<html>
  <head>
    <meta content="text/html; charset=ISO-8859-1"
      http-equiv="Content-Type">
  </head>
  <body text="#000000" bgcolor="#FFFFFF">
    Teo,<br>
      I would look at the conditions of the air that you are supplying
    to the building; my guess is that the air going in is VERY dry and
    probably quite cold as well. The RH in the room would drop because
    of the dry air being added to the zone (and the quantity of mixed
    air being drawn out of the zone and returned to the cooling coil.<br>
    <blockquote
cite="mid:0E4A4C480F9D464096C8B3D7861BE6A924C064AE@SIXPRD0111MB394.apcprd01.prod.exchangelabs.com"
      type="cite">
      <div style="direction: ltr;font-family: Tahoma;color:
        #000000;font-size: 10pt;">
        <div style="font-family: Times New Roman; color: #000000;
          font-size: 16px">
          <div>
            <div style="direction:ltr; font-family:Tahoma;
              color:#000000; font-size:10pt">1) does the gain from human
              actually contribute moisture? Or it only contributes only
              the latent heat in terms of energy but not in term of
              moisture?
              <br>
            </div>
          </div>
        </div>
      </div>
    </blockquote>
    yes, it does. If you look in the *.inf file, you'll see the
    following lines:<br>
    <br>
    GAIN PERS_ISO02<br>
     CONVECTIVE=156 : RADIATIVE=78 : HUMIDITY=0.081<br>
    <br>
    there is 0.081 kg/h of water added to the airnode per person (and
    according to your schedule)<br>
    <blockquote
cite="mid:0E4A4C480F9D464096C8B3D7861BE6A924C064AE@SIXPRD0111MB394.apcprd01.prod.exchangelabs.com"
      type="cite">
      <div style="direction: ltr;font-family: Tahoma;color:
        #000000;font-size: 10pt;">
        <div style="font-family: Times New Roman; color: #000000;
          font-size: 16px">
          <div>
            <div style="direction:ltr; font-family:Tahoma;
              color:#000000; font-size:10pt">
              2) Does the humidity model actually affects the amount of
              moisture the space is able to hold?<br>
            </div>
          </div>
        </div>
      </div>
    </blockquote>
    yes. There are two humidity models. The simpler of the two is the
    effective moisture capacitance model. Type56 computes the quantity
    of moisture that the air can absorb (based on its current conditions
    of temperature, pressure, and humidity ratio), then multiplies that
    quantity by the user-specified multiplier to determine the zone's
    actual ability to absorb moisture.<br>
    <blockquote
cite="mid:0E4A4C480F9D464096C8B3D7861BE6A924C064AE@SIXPRD0111MB394.apcprd01.prod.exchangelabs.com"
      type="cite">
      <div style="direction: ltr;font-family: Tahoma;color:
        #000000;font-size: 10pt;">
        <div style="font-family: Times New Roman; color: #000000;
          font-size: 16px">
          <div>
            <div style="direction:ltr; font-family:Tahoma;
              color:#000000; font-size:10pt">
              3) Where the moisture actually goes to in my model as i
              have a schedule running. <br>
            </div>
          </div>
        </div>
      </div>
    </blockquote>
    I am not sure I understand your question; humidity gains go into the
    zone's air node. <br>
    <blockquote
cite="mid:0E4A4C480F9D464096C8B3D7861BE6A924C064AE@SIXPRD0111MB394.apcprd01.prod.exchangelabs.com"
      type="cite">
      <div style="direction: ltr;font-family: Tahoma;color:
        #000000;font-size: 10pt;">
        <div style="font-family: Times New Roman; color: #000000;
          font-size: 16px">
          <div>
            <div style="direction:ltr; font-family:Tahoma;
              color:#000000; font-size:10pt">
              3) I would also like to have a positive pressure inside
              the space, how may i go about doing this?
              <br>
            </div>
          </div>
        </div>
      </div>
    </blockquote>
    Type56 assumes that the air in the building is at 1atm; there is no
    way to change that assumption as far as I am aware.<br>
    <br>
    Best,<br>
     David<br>
    <br>
    <pre class="moz-signature" cols="72">-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI  53703 USA

P:+1.608.274.2577
F:+1.608.278.1475
<a class="moz-txt-link-abbreviated" href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>

<a class="moz-txt-link-freetext" href="http://www.tess-inc.com">http://www.tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.trnsys.com">http://www.trnsys.com</a></pre>
  </body>
</html>