    Michael,<br>
      The HEATING and COOLING types that are built into TRNBuild and
    Type56 are primarily used for computing the idealized heating and
    cooling loads of the space. Those loads can then be imposed on a
    system but the performance of the system is then dependent only on
    that load, not on the delivery temperature or the room temperature.
    This method of calculating system energy use is called Energy Rate
    Control. What you are aiming for in your simulation is something
    called Temperature Level Control where a themostat senses room
    temperatures and sends control signals to equipment. The equipment
    provides flows of hot or cold water and air to the delivery devices
    and the room temperatures react accordingly. The Type56 model is
    computing an energy balance on the space that reacts to the delivery
    devices. You need to get away from using the built-in idealized
    HEATING inputs and towards defining the ventilation streams, active
    layers, and energy gains that will cause the space temperature to go
    up or down. There is a tutorial available that will step you through
    the basic process of migrating from Energy Rate Control to
    Temperature Level Control. Even though it does not directly apply to
    your radiator system, I think it will help your understanding of the
    underlying concepts.<br>
    <br>
<a class="moz-txt-link-freetext" href="http://sel.me.wisc.edu/trnsys/downloads/tutorials_and_examples/tlc_tutorial17.pdf">http://sel.me.wisc.edu/trnsys/downloads/tutorials_and_examples/tlc_tutorial17.pdf</a><br>
    <br>
    Best,<br>
     David<br>
    <br>
    <br>
    <br>
    <div class="moz-cite-prefix">On 10/20/2012 08:43, Michael Diekerhof
      wrote:<br>
    </div>
    <blockquote cite="mid:5082AA97.5080803@web.de" type="cite">
      <meta content="text/html; charset=UTF-8" http-equiv="Content-Type">
      <div class="moz-cite-prefix">David,<br>
        Unfortunetaly I don´t have access to the TESS library. I´m sorry
        but I dont understand what you were meaning with: <i>"If you do
          not, then I would imagine that you might be able to come up
          with a simplified set of equations that would give you the
          gains to the space that you need. "</i><br>
        <br>
        Do you mean that I use the GAINS to adjust the radiative and
        convective part ? But how to take the room temperature into
        account by also considering the outlet temperature out of my
        storage ?? Isn´t there also a way to work with HEATING INPUTS ?!
        I still dont have an idea how to cover my heat demand by using
        the outlet temperature :( <br>
        <br>
        Best,<br>
        Michael<br>
        <br>
        <br>
        <br>
        <br>
        Am 19.10.2012 20:15, schrieb David BRADLEY:<br>
      </div>
      <blockquote cite="mid:508198CE.2070803@tess-inc.com" type="cite">Michael,

