    Enyuan,<br>
       The u-value (and g-value) shown in the upper right corner of the
    TRNBuild window type manager are for display only; these values are
    simply read out of the w-4 library. At the end of the file, you will
    find some lines that look like the following:<br>
    <br>
     11015 OPTWHITE15                                   15           <font
      color="#ff0000">5.5</font>    <font color="#0000ff">0.87</font>    
    0.852    0.075   0.90    1   15.00<br>
     12001 Pilkington,OPTITHERM,Coating#3               4/16/4       <font
      color="#ff0000">1.3</font>    <font color="#0000ff">0.64</font>    
    0.516    0.213   0.76    2   24.00<br>
       <br>
    The u-value fields are shown in red, the g-value (SHGC) values are
    shown in blue. You can write whatever numbers you want in those
    fields; TRNBuild picks them up and displays them.<br>
    Kind regards,<br>
     David<br>
    <br>
    <br>
    <br>
    <div class="moz-cite-prefix">On 2/22/2013 14:43, Enyuan Hu wrote:<br>
    </div>
    <blockquote
cite="mid:CAJud35O8r81MnD55Qh4=LybD9FUAtmGMdP5o7=3Q51xfAKpGKw@mail.gmail.com"
      type="cite">
      <div dir="ltr">
        <div class="gmail_default"
style="font-family:arial,helvetica,sans-serif;font-size:small;color:rgb(51,51,255)">Dear
          all,</div>
        <div class="gmail_default"
style="font-family:arial,helvetica,sans-serif;font-size:small;color:rgb(51,51,255)"><br>
        </div>
        <div class="gmail_default"><font color="#3333ff" face="arial,
            helvetica, sans-serif">Recently I used WINDOWS 6.3 to define
            a windows with desired properties. I manipulated the
            configuration so that the outcome u value is 1.88 which I
            wanted it to be. Following the window-defining tutorial, I
            was able to transport the information into TRNSYS
            by modifying the W4-lib file and Prgwin.lib file. However,
            when I selected it from the windows library, the shown value
            was 1.63. Can anyone provide some possible explanations?
            Thanks.</font></div>
        <div class="gmail_default"
style="font-family:arial,helvetica,sans-serif;font-size:small;color:rgb(51,51,255)"><br>
        </div>
        <div class="gmail_default"
style="font-family:arial,helvetica,sans-serif;font-size:small;color:rgb(51,51,255)">cheers,</div>
        <div class="gmail_default"
style="font-family:arial,helvetica,sans-serif;font-size:small;color:rgb(51,51,255)">Enyuan</div>
      </div>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <br>
      <pre wrap="">_______________________________________________
TRNSYS-users mailing list
<a class="moz-txt-link-abbreviated" href="mailto:TRNSYS-users@cae.wisc.edu">TRNSYS-users@cae.wisc.edu</a>
<a class="moz-txt-link-freetext" href="https://mailman.cae.wisc.edu/listinfo/trnsys-users">https://mailman.cae.wisc.edu/listinfo/trnsys-users</a>
</pre>
    </blockquote>
    <br>
    <pre class="moz-signature" cols="72">-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI  53703 USA
P:+1.608.274.2577
F:+1.608.278.1475
<a class="moz-txt-link-abbreviated" href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.tess-inc.com">http://www.tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.trnsys.com">http://www.trnsys.com</a></pre>
  </body>
</html>