<font size="4">Dear all,<br><br>I have some questions about Energy balance for one zone (Ntype 904).<br><br>1)
 For Qtrans, it might be stored thermal energy (>0?) in the wall or 
directly transmitted (<0?) through the wall. But I want to calculate 
the two parts exactly, i.e. how to calculate the part of stored thermal 
energy in the wall and directly transmitted energy, separatedly?<br>
<br>2) For Qsolgain, does it mean Ntype 14 +15? or only Ntype 75?<br>What relationship between Qsolgain and Solar_rad. (kWh) in T56_stdoutput.sum file? Are both the same? or included relationship?<br><br>3) For Qgint, is it Ntype 7 + 13? Is it equal to Int_gains in T56_stdoutput.sum file?<br>



<br>4) I want to calculate Heat Loss (or energy consumption) in a zone 
e.g. in winter, whether or not the heat loss includes Qinf + Qvent 
+DQairdt+ Qtrans (only the part of directly transmitted through the 
wall, not the part of stored part, that is why I ask 1))?<br>
<br>For the actual heat gain e<font size="4">.g. </font>in winter in one zone, it only includes Qgint + Qsolgain?<br><br>However, Qheat and Qcool should be Heat loss or heat gain?<br><br>Many thanks in advance!<br>Br.<br>



<br>yang wang</font><br><br><br><br><div class="gmail_quote">2013/1/23 王洋 <span dir="ltr"><<a href="mailto:wanghongyang1767@gmail.com" target="_blank">wanghongyang1767@gmail.com</a>></span><br><blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex">
<br><br><br><div class="gmail_quote">2013/1/21 王洋 <span dir="ltr"><<a href="mailto:wanghongyang1767@gmail.com" target="_blank">wanghongyang1767@gmail.com</a>></span><br><blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex">

<br><div class="gmail_quote">2013/1/18 王洋 <span dir="ltr"><<a href="mailto:wanghongyang1767@gmail.com" target="_blank">wanghongyang1767@gmail.com</a>></span><br><blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex">


<br><br><div class="gmail_quote">2013/1/8  <span dir="ltr"><<a href="mailto:trnsys-users-request@cae.wisc.edu" target="_blank">trnsys-users-request@cae.wisc.edu</a>></span><br><blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex">



Send TRNSYS-users mailing list submissions to<br>
        <a href="mailto:trnsys-users@cae.wisc.edu" target="_blank">trnsys-users@cae.wisc.edu</a><br>
<br>
To subscribe or unsubscribe via the World Wide Web, visit<br>
        <a href="https://mailman.cae.wisc.edu/listinfo/trnsys-users" target="_blank">https://mailman.cae.wisc.edu/listinfo/trnsys-users</a><br>
or, via email, send a message with subject or body 'help' to<br>
        <a href="mailto:trnsys-users-request@cae.wisc.edu" target="_blank">trnsys-users-request@cae.wisc.edu</a><br>
<br>
You can reach the person managing the list at<br>
        <a href="mailto:trnsys-users-owner@cae.wisc.edu" target="_blank">trnsys-users-owner@cae.wisc.edu</a><br>
<br>
When replying, please edit your Subject line so it is more specific<br>
than "Re: Contents of TRNSYS-users digest..."<br>
<br>Today's Topics:<br>
<br>
   1. Re: 2 independet + 1 dependent variables in look-up files<br>
      (David BRADLEY)<br>
   2. Re: Type94a - multi array will be wrongly calculated<br>
      (David BRADLEY)<br>
   3. Hybrid dessicant dehumidifier (Graham S. Wright)<br>
<br><br>---------- 已转发邮件 ----------<br>From: David BRADLEY <<a href="mailto:d.bradley@tess-inc.com" target="_blank">d.bradley@tess-inc.com</a>><br>To: leen peeters <<a href="mailto:l.f.r.peeters@gmail.com" target="_blank">l.f.r.peeters@gmail.com</a>><br>



Cc: "<a href="mailto:trnsys-users@cae.wisc.edu" target="_blank">trnsys-users@cae.wisc.edu</a>" <<a href="mailto:TRNSYS-users@cae.wisc.edu" target="_blank">TRNSYS-users@cae.wisc.edu</a>>, <a href="mailto:vanreeth.b@bxl.daikineurope.com" target="_blank">vanreeth.b@bxl.daikineurope.com</a><br>



