    Zhe,<br>
      This is a problem with actual single stage heat pumps, not just a
    simulation problem. Single stage heat pumps cannot really modulate
    their output power so under low load conditions, they can overheat a
    fluid loop. One effective way of solving the problem is to put a
    water tank in between the load loop and the heat pump. It requires
    an additional pump but then the load loop draws water from and
    returns water to the tank. When the tank temperature drops, the heat
    pump loop turns on and heats the tank back up again. Under low load
    conditions, the load slowly draws the tank temperature down and the
    heat pump stays off.<br>
    <br>
      I am not sure what the problem with Type538 might be. I'd be
    interested if you could send me a project showing the difference in
    result between the two.<br>
    <br>
      As for the collector capacitance, often collector manufacturers
    will tell you the liquid volume of the collector. You can calculate
    a capacitance from the volume and from the specific heat of your
    working fluid. Without any better knowledge, though, we use a value
    of about 10 kJ/m2 of collector area. <br>
    Best,<br>
     David<br>
    <br>
    <br>
    <div class="moz-cite-prefix">On 10/18/2012 09:35, Zhe Li wrote:<br>
    </div>
    <blockquote cite="mid:002401cdad3d$d881adc0$89850940$%25Li@dit.ie"
      type="cite">
      <meta http-equiv="Content-Type" content="text/html;
        charset=ISO-8859-1">
      <meta name="Generator" content="Microsoft Word 12 (filtered
        medium)">
      <style><!--
/* Font Definitions */
@font-face
        {font-family:Calibri;
        panose-1:2 15 5 2 2 2 4 3 2 4;}
@font-face
        {font-family:Tahoma;
        panose-1:2 11 6 4 3 5 4 4 2 4;}
@font-face
        {font-family:Consolas;
        panose-1:2 11 6 9 2 2 4 3 2 4;}
/* Style Definitions */
p.MsoNormal, li.MsoNormal, div.MsoNormal
        {margin:0cm;
        margin-bottom:.0001pt;
        font-size:11.0pt;
        font-family:"Calibri","sans-serif";
        color:black;}
a:link, span.MsoHyperlink
        {mso-style-priority:99;
        color:blue;
        text-decoration:underline;}
a:visited, span.MsoHyperlinkFollowed
        {mso-style-priority:99;
        color:purple;
        text-decoration:underline;}
pre
        {mso-style-priority:99;
        mso-style-link:"HTML Preformatted Char";
        margin:0cm;
        margin-bottom:.0001pt;
        font-size:10.0pt;
        font-family:"Courier New";
        color:black;}
span.EmailStyle17
        {mso-style-type:personal;
        font-family:"Calibri","sans-serif";
        color:windowtext;}
span.HTMLPreformattedChar
        {mso-style-name:"HTML Preformatted Char";
        mso-style-priority:99;
        mso-style-link:"HTML Preformatted";
        font-family:Consolas;
        color:black;}
span.EmailStyle20
        {mso-style-type:personal-reply;
        font-family:"Calibri","sans-serif";
        color:#1F497D;}
.MsoChpDefault
        {mso-style-type:export-only;
        font-size:10.0pt;}
@page WordSection1
        {size:612.0pt 792.0pt;
        margin:72.0pt 72.0pt 72.0pt 72.0pt;}
div.WordSection1
        {page:WordSection1;}
--></style><!--[if gte mso 9]><xml>
<o:shapedefaults v:ext="edit" spidmax="1026" />
</xml><![endif]--><!--[if gte mso 9]><xml>
<o:shapelayout v:ext="edit">
<o:idmap v:ext="edit" data="1" />
</o:shapelayout></xml><![endif]-->
      <div class="WordSection1">
        <p class="MsoNormal"><span style="color:#1F497D">David,<o:p></o:p></span></p>
        <p class="MsoNormal"><span style="color:#1F497D"><o:p> </o:p></span></p>
        <p class="MsoNormal"><span style="color:#1F497D">Thank you very
            much for your response a couple of days ago. I have been
            considering your advice and trying to make some changes in
            my simulation models. However, I have not been successful. I
            did identify the major problem, as you have explained, once
            the controller trigger the ON function, the heat pump runs
            without limiting the useful energy required for the thermal
            load, this results a massive energy overproduced especially
            for summer months. I am trying to write an equation to
            reduce the flowrate in order to prevent energy been overly
            produced. The whole validation I am carrying out against is
            a system without a buffer tank, hence I will have to set up
            an air source heat pump system without a buffer tank even
            though I understand it is more accurate to do so.  In your
            experience, how would you do if you are in my situation? <o:p></o:p></span></p>
        <p class="MsoNormal"><span style="color:#1F497D"><o:p> </o:p></span></p>
        <p class="MsoNormal"><span style="color:#1F497D">Also come back
            to the solar thermal system. I remembered that you
            recommended flat plate solar collector type539 as it is the
            most robust collector as you mentioned. I have tried it, it
            worked pretty good. However, I would think evacuated tube
            solar collector type538 is also very robust and accurate,
