    Dear Yeo,<br>
      Jean's responses are all quite accurate. I wanted to add a little
    bit to the discussion in the hopes that it might make your life a
    little easier. Some years ago, we participated in a research project
    in which we were looking at whether the performance of certain
    pieces of HVAC equipment can effectively be normalized. In other
    words you look at the COP and capacity of a device at a particular
    combination of inlet conditions and then divide the COP and the
    capacity by the rated COP and capacity for the device. Then you plot
    the normalized performance over the entire operation range of the
    equipment and you do the same for the same piece of equipment from
    other manufacturers and of other rated capacities. It turns out that
    some kinds of equipment (particularly single stage heat pumps and
    both air and water cooled chillers) normalize very well meaning that
    their normalized performance curves all look about the same.
    Unloading (part load ratio) curves can look a bit different but they
    begin to look similar again if you first sort them by compressor
    type (screw, rotary, etc.). Other pieces of equipment do not look
    the same at all if you normalize them (absorption chillers are a
    good example). <br>
    <br>
      The lesson in all this is that if you have a specific chiller, it
    is best to get the manufacturer's data for that chiller and to
    create a data file from it. If, however, you just need a generic
    chiller, you can use the default performance curves in the
    \Trnsys17\Tess Models\SampleCatalogData\ directory and set the rated
    capacity and COP parameters in the Type; you will be quite close in
    your performance estimates.<br>
    <br>
      One other note; make sure that the rated capacity and COP that you
    enter for parameters are at the same conditions to which the
    external data file is normalized. In other words, if the data file
    is normalized to a 5C oulet chilled water temperature and a 16C
    inlet cooling water temperature then make sure that the capacity and
    COP that you enter as the rated values are at those same conditions.
    <br>
    Best,<br>
     David<br>
      <br>
    <br>
    <div class="moz-cite-prefix">On 2/15/2013 07:10, Jean Marais wrote:<br>
    </div>
    <blockquote
cite="mid:CAAGg3bzeMafHHEArf5De+wJnNRmQW799SrHYSWCbgLSGCOsrOg@mail.gmail.com"
      type="cite">Wow. You stated these questions so well that I can
      only think that you did so already knowing the answeres.<br>
      1. You can't. You need a comprehensive data set from your chiller
      supplier, specifying a matrix of COPs at different water
      temperatures on supply and return side as well as condenser supply
      and return side.<br>
      2. This will be clear in the data set. It is very possible.<br>
      3. There is no mathematical thermal corrolation. It is chiller
      dependant. It is a different data set.<br>
      4. Yes. You'll need data at all the points where your chiller may
      operate at. For example if you don't have data for the chiller
      performance at less than 20% of full rated capacity, then the
      simulation will issue a warning when your chiller model is
      required to output results at these conditions (most chillers will
      turn off below 20% demand).<br>
      5. Correct.<br>
      I stand corrected on any points.<br>
      <br>
      <div class="gmail_quote">On 15 February 2013 10:36, #YEO KEAT KEE#
        <span dir="ltr"><<a moz-do-not-send="true"
            href="mailto:YEOK0031@e.ntu.edu.sg" target="_blank">YEOK0031@e.ntu.edu.sg</a>></span>
        wrote:<br>
        <blockquote class="gmail_quote" style="margin:0 0 0
          .8ex;border-left:1px #ccc solid;padding-left:1ex">
          <div link="blue" vlink="purple" lang="EN-SG">
            <div>
              <p class="MsoNormal"><span lang="EN-US">Dear Fellow Trnsys
                  Users</span></p>
              <p class="MsoNormal"><span lang="EN-US"> </span></p>
              <p class="MsoNormal"><span lang="EN-US">I am a new user to
                  Trnsys and is modeling a water cooled chiller system
                  using type 666 as the chiller.  </span></p>
              <p class="MsoNormal"><span lang="EN-US"> </span></p>
              <p class="MsoNormal"><span lang="EN-US">I understand that
                  if I want to model a specific chiller model in the
                  system, I will have to make changes to the chiller
                  performance data file and the part load performance
                  data file.
                </span></p>
              <p class="MsoNormal"><span lang="EN-US"> </span></p>
              <p class="MsoNormal"><span lang="EN-US">In the chiller
                  performance data file, I see that there the capacity
                  ratio and the COP ratio being defined as 1 at 7C
                  Outlet CHWT 30C INLET CWT.
