Dear Benoit,<br><br>Thanks for your patient reply!<br>I saw your attached figure. But there is a new problem. As I said for my first email, my air layer is about 1m, however, this figure's maximal thickness of air is only 300 mm. therefore, Whether or not it is right when I still use 4.5 W/m2K your figure said as the air layer's U-value?<br>
<br>thanks!<br>Br.<br><br>yang wang<br><br><div class="gmail_quote">2012/11/21 Benoit Delcroix <span dir="ltr"><<a href="mailto:benoit.delcroix@polymtl.ca" target="_blank">benoit.delcroix@polymtl.ca</a>></span><br><blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex">
  
    
  
  <div text="#000000" bgcolor="#FFFFFF">
    <div>Hi, <br>
      <br>
      The new value is including convection, radiation and conduction
      (and not only conduction). There is a reference in English in 2009
      ASHRAE Handbook - fundamentals (chapter 26). The reference I have
      is in French (a Belgian regulation on energy performance of
      buildings). I have attached a jpg file with the table if you want.
      The first column is the thickness (in mm). The 3 next are
      depending on the heat flux direction (respectively upward,
      horizontal and downward). And the values in the table are
      resistances in m²K/W. The reference in ASHRAE is a little bit more
      complicated. <br>
      <br>
      Best,<br>
      <br>
      Benoit<br>
      <br>
      Le 2012-11-21 04:27, 王洋 a écrit :<br>
    </div><div><div class="h5">
    <blockquote type="cite">Dear Benoit,<br>
      <br>
      Thanks for your reply!<br>
      <br>
      I did as you said, i.e. I changed the air U-value from 0.09252
      W/m2K into 4.65 W/m2K. Then the min. timebase 2 hours can work.
      But I'd like to ask you why we should set this value 4.65 W/m2K?
      Could you please tell me which reference literature said? Because
      I checked the air conductivity as 0.09252 kJ/hmK from the
      literature.<br>
      <br>
      Thanks!<br>
      Br.<br>
      yang wang<br>
      <br>
      <div class="gmail_quote">2012/11/20 Benoit Delcroix <span dir="ltr"><<a href="mailto:benoit.delcroix@polymtl.ca" target="_blank">benoit.delcroix@polymtl.ca</a>></span><br>
        <blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex">
          <div text="#000000" bgcolor="#FFFFFF">
            <div>Hello,<br>
              <br>
              To me, I think you should set your air layer as a
              resistive layer and set the air U-value to 4.55 - 4.65
              W/(m²K) (if there is no ventilation in the basement). And
              normally, afterwards, you should be able to decrease the
              timebase value (normally 1 hour should be possible). If
              you want less, split the heaviest walls with an active
              layer (probably the roof and groundfloor walls).<br>
              <br>
              Best,<br>
              <br>
              Benoit   <br>
              <br>
              Le 2012-11-19 04:31, 王洋 a écrit :<br>
            </div>
            <div>
              <div>
                <blockquote type="cite"><br>
                  Dear Leen, Jean, Marion, Benoit and others,<br>
                  <br>
                  Many thanks for your reply!<br>
                  <br>
                  I checked my Wall's thickness and thermal property
                  etc. again. Why needs it 9 hours as the timebase? I
                  think maybe it is due to my Ground floor (it is the
                  basement's floor of the building) which includes about
                  0.99 m's Air Layer.<br>
                  When I changed it into 0.1 m, the min. timebase 2.5
                  hours can work without the ERROR:Error creating the
                  wall transfer function coeffients.<br>
                  <br>
                  Therefore, I'd like to ask you, <br>
                  1) Is it normal for TRNBuild setting how large the
                  timebase is maximally? 5 hours or others?<br>
                  2) How to solve this problem of the ground floor with
                  about 0.99 m's Air Layer? But our building project
                  indeed has<br>
                  the ground floor with about 0.99 m's Air Layer. I
                  can't reduce it into 0.1m? Is the only way to <span style="color:rgb(51,51,255)"> try the active layer
                    approach of The group of Michael Kummert in Montreal</span>?