            however the result I am getting is significantly larger than
            expected. Then I tried the simple version Type71 evacuated
            tube collector, it does give me decent result. The results
            difference between Type538 and Type71 is about 33% which I
            think it is huge. Would you recommend Type538 for general
            use even though I do think this type is quite sophisticated
            from what I have seen in Mathematic description in Tess
            model? <o:p></o:p></span></p>
        <p class="MsoNormal"><span style="color:#1F497D"><o:p> </o:p></span></p>
        <p class="MsoNormal"><span style="color:#1F497D">I have one
            final question, where could I get information for the
            capacitance of collector? I have tried varies manufacture
            website, none of them has given this value.  If I leave the
            default value, is this going to affect my result by much?<o:p></o:p></span></p>
        <p class="MsoNormal"><span style="color:#1F497D"><o:p> </o:p></span></p>
        <p class="MsoNormal"><span style="color:#1F497D">Thank you very
            much for your help.<o:p></o:p></span></p>
        <p class="MsoNormal"><span style="color:#1F497D"><o:p> </o:p></span></p>
        <p class="MsoNormal"><span style="color:#1F497D">Zhe Li <o:p></o:p></span></p>
        <p class="MsoNormal"><span style="color:#1F497D"><o:p> </o:p></span></p>
        <div>
          <div style="border:none;border-top:solid #B5C4DF
            1.0pt;padding:3.0pt 0cm 0cm 0cm">
            <p class="MsoNormal"><b><span
style="font-size:10.0pt;font-family:"Tahoma","sans-serif";color:windowtext"
                  lang="EN-US">From:</span></b><span
style="font-size:10.0pt;font-family:"Tahoma","sans-serif";color:windowtext"
                lang="EN-US"> David BRADLEY
                [<a class="moz-txt-link-freetext" href="mailto:d.bradley@tess-inc.com">mailto:d.bradley@tess-inc.com</a>] <br>
                <b>Sent:</b> 16 October 2012 17:04<br>
                <b>To:</b> Zhe Li<br>
                <b>Cc:</b> <a class="moz-txt-link-abbreviated" href="mailto:trnsys-users@cae.wisc.edu">trnsys-users@cae.wisc.edu</a><br>
                <b>Subject:</b> Re: [TRNSYS-users] Air source heat pump
                system validation<o:p></o:p></span></p>
          </div>
        </div>
        <p class="MsoNormal"><o:p> </o:p></p>
        <p class="MsoNormal" style="margin-bottom:12.0pt">Zhe Li,<br>
            I look at similar energy balances quite often so I suspect
          there is not a systematic problem but something wrong in the
          simulation. There are a few things to look at.<br>
          <br>
          First, make sure that you have some thermal capacitance in the
          liquid loop. This will usually take the form of a buffer tank.
          The tank should have enough volume to store at least one
          timestep of liquid at whatever flow rate your pump is running.
          <br>
          <br>
          Second, look at the controls on your flow loop. Type941 is
          basically an ON/OFF device; it does not meet a set point
          temperature but simply puts its entire current capacity into
          cooling down (or heating up) the liquid loop. Under low load
          situations, this can dramatically overheat or overcool the
          liquid loop; the tank above should help this a lot.<br>
          <br>
          Third, make sure that you are using a reasonably short
          timestep (1 or 5 minutes). this will allow your system to be
          controller appropriately.<br>
          <br>
          When you look at the energy balance, you have to also look at
          the beginning and ending temperature of the liquid loop. If it
          is significantly different than it was at the simulation
          start, you have to account for stored energy in your balance.<br>
          Kind regards,<br>
           David<br>
          <br>
          <br>
          <o:p></o:p></p>
        <div>
          <p class="MsoNormal">On 10/16/2012 08:42, Zhe Li wrote:<o:p></o:p></p>
        </div>
        <blockquote style="margin-top:5.0pt;margin-bottom:5.0pt">
          <p class="MsoNormal">Dear TRNSYS users,<o:p></o:p></p>
          <p class="MsoNormal"> <o:p></o:p></p>
          <p class="MsoNormal">Thanks for your time. <o:p></o:p></p>
          <p class="MsoNormal"> <o:p></o:p></p>
          <p class="MsoNormal">I am currently performing a simple
            validation of an air source heat pump system. The air-source
            heat pump is Type941, and I am using a defined thermal load
            (Type682) with an input file (Type9). However, the results I
            am getting for the Total Heat Transfer to Liquid from output
            option in air source heat pump component is between 2 and 3
            times higher than the Heating Load Met from output option in
            thermal load. I cannot think of any reason why the generated
            energy is significantly higher than the load met.  I would
            understand if the generated energy is a bit higher than the
            load met as there might be heat losses from connected pipes.
