    <div class="moz-cite-prefix">David,<br>
      thanks for this fast reply. Since I connected the pressure as well
      (don´t know how i could miss this) there are no more warnings due
      to psychometrics. Just at the end there´s one warning left, which
      doesn´t sound good:<br>
      <br>
      <i>*** Warning at time       :      8760.000000</i><i><br>
      </i><i>    Generated by Unit     :     6</i><i><br>
      </i><i>    Generated by Type     :   112</i><i><br>
      </i><i>    Message               : Fan mass balance failed during
        35040 timesteps. Please check the connections.</i><br>
      <br>
      Do you have any idea what in detail could be wrong ? I made the
      connections for dry bulb, humidity and pressure. <br>
      <br>
      Thanks in advance!<br>
      Best,<br>
      Michael <br>
      <br>
      <br>
      <br>
      <br>
      Am 12/3/2012 6:39 PM, schrieb David BRADLEY:<br>
    </div>
    <blockquote cite="mid:50BCE3D1.6090508@tess-inc.com" type="cite">
      <meta content="text/html; charset=ISO-8859-1"
        http-equiv="Content-Type">
      Michael,<br>
        You need to connect the pressure as well. It is surprising that
      you always get the warning. I would understand if you get that
      warning for some timesteps (maybe even enough timesteps to go over
      the allowable number of warnings in a simulation. However, if you
      get that warning at every single timestep, there might be
      something else wrong.<br>
      Regards,<br>
       David<br>
      <br>
      <br>
      <div class="moz-cite-prefix">On 12/3/2012 05:39, Michael Diekerhof
        wrote:<br>
      </div>
      <blockquote
cite="mid:trinity-a9d1d262-dda8-4b33-b262-3defa7db93eb-1354534798680@3capp-webde-bs27"
        type="cite">
        <div style="font-family: Verdana;font-size: 12.0px;">
          <div>Dear all,<br>
          </div>
          <div><br>
          </div>
          <div>I´m using type 112 as a fan for an air-Source heat pump
            (type401). <br>
          </div>
          <div><br>
          </div>
          <div>Between Type 15(weather) and type 112 i made the
            following connections:<br>
          </div>
          <div><br>
          </div>
          <div>Dry bulb temperature => Inlet temperature<br>
          </div>
          <div>Humity ratio => Inlet air humidity ratio<br>
          </div>
          <div><br>
          </div>
          <div>But unfortunetaly I do always receive the following
            warning which results in an Error:<br>
          </div>
          <div><br>
          </div>
          <div><em>"The referenced UNIT has called the PSYCHROMETRICS
              routine witha humidity ratio above the saturation humidity
              ratio for the given dry bulb temperature. <br>
            </em></div>
          <div><em>The air was assumed saturated at the given dry bulb
              temperature and the humidity ratio set for this condition</em>"<br>
          </div>
          <div><br>
          </div>
          <div>Does anyone has a suggestion to solve this problem ?? I
            appreciate any idea :)<br>
          </div>
          <div><br>
          </div>
          <div>Best,<br>
            Michael <br>
          </div>
        </div>
        <br>
        <fieldset class="mimeAttachmentHeader"></fieldset>
        <br>
        <pre wrap="">_______________________________________________
TRNSYS-users mailing list
<a moz-do-not-send="true" class="moz-txt-link-abbreviated" href="mailto:TRNSYS-users@cae.wisc.edu">TRNSYS-users@cae.wisc.edu</a>
<a moz-do-not-send="true" class="moz-txt-link-freetext" href="https://mailman.cae.wisc.edu/listinfo/trnsys-users">https://mailman.cae.wisc.edu/listinfo/trnsys-users</a>
</pre>
      </blockquote>
      <br>
      <pre class="moz-signature" cols="72">-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI  53703 USA

P:+1.608.274.2577
F:+1.608.278.1475
<a moz-do-not-send="true" class="moz-txt-link-abbreviated" href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>

<a moz-do-not-send="true" class="moz-txt-link-freetext" href="http://www.tess-inc.com">http://www.tess-inc.com</a>
<a moz-do-not-send="true" class="moz-txt-link-freetext" href="http://www.trnsys.com">http://www.trnsys.com</a></pre>
    </blockquote>
    <br>
  </body>
</html>