        <br>
          Ideally, you need a radiator model that will deal with the
        water side, take room temperature from Type56 and output the
        convective and radiative gains to the space as outputs. Such a
        model exists in the TESS HVAC library for Trnsys17 if you have
        access to it (Type1231). If you do not, then I would imagine
        that you might be able to come up with a simplified set of
        equations that would give you the gains to the space that you
        need. <br>
        Best, <br>
         David <br>
        <br>
        <br>
        On 10/18/2012 09:24, Michael Diekerhof wrote: <br>
        <blockquote type="cite">David, <br>
          <br>
          thanks a lot. I´ll have a look. <br>
          <br>
          Could you please help me in another case. My plan is to
          connect the HP to a storage tank and then giving a temperature
          from the storage (type4) to my type56... How can I realize
          that my type 56 can be heated to achieve a constant room
          temperature of e.g. 20°C ?! <br>
          <br>
          Someone told me that I must use HEATING and then INPUT...  but
          what if i would like to simulate a simple radiator with a
          simple inlet temperature of e.g. 55°C. <br>
          <br>
          Do you understand my problem? I dont know how to cover my heat
          demand out of the storage. <br>
          <br>
          Thanks in advance <br>
          <br>
          Best, <br>
          Michael <br>
          <br>
          <br>
          <br>
          Am 18.10.2012 16:16, schrieb David BRADLEY: <br>
          <blockquote type="cite">Michael, <br>
              I would recommend that you look online at manufacturer's
            sites for similarly sized heat pumps. Trane and Carrier both
            have significant amounts of performance data in the product
            literature parts of their sites. You can probably get a good
            estimate of the flow rates on both the condenser and
            evaporator sizes from them. <br>
            Best, <br>
             david <br>
            <br>
            <br>
            On 10/18/2012 03:53, Michael Diekerhof wrote: <br>
            <blockquote type="cite">Dear all, <br>
              <br>
              I´m working with the heat pump non-standard type 401 and
              try to display an air-source heat pump. <br>
              <br>
              I dont have typical values for the Input 2 (evaporator
              mass flowrate) and Input 4 (condenser mass flowrate). <br>
              The only real connection I´m using is the dry bulb temp,
              coming from type 15, as the evaporator inlet temperature.
              For the massflowrates I would like to assume constant
              values. <br>
              <br>
              How can I adjust an outlet condenser temperature of e.g.
              55°C. Just about the massflowrates ?! <br>
              <br>
              Does anyone have experience with heat pump mass flow
              rates?! I guess it´s not necessary to have expieriences
              with Type 401. <br>
              <br>
              I´m thankful for any advices. <br>
              <br>
              Best, <br>
              <br>
              Michael <br>
              _______________________________________________ <br>
              TRNSYS-users mailing list <br>
              <a moz-do-not-send="true" class="moz-txt-link-abbreviated"
                href="mailto:TRNSYS-users@cae.wisc.edu">TRNSYS-users@cae.wisc.edu</a>
              <br>
              <a moz-do-not-send="true" class="moz-txt-link-freetext"
                href="https://mailman.cae.wisc.edu/listinfo/trnsys-users">https://mailman.cae.wisc.edu/listinfo/trnsys-users</a>
              <br>
            </blockquote>
            <br>
          </blockquote>
          <br>
          <br>
          <br>
          <br>
          Am 18.10.2012 16:16, schrieb David BRADLEY: <br>
          <blockquote type="cite">Michael, <br>
              I would recommend that you look online at manufacturer's
            sites for similarly sized heat pumps. Trane and Carrier both
            have significant amounts of performance data in the product
            literature parts of their sites. You can probably get a good
            estimate of the flow rates on both the condenser and
            evaporator sizes from them. <br>
            Best, <br>
             david <br>
            <br>
            <br>
            On 10/18/2012 03:53, Michael Diekerhof wrote: <br>
            <blockquote type="cite">Dear all, <br>
              <br>
              I´m working with the heat pump non-standard type 401 and
              try to display an air-source heat pump. <br>
              <br>
              I dont have typical values for the Input 2 (evaporator
              mass flowrate) and Input 4 (condenser mass flowrate). <br>
              The only real connection I´m using is the dry bulb temp,
              coming from type 15, as the evaporator inlet temperature.
              For the massflowrates I would like to assume constant
              values. <br>
              <br>
              How can I adjust an outlet condenser temperature of e.g.
              55°C. Just about the massflowrates ?! <br>
              <br>
              Does anyone have experience with heat pump mass flow
              rates?! I guess it´s not necessary to have expieriences
              with Type 401. <br>
              <br>
              I´m thankful for any advices. <br>
              <br>
              Best, <br>
              <br>
              Michael <br>
              _______________________________________________ <br>
              TRNSYS-users mailing list <br>
              <a moz-do-not-send="true" class="moz-txt-link-abbreviated"
                href="mailto:TRNSYS-users@cae.wisc.edu">TRNSYS-users@cae.wisc.edu</a>
              <br>
              <a moz-do-not-send="true" class="moz-txt-link-freetext"
                href="https://mailman.cae.wisc.edu/listinfo/trnsys-users">https://mailman.cae.wisc.edu/listinfo/trnsys-users</a>
              <br>
            </blockquote>
            <br>
          </blockquote>
          <br>
          <br>
        </blockquote>
        <br>
      </blockquote>
      <br>
    </blockquote>
    <br>
    <pre class="moz-signature" cols="72">-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI  53703 USA

P:+1.608.274.2577
F:+1.608.278.1475
<a class="moz-txt-link-abbreviated" href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>

<a class="moz-txt-link-freetext" href="http://www.tess-inc.com">http://www.tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.trnsys.com">http://www.trnsys.com</a></pre>
  </body>
</html>