    Prof Sommer,<br>
      For the case of no fins (ie no contact resistance) and no
    pipe-in-pipe configuration, parameters 41 and 42 have the same
    value; that of the thermal conductivity of the heat exchanger
    material (copper probably). Type60 does not decrease the volume of
    the nodes by the fluid volume occupied by the heat exchanger. It
    assumes that the heat exchanger volume is small in comparison to the
    tank volume. The storage tank in the TESS Storage library does
    remove the volume of the heat exchanger from the volume of each tank
    node and may be more appropriate for tanks that contain large heat
    exchangers.<br>
    Kind regards,<br>
     David<br>
     <br>
    <br>
    <div class="moz-cite-prefix">On 11/24/2012 04:41, Prof K Sommer
      wrote:<br>
    </div>
    <blockquote cite="mid:50B0A474.9070101@fh-koeln.de" type="cite">Hi,
      <br>
      <br>
      I try to simulate the buffer tank, details of that are attached,
      with type 60 in TRNSYS 16.
      <br>
      My questions to the parameters 41 and 42:
      <br>
      What exactly covers "Heat exchanger wall conductivity" and what
      would be the right input value for this parameter if there is only
      a single pipe hx without fins and without pipe-in-pipe solution?
      <br>
      And how does the model handle the 60 liter water volume inside the
      pipe hx from time step to time step if the DHW usage is every hour
      at the
      <br>
      beginning around 30 to 50 liter per min.?
      <br>
      <br>
      Many thanks in advance.
      <br>
      <br>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <br>
      <pre wrap="">_______________________________________________
TRNSYS-users mailing list
<a class="moz-txt-link-abbreviated" href="mailto:TRNSYS-users@cae.wisc.edu">TRNSYS-users@cae.wisc.edu</a>
<a class="moz-txt-link-freetext" href="https://mailman.cae.wisc.edu/listinfo/trnsys-users">https://mailman.cae.wisc.edu/listinfo/trnsys-users</a>
</pre>
    </blockquote>
    <br>
    <pre class="moz-signature" cols="72">-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI  53703 USA
P:+1.608.274.2577
F:+1.608.278.1475
<a class="moz-txt-link-abbreviated" href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.tess-inc.com">http://www.tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.trnsys.com">http://www.trnsys.com</a></pre>
  </body>
</html>