<div dir="ltr">Hey David, i saw that there is a Type 177 that was used by IEA - SHC task 25. This model is freely available at <a href="http://www.eta.tu-berlin.de">www.eta.tu-berlin.de</a>, however the author at this site doesn't give the source code of the model. I realized that one of the four options under this type was specifically developed for Yazaki model WFC 10, the exact chiller model i am simulating. He suggests that we can get the source code from from <a href="http://www.iea-shc-task25.com">www.iea-shc-task25.com</a>, but i checked this source and it so happened that source code link is nolonger available since 2009. Could you be having an idea of how i can get this source code??? thanks<br>
<br>Best regards<br>Martin  <br><br><div class="gmail_quote">On Wed, Dec 19, 2012 at 8:34 PM,  <span dir="ltr"><<a href="mailto:trnsys-users-request@cae.wisc.edu" target="_blank">trnsys-users-request@cae.wisc.edu</a>></span> wrote:<br>
<blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex">Send TRNSYS-users mailing list submissions to<br>
        <a href="mailto:trnsys-users@cae.wisc.edu">trnsys-users@cae.wisc.edu</a><br>
<br>
To subscribe or unsubscribe via the World Wide Web, visit<br>
        <a href="https://mailman.cae.wisc.edu/listinfo/trnsys-users" target="_blank">https://mailman.cae.wisc.edu/listinfo/trnsys-users</a><br>
or, via email, send a message with subject or body 'help' to<br>
        <a href="mailto:trnsys-users-request@cae.wisc.edu">trnsys-users-request@cae.wisc.edu</a><br>
<br>
You can reach the person managing the list at<br>
        <a href="mailto:trnsys-users-owner@cae.wisc.edu">trnsys-users-owner@cae.wisc.edu</a><br>
<br>
When replying, please edit your Subject line so it is more specific<br>
than "Re: Contents of TRNSYS-users digest..."<br>
<br>Today's Topics:<br>
<br>
   1. Re: Yazaki chiller unit model (David BRADLEY)<br>
   2. Re: Defining transparent wall (David BRADLEY)<br>
   3. Re: building simulation (David BRADLEY)<br>
<br><br>---------- Forwarded message ----------<br>From: David BRADLEY <<a href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>><br>To: Martin Ssembatya <<a href="mailto:mssembatya@gmail.com">mssembatya@gmail.com</a>><br>
Cc: <a href="mailto:trnsys-users@cae.wisc.edu">trnsys-users@cae.wisc.edu</a><br>Date: Wed, 19 Dec 2012 11:05:01 -0600<br>Subject: Re: [TRNSYS-users] Yazaki chiller unit model<br>
  
    
  
  <div text="#000000" bgcolor="#FFFFFF">
    Martin,<br>
      I would recommend that you make a very simple project where the
    chiller is subject to a known constant load with known constant
    outdoor conditions. Hook up a Type65 online plotter to the chiller
    and take a look at its performance under these known conditions;
    once the model looks up the performance data in the data file, its
    computations are really quite simplistic. You can verify them by
    hand using the documentation in the 04-Mathematical Reference. This
    will give you some confidence in your model.<br>
    <br>
      One of the issues that often occurs in modeling absorption
    chillers is that if you compute a building load and pass it directly
    to the chiller then the chiller spends a lot of its time running at
    a very very low part load. In reality, a chiller can't operate much
    below 20% capacity so you have to make sure that this is reflected
    in the data file. The data file should have near zero capacity and
    near zero fraction of design energy input below about 20% PLR (part
    load ratio). At one time, I think there was an error in the Type107
    example data file that showed too large a capacity at very low PLR.
    The more correct way to model the system would be to place the
    chiller on its own primary loop and to place the load on a secondary
    loop. The loops can be separated by a thermal storage tank whose
    volume is equal to the volume of the primary and secondary loops.
    The chiller operates to keep the primary loop cold and the secondary
    loop draws off only as much as it needs to meet the load.<br>
    Kind regards,<br>
     David<br>
    <br>
    <br>
    <br>
    <div>On 12/19/2012 01:51, Martin Ssembatya
      wrote:<br>
    </div>
    <blockquote type="cite">
      <div dir="ltr">
        <div>Hello there,</div>
        <div> </div>
        <div>I have been modelling a solar ooling system that uses one
          of the YAazaki chiller models. I used type 107 for the
          modelling of the absorption chiller partly because i did not
          have satisfactory chiller performance data from the
          manufacturer to model the chiller unit, but alos because i did
          not have enough time and compiling language to create my own
          model for this chiller. <i>But on using type 107 for this
            purpose, i am not getting satifactory results from my
            simulation i.e. the chilling energy is always too low
            compared to the rated capacity of the chiller regardless of
            the season of the year, including summer periods with high
            insolation values. Is there any one who could have created a
            TRNSYS model for any Yazaki absorption chiller unit? If yes,
            can you kindly help me with that model you created and to
            use it in my simulation and see its effect on results. I
            will be very grateful. </i></div>
        <div><i></i> </div>
        <div>Best regards</div>
        <div>Martin</div>
      </div>
      <br>
      <fieldset></fieldset>
      <br>
      <pre>_______________________________________________
TRNSYS-users mailing list
<a href="mailto:TRNSYS-users@cae.wisc.edu" target="_blank">TRNSYS-users@cae.wisc.edu</a>
<a href="https://mailman.cae.wisc.edu/listinfo/trnsys-users" target="_blank">https://mailman.cae.wisc.edu/listinfo/trnsys-users</a>
</pre>
    </blockquote>
    <br>
    <pre cols="72">-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI  53703 USA