            <o:p></o:p></p>
          <p class="MsoNormal"> <o:p></o:p></p>
          <p class="MsoNormal">Could anyone give me some advices? This
            is very important for me to continue my research project.<o:p></o:p></p>
          <p class="MsoNormal"> <o:p></o:p></p>
          <p class="MsoNormal">Thanks very much in advance.<o:p></o:p></p>
          <p class="MsoNormal"> <o:p></o:p></p>
          <p class="MsoNormal">Zhe Li<o:p></o:p></p>
          <p class="MsoNormal"><span
              style="font-size:12.0pt;font-family:"Times New
              Roman","serif""><br clear="all">
              Tá an teachtaireacht seo scanta ó thaobh ábhar agus víreas
              ag Seirbhís Scanta Ríomhphost de chuid Seirbhísí
              Faisnéise, ITBÁC agus meastar í a bheith slán. <a
                moz-do-not-send="true" href="http://www.dit.ie">http://www.dit.ie</a><br>
              This message has been scanned for content and viruses by
              the DIT Information Services E-Mail Scanning Service, and
              is believed to be clean. <a moz-do-not-send="true"
                href="http://www.dit.ie">http://www.dit.ie</a> <br>
              <br>
              <br>
              <o:p></o:p></span></p>
          <pre>_______________________________________________<o:p></o:p></pre>
          <pre>TRNSYS-users mailing list<o:p></o:p></pre>
          <pre><a moz-do-not-send="true" href="mailto:TRNSYS-users@cae.wisc.edu">TRNSYS-users@cae.wisc.edu</a><o:p></o:p></pre>
          <pre><a moz-do-not-send="true" href="https://mailman.cae.wisc.edu/listinfo/trnsys-users">https://mailman.cae.wisc.edu/listinfo/trnsys-users</a><o:p></o:p></pre>
        </blockquote>
        <p class="MsoNormal"><span
            style="font-size:12.0pt;font-family:"Times New
            Roman","serif""><br>
            <br>
            <o:p></o:p></span></p>
        <pre>-- <o:p></o:p></pre>
        <pre>***************************<o:p></o:p></pre>
        <pre>David BRADLEY<o:p></o:p></pre>
        <pre>Principal<o:p></o:p></pre>
        <pre>Thermal Energy Systems Specialists, LLC<o:p></o:p></pre>
        <pre>22 North Carroll Street - suite 370<o:p></o:p></pre>
        <pre>Madison, WI  53703 USA<o:p></o:p></pre>
        <pre><o:p> </o:p></pre>
        <pre>P:+1.608.274.2577<o:p></o:p></pre>
        <pre>F:+1.608.278.1475<o:p></o:p></pre>
        <pre><a moz-do-not-send="true" href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a><o:p></o:p></pre>
        <pre><o:p> </o:p></pre>
        <pre><a moz-do-not-send="true" href="http://www.tess-inc.com">http://www.tess-inc.com</a><o:p></o:p></pre>
        <pre><a moz-do-not-send="true" href="http://www.trnsys.com">http://www.trnsys.com</a><o:p></o:p></pre>
      </div>
      <br clear="all">
      Tá an teachtaireacht seo scanta ó thaobh ábhar agus víreas ag
      Seirbhís Scanta Ríomhphost de chuid Seirbhísí Faisnéise, ITBÁC
      agus meastar í a bheith slán. <a moz-do-not-send="true"
        href="http://www.dit.ie">http://www.dit.ie</a><br>
      This message has been scanned for content and viruses by the DIT
      Information Services E-Mail Scanning Service, and is believed to
      be clean. <a moz-do-not-send="true" href="http://www.dit.ie">http://www.dit.ie</a>
    </blockquote>
    <br>
    <pre class="moz-signature" cols="72">-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI  53703 USA

P:+1.608.274.2577
F:+1.608.278.1475
<a class="moz-txt-link-abbreviated" href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>

<a class="moz-txt-link-freetext" href="http://www.tess-inc.com">http://www.tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.trnsys.com">http://www.trnsys.com</a></pre>
  </body>
</html>