                </span></p>
              <p class="MsoNormal"><span lang="EN-US"> </span></p>
              <p><span lang="EN-US"><span>1.<span style="font:7.0pt
                      "Times New Roman"">      
                    </span></span></span><span lang="EN-US">If I only
                  have the performance data of the chiller at  6.7C
                  Outlet CHWT 29.4C INLET CWT, how can I make use of
                  this data to input it into the chiller performance
                  data file?</span></p>
              <p><span lang="EN-US"> </span></p>
              <p><span lang="EN-US"><span>2.<span style="font:7.0pt
                      "Times New Roman"">      
                    </span></span></span><span lang="EN-US">Must the
                  capacity ratio and the COP ratio being defined as 1 at
                  7C Outlet CHWT 30C INLET CWT, or can it be defined as
                  1 at other  Outlet CHWT and Inlet CWT ?</span></p>
              <p><span lang="EN-US"> </span></p>
              <p><span lang="EN-US"><span>3.<span style="font:7.0pt
                      "Times New Roman"">      
                    </span></span></span><span lang="EN-US">How does the
                  part load ratio data of the chiller relate to the
                  different Capacity Ratio and COP ratio ?</span></p>
              <p><span lang="EN-US"> </span></p>
              <p><span lang="EN-US"><span>4.<span style="font:7.0pt
                      "Times New Roman"">      
                    </span></span></span><span lang="EN-US">In the
                  parameter tab of the type 666 chiller, it is stated
                  that “The capacity of the machine at its rated
                  condition (typically 30 C (85 F) inlet cooling water
                  temperature and 7 C (44 F) chilled water set point
                  temperature)The data file associated with this model
                  should be consistent with this rating conditions.” .
                  Does it mean that I have to include the chiller
                  performance at 7C chilled water set point and 30C
                  inlet cooling water temperature in the chiller
                  performance data file ?</span></p>
              <p><span lang="EN-US"> </span></p>
              <p><span lang="EN-US"><span>5.<span style="font:7.0pt
                      "Times New Roman"">      
                    </span></span></span><span lang="EN-US">In the
                  chiller performance data file, it is observed that the
                  chiller capacity ratio can be more than 1.  Does this
                  means that the chiller current capacity is higher than
                  the rated capacity?
                </span></p>
              <p><span lang="EN-US"> </span></p>
              <p class="MsoNormal"><span lang="EN-US">Can anyone kindly
                  advice on the above mentioned queries ?</span></p>
              <p class="MsoNormal"><span lang="EN-US"> </span></p>
              <p class="MsoNormal"><span lang="EN-US">Thank You !</span></p>
              <p class="MsoNormal"><span lang="EN-US"> </span></p>
              <p class="MsoNormal"><span lang="EN-US">Best Regards</span></p>
              <p class="MsoNormal"><span lang="EN-US">KK Yeo</span></p>
              <p><span lang="EN-US"> </span></p>
            </div>
          </div>
          <br>
          _______________________________________________<br>
          TRNSYS-users mailing list<br>
          <a moz-do-not-send="true"
            href="mailto:TRNSYS-users@cae.wisc.edu">TRNSYS-users@cae.wisc.edu</a><br>
          <a moz-do-not-send="true"
            href="https://mailman.cae.wisc.edu/listinfo/trnsys-users"
            target="_blank">https://mailman.cae.wisc.edu/listinfo/trnsys-users</a><br>
          <br>
        </blockquote>
      </div>
      <br>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <br>
      <pre wrap="">_______________________________________________
TRNSYS-users mailing list
<a class="moz-txt-link-abbreviated" href="mailto:TRNSYS-users@cae.wisc.edu">TRNSYS-users@cae.wisc.edu</a>
<a class="moz-txt-link-freetext" href="https://mailman.cae.wisc.edu/listinfo/trnsys-users">https://mailman.cae.wisc.edu/listinfo/trnsys-users</a>
</pre>
    </blockquote>
    <br>
    <pre class="moz-signature" cols="72">-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI  53703 USA

P:+1.608.274.2577
F:+1.608.278.1475
<a class="moz-txt-link-abbreviated" href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>

<a class="moz-txt-link-freetext" href="http://www.tess-inc.com">http://www.tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.trnsys.com">http://www.trnsys.com</a></pre>