Date: Tue, 08 Jan 2013 09:10:04 -0600<br>Subject: Re: [TRNSYS-users] 2 independet + 1 dependent variables in look-up files<br>
  
    
  
  <div text="#000000" bgcolor="#FFFFFF">
    Leen,<br>
      Unless I am misunderstanding what you want to do, the solution is
    quite easy as long as you are able and willing to write a new Type;
    TRNSYS has a built-in kernel subroutine called InterpolateData
    (formerly called DynamicData) that performs exactly the function
    that you are looking for. The subroutine is called from a Type with
    the values of as many as 6 independent variables. The subroutine
    looks through an external file, finds and returns the values of as
    many as 10 dependent variables that correspond to the input values.
    The subroutine interpolates linearly between values but cannot
    extrapolate beyond the range of values that is given in the data
    file.<br>
    <br>
      Before you go too far down the path of writing a new heat pump
    model, I would recommend that you look through the TESS HVAC Library
    documentation on existing heat pump models and also take a look at
    the code of some of those models. Most of them stay away from energy
    rate control (in which a precalculated load is imposed on the heat
    pump) and stick with temperature level control (in which case heat
    pump capacity and fraction of full load power are computed based on
    inlet and ambient conditions.) Those models may be what you are
    looking for or could be modified with little effort to better suit
    your needs.<br>
    Best,<br>
     David<br>
        <br>
    <br>
    <br>
    <div>On 1/8/2013 06:35, leen peeters wrote:<br>
    </div>
    <blockquote type="cite">
      <div dir="ltr">
        <div>Hi all,</div>
        <div> </div>
        <div>We are trying to model more accurately a heat pump for
          which the performance should ideally be read out from a text
          or excel file.</div>
        <div>The data depend on 3 parameters (outdoor and indoor air
          temperature, requested output). </div>
        <div>Part load ratios are hard to define, as the actual capacity
          depends on the model type and the outdoor conditions. So it
          seems logic to use excell. However, values are not a function,
          but should be looked up in the excell table, potentially
          interpolated, ... and to make it more challenging, the final
          SPF does depend on PLR, outdoor and indoor temperature. So it
          is not just using the external temperature and required
          capacity to calculate PLR and consequently use that PLR plus
          indoor temperature to calculate SPF.</div>
        <div> </div>
        <div>Calling 6 different excell files in a simulation of 8760*4
          steps will take considerable time. The current standard TRNSYS
          look up model allows two independent parameters defining the
          output ... so insufficiently accurate.</div>
        <div> </div>
        <div>any suggestions on how to solve that? </div>
        <div> </div>
        <div>thanks,</div>
        <div> </div>
        <div>leen</div>
      </div>
      <br>
      <fieldset></fieldset>
      <br>
      <pre>_______________________________________________
TRNSYS-users mailing list
<a href="mailto:TRNSYS-users@cae.wisc.edu" target="_blank">TRNSYS-users@cae.wisc.edu</a>
<a href="https://mailman.cae.wisc.edu/listinfo/trnsys-users" target="_blank">https://mailman.cae.wisc.edu/listinfo/trnsys-users</a>
</pre>
    </blockquote>
    <br>
    <pre cols="72">-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI  53703 USA

P:<a href="tel:%2B1.608.274.2577" value="+16082742577" target="_blank">+1.608.274.2577</a>
F:<a href="tel:%2B1.608.278.1475" value="+16082781475" target="_blank">+1.608.278.1475</a>
<a href="mailto:d.bradley@tess-inc.com" target="_blank">d.bradley@tess-inc.com</a>

<a href="http://www.tess-inc.com" target="_blank">http://www.tess-inc.com</a>
<a href="http://www.trnsys.com" target="_blank">http://www.trnsys.com</a></pre>
  </div>

<br><br>---------- 已转发邮件 ----------<br>From: David BRADLEY <<a href="mailto:d.bradley@tess-inc.com" target="_blank">d.bradley@tess-inc.com</a>><br>To: Olaf Scholz <<a href="mailto:olaf.scholz@online.de" target="_blank">olaf.scholz@online.de</a>><br>



Cc: <a href="mailto:trnsys-users@cae.wisc.edu" target="_blank">trnsys-users@cae.wisc.edu</a><br>Date: Tue, 08 Jan 2013 09:16:30 -0600<br>Subject: Re: [TRNSYS-users] Type94a - multi array will be wrongly calculated<br>
  
    
  