P:+1.608.274.2577
F:+1.608.278.1475
<a href="mailto:d.bradley@tess-inc.com" target="_blank">d.bradley@tess-inc.com</a>

<a href="http://www.tess-inc.com" target="_blank">http://www.tess-inc.com</a>
<a href="http://www.trnsys.com" target="_blank">http://www.trnsys.com</a></pre>
  </div>

<br><br>---------- Forwarded message ----------<br>From: David BRADLEY <<a href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>><br>To: Martin Ssembatya <<a href="mailto:mssembatya@gmail.com">mssembatya@gmail.com</a>><br>
Cc: <a href="mailto:trnsys-users@cae.wisc.edu">trnsys-users@cae.wisc.edu</a><br>Date: Wed, 19 Dec 2012 11:14:23 -0600<br>Subject: Re: [TRNSYS-users] Defining transparent wall<br>
  
    
  
  <div text="#000000" bgcolor="#FFFFFF">
    Martin,<br>
      A few years back, I was faced with modeling some greenhouses that
    were covered by a plastic film. I ended up modeling them as a window
    in Type56 and worked a lot in LBNL's WINDOW5 software to create a
    glazing system that represented the plastic film. The process was no
    different from creating any other new window for TRNBuild/Type56. I
    wasn't entirely happy with the solution in part because of the
    diffusion of the incoming solar caused by the plastic. However, it
    was the best I could do at the time and the results were 
    defensible. At the time, I also looked for (and found) some models
    of actual greenhouses that people had developed. None of them suited
    the project very well but that might be a good avenue to pursue as
    well.<br>
    Kind regards,<br>
     David<br>
    <br>
    <br>
    <div>On 12/12/2012 02:26, Martin Ssembatya
      wrote:<br>
    </div>
    <blockquote type="cite">
      <div dir="ltr">Hello there,<br>
        <br>
        I am using TRNSYS 16 to estimate the total cooling requirement
        of three temporally built structures. One of the structures is a
        tent whose vertical walls contain like 50 percent plastic
        transparent parts. How can i create a layer and define it to be
        transparent to the incoming radiation?? I know that this must be
        having a huge effect on the total cooling requirement. Can
        someone please help me with some ideas how this can be done?!<br>
        <br>
        Thanks <br>
        Martin<br>
      </div>
      <br>
      <fieldset></fieldset>
      <br>
      <pre>_______________________________________________
TRNSYS-users mailing list
<a href="mailto:TRNSYS-users@cae.wisc.edu" target="_blank">TRNSYS-users@cae.wisc.edu</a>
<a href="https://mailman.cae.wisc.edu/listinfo/trnsys-users" target="_blank">https://mailman.cae.wisc.edu/listinfo/trnsys-users</a>
</pre>
    </blockquote>
    <br>
    <pre cols="72">-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI  53703 USA

P:+1.608.274.2577
F:+1.608.278.1475
<a href="mailto:d.bradley@tess-inc.com" target="_blank">d.bradley@tess-inc.com</a>

<a href="http://www.tess-inc.com" target="_blank">http://www.tess-inc.com</a>
<a href="http://www.trnsys.com" target="_blank">http://www.trnsys.com</a></pre>
  </div>

<br><br>---------- Forwarded message ----------<br>From: David BRADLEY <<a href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>><br>To: Matthias Maier <<a href="mailto:matthiasmaier90@googlemail.com">matthiasmaier90@googlemail.com</a>><br>
Cc: <a href="mailto:trnsys-users@cae.wisc.edu">trnsys-users@cae.wisc.edu</a><br>Date: Wed, 19 Dec 2012 11:34:53 -0600<br>Subject: Re: [TRNSYS-users] building simulation<br>
  
