    Martin,<br>
      I would recommend that you make a very simple project where the
    chiller is subject to a known constant load with known constant
    outdoor conditions. Hook up a Type65 online plotter to the chiller
    and take a look at its performance under these known conditions;
    once the model looks up the performance data in the data file, its
    computations are really quite simplistic. You can verify them by
    hand using the documentation in the 04-Mathematical Reference. This
    will give you some confidence in your model.<br>
    <br>
      One of the issues that often occurs in modeling absorption
    chillers is that if you compute a building load and pass it directly
    to the chiller then the chiller spends a lot of its time running at
    a very very low part load. In reality, a chiller can't operate much
    below 20% capacity so you have to make sure that this is reflected
    in the data file. The data file should have near zero capacity and
    near zero fraction of design energy input below about 20% PLR (part
    load ratio). At one time, I think there was an error in the Type107
    example data file that showed too large a capacity at very low PLR.
    The more correct way to model the system would be to place the
    chiller on its own primary loop and to place the load on a secondary
    loop. The loops can be separated by a thermal storage tank whose
    volume is equal to the volume of the primary and secondary loops.
    The chiller operates to keep the primary loop cold and the secondary
    loop draws off only as much as it needs to meet the load.<br>
    Kind regards,<br>
     David<br>
    <br>
    <br>
    <br>
    <div class="moz-cite-prefix">On 12/19/2012 01:51, Martin Ssembatya
      wrote:<br>
    </div>
    <blockquote
cite="mid:CAOVnU7sDw274AtKQSsHc1+KXaaiPtUfhJgrATEmbMh-T1dW6tg@mail.gmail.com"
      type="cite">
      <div dir="ltr">
        <div>Hello there,</div>
        <div> </div>
        <div>I have been modelling a solar ooling system that uses one
          of the YAazaki chiller models. I used type 107 for the
          modelling of the absorption chiller partly because i did not
          have satisfactory chiller performance data from the
          manufacturer to model the chiller unit, but alos because i did
          not have enough time and compiling language to create my own
          model for this chiller. <em>But on using type 107 for this
            purpose, i am not getting satifactory results from my
            simulation i.e. the chilling energy is always too low
            compared to the rated capacity of the chiller regardless of
            the season of the year, including summer periods with high
            insolation values. Is there any one who could have created a
            TRNSYS model for any Yazaki absorption chiller unit? If yes,
            can you kindly help me with that model you created and to
            use it in my simulation and see its effect on results. I
            will be very grateful. </em></div>
        <div><em></em> </div>
        <div>Best regards</div>
        <div>Martin</div>
      </div>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <br>
      <pre wrap="">_______________________________________________
TRNSYS-users mailing list
<a class="moz-txt-link-abbreviated" href="mailto:TRNSYS-users@cae.wisc.edu">TRNSYS-users@cae.wisc.edu</a>
<a class="moz-txt-link-freetext" href="https://mailman.cae.wisc.edu/listinfo/trnsys-users">https://mailman.cae.wisc.edu/listinfo/trnsys-users</a>
</pre>
    </blockquote>
    <br>
    <pre class="moz-signature" cols="72">-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI  53703 USA

P:+1.608.274.2577
F:+1.608.278.1475
<a class="moz-txt-link-abbreviated" href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>

<a class="moz-txt-link-freetext" href="http://www.tess-inc.com">http://www.tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.trnsys.com">http://www.trnsys.com</a></pre>
  </body>
</html>