Dear Benoit,<br><br>Thanks for your reply!<br><br>I did as you said, i.e. I changed the air U-value from 0.09252 W/m2K into 4.65 W/m2K. Then the min. timebase 2 hours can work. But I'd like to ask you why we should set this value  4.65 W/m2K? Could you please tell me which reference literature said? Because I checked the air conductivity as 0.09252 kJ/hmK from the literature.<br>
<br>Thanks!<br>Br.<br>yang wang<br><br><div class="gmail_quote">2012/11/20 Benoit Delcroix <span dir="ltr"><<a href="mailto:benoit.delcroix@polymtl.ca" target="_blank">benoit.delcroix@polymtl.ca</a>></span><br><blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex">

  
    
  
  <div text="#000000" bgcolor="#FFFFFF">
    <div>Hello,<br>
      <br>
      To me, I think you should set your air layer as a resistive layer
      and set the air U-value to 4.55 - 4.65 W/(m²K) (if there is no
      ventilation in the basement). And normally, afterwards, you should
      be able to decrease the timebase value (normally 1 hour should be
      possible). If you want less, split the heaviest walls with an
      active layer (probably the roof and groundfloor walls).<br>
      <br>
      Best,<br>
      <br>
      Benoit   <br>
      <br>
      Le 2012-11-19 04:31, 王洋 a écrit :<br>
    </div><div><div class="h5">
    <blockquote type="cite"><br>
      Dear Leen, Jean, Marion, Benoit and others,<br>
      <br>
      Many thanks for your reply!<br>
      <br>
      I checked my Wall's thickness and thermal property etc. again. Why
      needs it 9 hours as the timebase? I think maybe it is due to my
      Ground floor (it is the basement's floor of the building) which
      includes about 0.99 m's Air Layer.<br>
      When I changed it into 0.1 m, the min. timebase 2.5 hours can work
      without the ERROR:Error creating the wall transfer function
      coeffients.<br>
      <br>
      Therefore, I'd like to ask you, <br>
      1) Is it normal for TRNBuild setting how large the timebase is
      maximally? 5 hours or others?<br>
      2) How to solve this problem of the ground floor with about 0.99
      m's Air Layer? But our building project indeed has<br>
      the ground floor with about 0.99 m's Air Layer. I can't reduce it
      into 0.1m? Is the only way to <span style="color:rgb(51,51,255)">
        try the active layer approach of The group of Michael Kummert in
        Montreal</span>?   <br>
      <br>
      Please see the Attached INF file.<br>
      <br>
      Thanks in advance!<br>
      Br.<br>
      <br>
      wang<br>
      <br>
      <br>
      <div class="gmail_quote">2012/11/17 Benoit Delcroix <span dir="ltr"><<a href="mailto:benoit.delcroix@polymtl.ca" target="_blank">benoit.delcroix@polymtl.ca</a>></span><br>
        <blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex">
          <div text="#000000" bgcolor="#FFFFFF">
            <div>Hello,<br>
              <br>
              I'm one of the students of Michaël Kummert working on a
              new method to generate the tranfer functions. I thing I
              can help you for your problem. As Leen said, TRNSYS is
              unable to generate the transfer functions coefficients for
              a heavy and insulated wall with a low timebase. In the
              TRNBuild project, you can modify that value and increase
              it to allow TRNSYS to generate the transfer functions.
              Actually, TRNSYS is unable to generate the transfer
              function as soon as the Fourier number of the wall
              (thermal diffusivity * timebase / thhickness²) is lower
              than 0.0005. To check that, TRNBuild make the sum of one
              of the coefficients series (a, b or c). The 3 sums are
              equal and means, according to TRNBuild (I don't personally
              think so...but it's like this), the Fourier number. <br>
              <br>
              As Leen said, it exists a trick. You can use an active
              layer to split the wall in 2 and then forcing TRNSYS to
              generate 2 series of transfer functions coefficients for
              the same wall. As the 2 parts are thinner, you could use a
              better timebase value. When you insert the active layer in
              the wall, try to split the layer with the lowest Fourier
              number. And then to insert the active layer, use the
              expert mode that allows you to insert an equivalent
              conductivity. Insert the biggest value you can. Like that,
              the active layer is negligible at the thermal point of
              view. Actually, the active layer is acting as a mini-zone
              to split the wall. It is a little tricky but it
              works...before having better solution.<br>
              <br>
              Good luck for your project and have a nice week-end,<br>
              <br>
              Benoit   <br>
              <br>
              Le 2012-11-17 14:43, <a href="mailto:trnsys-users-request@cae.wisc.edu" target="_blank">trnsys-users-request@cae.wisc.edu</a> a
              écrit :<br>
            </div>
            <blockquote type="cite">
              <div>
                <div>
                  <pre>Send TRNSYS-users mailing list submissions to
        <a href="mailto:trnsys-users@cae.wisc.edu" target="_blank">trnsys-users@cae.wisc.edu</a>

To subscribe or unsubscribe via the World Wide Web, visit
        <a href="https://mailman.cae.wisc.edu/listinfo/trnsys-users" target="_blank">https://mailman.cae.wisc.edu/listinfo/trnsys-users</a>
or, via email, send a message with subject or body 'help' to
        <a href="mailto:trnsys-users-request@cae.wisc.edu" target="_blank">trnsys-users-request@cae.wisc.edu</a>

You can reach the person managing the list at
        <a href="mailto:trnsys-users-owner@cae.wisc.edu" target="_blank">trnsys-users-owner@cae.wisc.edu</a>

When replying, please edit your Subject line so it is more specific
than "Re: Contents of TRNSYS-users digest..."
</pre>
                  <br>
                  <fieldset></fieldset>
                  <br>
                </div>
              </div>
              <pre>Today's Topics:

   1. Re: Fwd: Error creating the wall transfer function        coeffients
      (leen peeters)
</pre>
              <br>
              <fieldset></fieldset>
              <br>
              <pre>_______________________________________________
TRNSYS-users mailing list
<a href="mailto:TRNSYS-users@cae.wisc.edu" target="_blank">TRNSYS-users@cae.wisc.edu</a>
<a href="https://mailman.cae.wisc.edu/listinfo/trnsys-users" target="_blank">https://mailman.cae.wisc.edu/listinfo/trnsys-users</a>
</pre>
            </blockquote>
            <br>
          </div>
        </blockquote>
      </div>
      <br>
    </blockquote>
    <br>
  </div></div></div>

</blockquote></div><br>