                    <br>
                  <br>
                  Please see the Attached INF file.<br>
                  <br>
                  Thanks in advance!<br>
                  Br.<br>
                  <br>
                  wang<br>
                  <br>
                  <br>
                  <div class="gmail_quote">2012/11/17 Benoit Delcroix <span dir="ltr"><<a href="mailto:benoit.delcroix@polymtl.ca" target="_blank">benoit.delcroix@polymtl.ca</a>></span><br>
                    <blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex">
                      <div text="#000000" bgcolor="#FFFFFF">
                        <div>Hello,<br>
                          <br>
                          I'm one of the students of Michaël Kummert
                          working on a new method to generate the
                          tranfer functions. I thing I can help you for
                          your problem. As Leen said, TRNSYS is unable
                          to generate the transfer functions
                          coefficients for a heavy and insulated wall
                          with a low timebase. In the TRNBuild project,
                          you can modify that value and increase it to
                          allow TRNSYS to generate the transfer
                          functions. Actually, TRNSYS is unable to
                          generate the transfer function as soon as the
                          Fourier number of the wall (thermal
                          diffusivity * timebase / thhickness²) is lower
                          than 0.0005. To check that, TRNBuild make the
                          sum of one of the coefficients series (a, b or
                          c). The 3 sums are equal and means, according
                          to TRNBuild (I don't personally think so...but
                          it's like this), the Fourier number. <br>
                          <br>
                          As Leen said, it exists a trick. You can use
                          an active layer to split the wall in 2 and
                          then forcing TRNSYS to generate 2 series of
                          transfer functions coefficients for the same
                          wall. As the 2 parts are thinner, you could
                          use a better timebase value. When you insert
                          the active layer in the wall, try to split the
                          layer with the lowest Fourier number. And then
                          to insert the active layer, use the expert
                          mode that allows you to insert an equivalent
                          conductivity. Insert the biggest value you
                          can. Like that, the active layer is negligible
                          at the thermal point of view. Actually, the
                          active layer is acting as a mini-zone to split
                          the wall. It is a little tricky but it
                          works...before having better solution.<br>
                          <br>
                          Good luck for your project and have a nice
                          week-end,<br>
                          <br>
                          Benoit   <br>
                          <br>
                          Le 2012-11-17 14:43, <a href="mailto:trnsys-users-request@cae.wisc.edu" target="_blank">trnsys-users-request@cae.wisc.edu</a>
                          a écrit :<br>
                        </div>
                        <blockquote type="cite">
                          <div>
                            <div>
                              <pre>Send TRNSYS-users mailing list submissions to
        <a href="mailto:trnsys-users@cae.wisc.edu" target="_blank">trnsys-users@cae.wisc.edu</a>
To subscribe or unsubscribe via the World Wide Web, visit
        <a href="https://mailman.cae.wisc.edu/listinfo/trnsys-users" target="_blank">https://mailman.cae.wisc.edu/listinfo/trnsys-users</a>
or, via email, send a message with subject or body 'help' to
        <a href="mailto:trnsys-users-request@cae.wisc.edu" target="_blank">trnsys-users-request@cae.wisc.edu</a>
You can reach the person managing the list at
        <a href="mailto:trnsys-users-owner@cae.wisc.edu" target="_blank">trnsys-users-owner@cae.wisc.edu</a>
When replying, please edit your Subject line so it is more specific
than "Re: Contents of TRNSYS-users digest..."
</pre>
                              <br>
                              <fieldset></fieldset>
                              <br>
                            </div>
                          </div>
                          <pre>Today's Topics:
   1. Re: Fwd: Error creating the wall transfer function        coeffients
      (leen peeters)
</pre>
                          <br>
                          <fieldset></fieldset>
                          <br>
                          <pre>_______________________________________________
TRNSYS-users mailing list
<a href="mailto:TRNSYS-users@cae.wisc.edu" target="_blank">TRNSYS-users@cae.wisc.edu</a>
<a href="https://mailman.cae.wisc.edu/listinfo/trnsys-users" target="_blank">https://mailman.cae.wisc.edu/listinfo/trnsys-users</a>