  <div text="#000000" bgcolor="#FFFFFF">
    Olaf,<br>
     I have used multiple instances of Type94 to compute the output of
    differently oriented PV arrays a number of times and have gotten
    good results so I suspect that there may be a problem in the way the
    model has been defined. One complexity of Type94 is that it has two
    power outputs; one that gives the power at the maximum power point
    (and therefore assumes that the array is equipped with a maximum
    power point tracking (MPPT) device) and another that gives the array
    power at a particular load voltage. This second output is used for
    direct-connected systems that do not have an MPPT and in this case,
    the load voltage is an input to the model. Make sure that you are
    looking at the maximum power point power when you compare the output
    of the three arrays; otherwise, the problem may be that the load
    voltage on the array is so low that the power output of the array is
    minimal no matter what its orientation.  If you are unable to find
    the solution then I would recommend that you send your project to
    your distributor for further assistance.<br>
    Best,<br>
     David<br>
    <br>
    <br>
    <div>On 1/8/2013 03:12, Olaf Scholz wrote:<br>
    </div>
    <blockquote type="cite">
      
      
      
      <div>
        <p class="MsoNormal"><span lang="EN-US">I created a PV collector
            field consisting of three fields (type 94a) for 3 incident
            directions (east, south, west) all 94a- modules are
            connected tot o a type109 weather generator. The total
            incident radiation for the three directions seems to be
            calculated correctly (output of type109 for three different
            surfaces). But the power output of the PV modules seems to
            be always the same, which is not correct. Do you have a
            solution for that ?<u></u><u></u></span></p>
        <p class="MsoNormal"><span lang="EN-US">It seems to be the used
            input variable in type 94a is always the same, so that only
            the last value is used for the calculation.<u></u><u></u></span></p>
        <p class="MsoNormal"><span lang="EN-US"><u></u> <u></u></span></p>
        <p class="MsoNormal"><b><span style="font-size:12.0pt">Olaf</span></b><span><u></u><u></u></span></p>
        <p class="MsoNormal"><u></u> <u></u></p>
      </div>
      <br>
      <fieldset></fieldset>
      <br>
      <pre>_______________________________________________
TRNSYS-users mailing list
<a href="mailto:TRNSYS-users@cae.wisc.edu" target="_blank">TRNSYS-users@cae.wisc.edu</a>
<a href="https://mailman.cae.wisc.edu/listinfo/trnsys-users" target="_blank">https://mailman.cae.wisc.edu/listinfo/trnsys-users</a>
</pre>
    </blockquote>
    <br>
    <pre cols="72">-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI  53703 USA

P:<a href="tel:%2B1.608.274.2577" value="+16082742577" target="_blank">+1.608.274.2577</a>
F:<a href="tel:%2B1.608.278.1475" value="+16082781475" target="_blank">+1.608.278.1475</a>
<a href="mailto:d.bradley@tess-inc.com" target="_blank">d.bradley@tess-inc.com</a>

<a href="http://www.tess-inc.com" target="_blank">http://www.tess-inc.com</a>
<a href="http://www.trnsys.com" target="_blank">http://www.trnsys.com</a></pre>
  </div>

<br><br>---------- 已转发邮件 ----------<br>From: "Graham S. Wright" <<a href="mailto:graham@wrightonsustainability.com" target="_blank">graham@wrightonsustainability.com</a>><br>To: <a href="mailto:trnsys-users@cae.wisc.edu" target="_blank">trnsys-users@cae.wisc.edu</a><br>



Cc: <br>Date: Tue, 8 Jan 2013 09:20:31 -0600<br>Subject: [TRNSYS-users] Hybrid dessicant dehumidifier<br><br>
Hello,<br>
<br>
I am wondering if some one has made a TRNSYS component for this thing, or if there is a way to model it with existing ones.  The DryCool HD dessicant dehumidifier by Munters.  See screenshot below from the manual.<br>
<br>
Thanks,<br>
<br>
Graham S. Wright<br>
Passive House Institute US<br>
<br>
<br>_______________________________________________<br>
TRNSYS-users mailing list<br>
<a href="mailto:TRNSYS-users@cae.wisc.edu" target="_blank">TRNSYS-users@cae.wisc.edu</a><br>
<a href="https://mailman.cae.wisc.edu/listinfo/trnsys-users" target="_blank">https://mailman.cae.wisc.edu/listinfo/trnsys-users</a><br>
<br></blockquote></div><br>
</blockquote></div><br>
</blockquote></div><br>
</blockquote></div><br>