<html>
  <head>
    <meta content="text/html; charset=ISO-8859-1"
      http-equiv="Content-Type">
  </head>
  <body bgcolor="#FFFFFF" text="#000000">
    Martin,<br>
      A couple of pointers come to mind (and these apply to systems in
    general, not just to this particular system).<br>
    <br>
    1. There should also be a pump in the loop whose rated flow rate
    matches the hot water flow requirements of the absorption chiller.
    The pump should be controlled in the same manner as the chiller so
    that if there is no load on the chiller, both the chiller and the
    pump turn off.<br>
    <br>
    2.  There should probably be an auxiliary heating device in the loop
    (Type6 perhaps) that raises the liquid temperature going to the
    chiller in case the water in the tank was not hot enough.<br>
    <br>
    3. Most importantly, make sure that the tank is large enough to
    contain more than one timestep's worth of flow from the pump. For
    example, if your pump has a rated flow rate of 10000 kg/h and you
    are running with a 5 minute timestep, your tank needs to be more
    than 833L. If you try and run with a 1-hour timestep, you will
    almost never get convergence because the tank volume turns over more
    than once in a timestep.<br>
    Best,<br>
     David<br>
    <br>
    <br>
    <div class="moz-cite-prefix">On 10/29/2012 04:24, Martin Ssembatya
      wrote:<br>
    </div>
    <blockquote
cite="mid:CAOVnU7s=Yj06_wsCCOCV5+9UZgLgzozDZ4dEzGMCyPTRtKKfuA@mail.gmail.com"
      type="cite">
      <div dir="ltr">Hello there,<br>
        <br>
        I am carrying out ma Msc. thesis project involving simulation of
        a solar cooling system. The system contains an absorption
        chiller connected to a hot thermal storage tank that receives
        hot water from solar thermal collectors. I am finding a problem
        with making a closed loop between the absorption chiller
        (modeled with type 107) and the storage tank (modeled with type
        4a). Every time i try to connect the hot water absorption
        chiller outlet temperature as the inlet temperature of the cold
        side of the tank, the system returns unexpected errors (i.e lack
        of convergence). Am getting stuck on this. Can some one please
        help me with some information how i can go about this problem.<br>
        <br>
        Thanks in advance<br>
        <br>
        Martin <br>
      </div>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <br>
      <pre wrap="">_______________________________________________
TRNSYS-users mailing list
<a class="moz-txt-link-abbreviated" href="mailto:TRNSYS-users@cae.wisc.edu">TRNSYS-users@cae.wisc.edu</a>
<a class="moz-txt-link-freetext" href="https://mailman.cae.wisc.edu/listinfo/trnsys-users">https://mailman.cae.wisc.edu/listinfo/trnsys-users</a>
</pre>
    </blockquote>
    <br>
    <pre class="moz-signature" cols="72">-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI  53703 USA

P:+1.608.274.2577
F:+1.608.278.1475
<a class="moz-txt-link-abbreviated" href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>

<a class="moz-txt-link-freetext" href="http://www.tess-inc.com">http://www.tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.trnsys.com">http://www.trnsys.com</a></pre>
  </body>
</html>