    
  
  <div text="#000000" bgcolor="#FFFFFF">
    Matthias,<br>
      I think the answer would depend a lot on the complexity of the
    HVAC systems and on the level of detail to which you would need to
    model them. The most comprehensive building models that I have done
    are for LEED projects (proposed building, proposed mechanical
    system, baseline (comparison) building, baseline (comparison) HVAC
    system, and lots of report writing). These projects can range from
    70 to 200 hours of time with most coming in around 100 to 150.
    Again, though, that is modeling two buildings. To model just the one
    proposed building, I think you would probably be in the range of 50
    to 150 hours.<br>
    <br>
      Some other thoughts for you, though (which I realize you didn't
    request... ;-)   ). Every model, every building simulation tool that
    is out there is some simplification of a real process. The more
    assumptions the model developer builds into the model, the simpler
    the model is to implement but the less flexible it becomes. The
    fewer assumptions that the developer builds in, the more flexible
    the tool but the more complexity there is involved with implementing
    a system model. I have found it helpful to think of building energy
    modeling tools on a sliding scale where on one end are tools that
    are relatively quick to use, which have a LOT of built-in
    assumptions and which are therefore not very flexible. One the other
    end are tools that are very flexible in terms of what you can model
    but which are more time consuming to use. TRNSYS is definitely on
    the "flexible but complex" end of that scale - intentionally so. If
    you are trying to model a building that has some unusual features
    (radiant floors, natural ventilation, double skin facades, complex
    HVAC systems, etc.) in it then TRNSYS is a good tool to use, even
    though it will require more hours to implement the model. If the
    building has nothing but conventional envelope and systems then
    there is no advantage to TRNSYS (or other tools like it); you will
    spend an unnecessarily long time implementing the model. On the
    other hand, it may be quick to implement a model in another software
    but if the building has features that cannot be modeled by the other
    software, you need to change to another, more comprehensive or
    flexible tool.<br>
    <br>
    Best,<br>
     David<br>
    <br>
    <div><br>
      <br>
      <br>
      On 12/12/2012 09:30, Matthias Maier wrote:<br>
    </div>
    <blockquote type="cite">Hi TRNSYS-users,<br>
      <br>
      <div>I am studying electrical engineering at the Technical
        University of Munich and currently I am writing my bachelor´s
        thesis at the Institute for Energy Economy and Application
        Technology. My subject is the comparison and assessment of
        various building simulation programs. Background of this thesis
        is the development of an automatized demand side management for
        commercial buildings, in case of the emergence of a dynamic
        electricity tariff in Germany. Therefor a whole thermal
        simulation of the building and it´s HVAC systems would be
        necessary.<br>
      </div>
      <br>
      One of my tasks is to estimate the costs for the implementation of
      a building including its HVAC systems. For this reason I selected
      an example building to estimate the costs for (added in the
      attachment). Support referred me to this user service. I would be
      very grateful if anyone could tell me how long it takes to
      implement this example building including its HVAC to TRNSYS and
      perform a high-resolution simulation (minute-basis) for a
      eperienced user. 
      <div>
        <br>
      </div>
      <div>Thank you for your attention.</div>
      <div><br>
      </div>
      <div>Regards,</div>
      <div>Matthias Maier</div>
      <br>
      <fieldset></fieldset>
      <br>
      <pre>_______________________________________________
TRNSYS-users mailing list
<a href="mailto:TRNSYS-users@cae.wisc.edu" target="_blank">TRNSYS-users@cae.wisc.edu</a>
<a href="https://mailman.cae.wisc.edu/listinfo/trnsys-users" target="_blank">https://mailman.cae.wisc.edu/listinfo/trnsys-users</a>
</pre>
    </blockquote>
    <br>
    <pre cols="72">-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI  53703 USA

P:+1.608.274.2577
F:+1.608.278.1475
<a href="mailto:d.bradley@tess-inc.com" target="_blank">d.bradley@tess-inc.com</a>

<a href="http://www.tess-inc.com" target="_blank">http://www.tess-inc.com</a>
<a href="http://www.trnsys.com" target="_blank">http://www.trnsys.com</a></pre>
  </div>

<br>_______________________________________________<br>
TRNSYS-users mailing list<br>
<a href="mailto:TRNSYS-users@cae.wisc.edu">TRNSYS-users@cae.wisc.edu</a><br>
<a href="https://mailman.cae.wisc.edu/listinfo/trnsys-users" target="_blank">https://mailman.cae.wisc.edu/listinfo/trnsys-users</a><br>
<br></blockquote></div><br></div>