt-link-abbreviated" href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>

<a class="moz-txt-link-freetext" href="http://www.tess-inc.com">http://www.tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.trnsys.com">http://www.trnsys.com</a></pre>
  </body>
</html>