<html>
  <head>
    <meta content="text/html; charset=ISO-8859-1"
      http-equiv="Content-Type">
  </head>
  <body bgcolor="#FFFFFF" text="#000000">
    Wojciech,<br>
    I am not familiar with Type401. However, there are a number of heat
    pump models in the TESS Libraries and they probably work about the
    same. The problem with the existing models from your point of view
    is that they take the entering conditions (of air and water) and
    they compute the power required by the heat pump. I am not aware of
    any heat pump models that take power available as an input. I think
    you might still be able to achieve your simulation however. You need
    to first find the threshold power above which the heat pump can run
    (perhaps this would be the rated power? perhaps it would be the
    lowest power listed in the performance data?) Run your PV array and
    whenever its output power is above the heat pump's minimum allowable
    power then run the heat pump. You can write an equation that will
    multiply the thermostat's heat/cool signal by the PV's "power
    available" signal.<br>
    Best,<br>
     David<br>
    <br>
    <br>
    <br>
    <div class="moz-cite-prefix">On 10/10/2012 03:33, Malik Wojciech
      wrote:<br>
    </div>
    <blockquote
cite="mid:C1677A178671DA4F855B87B5DEB91BB34D203B9511@haasv-002.ochsner.loc"
      type="cite">
      <meta http-equiv="Content-Type" content="text/html;
        charset=ISO-8859-1">
      <meta name="Generator" content="Microsoft Word 12 (filtered
        medium)">
      <style><!--
/* Font Definitions */
@font-face
        {font-family:Calibri;
        panose-1:2 15 5 2 2 2 4 3 2 4;}
/* Style Definitions */
p.MsoNormal, li.MsoNormal, div.MsoNormal
        {margin:0cm;
        margin-bottom:.0001pt;
        font-size:11.0pt;
        font-family:"Calibri","sans-serif";}
a:link, span.MsoHyperlink
        {mso-style-priority:99;
        color:blue;
        text-decoration:underline;}
a:visited, span.MsoHyperlinkFollowed
        {mso-style-priority:99;
        color:purple;
        text-decoration:underline;}
span.E-MailFormatvorlage17
        {mso-style-type:personal-compose;
        font-family:"Calibri","sans-serif";
        color:windowtext;}
.MsoChpDefault
        {mso-style-type:export-only;}
@page WordSection1
        {size:612.0pt 792.0pt;
        margin:70.85pt 70.85pt 2.0cm 70.85pt;}
div.WordSection1
        {page:WordSection1;}
--></style><!--[if gte mso 9]><xml>
<o:shapedefaults v:ext="edit" spidmax="1026" />
</xml><![endif]--><!--[if gte mso 9]><xml>
<o:shapelayout v:ext="edit">
<o:idmap v:ext="edit" data="1" />
</o:shapelayout></xml><![endif]-->
      <div class="WordSection1">
        <p class="MsoNormal">Hello <o:p></o:p></p>
        <p class="MsoNormal"><o:p> </o:p></p>
        <p class="MsoNormal"><span lang="EN-US">Could anybody give the
            prompt how to simulate and which components must be used in
            Heat Pump system combined with the PV cells? <o:p></o:p></span></p>
        <p class="MsoNormal"><span lang="EN-US">The main assumptions
            that I have made are: Type 401 combined with Type 94a and
            with the building Tpe56. It is possible that the PV will
            support power consumption of the Heat Pump?<o:p></o:p></span></p>
        <p class="MsoNormal"><span lang="EN-US">As an result of this
            simulation I would like to achieve information about the COP
            (it depends of assumed parameters)  and how the COP value
            varies depending on the season and the weather.<o:p></o:p></span></p>
        <p class="MsoNormal"><span lang="EN-US">Also I would like to get
            information about the cost of this combination (PV+ HP) –
            how much money we can save using this combination. <o:p></o:p></span></p>
        <p class="MsoNormal"><span lang="EN-US">Do you have any ideas or
            suggestions how can I started this simulation and which
            Types I should use? <o:p></o:p></span></p>
        <p class="MsoNormal"><span lang="EN-US"><o:p> </o:p></span></p>
        <p class="MsoNormal"><span lang="EN-US">I will appreciate any
            kind of help.<o:p></o:p></span></p>
        <p class="MsoNormal"><span lang="EN-US"><o:p> </o:p></span></p>
        <p class="MsoNormal"><span lang="EN-US">Sincerely<o:p></o:p></span></p>
        <p class="MsoNormal"><span lang="EN-US">Wojciech<o:p></o:p></span></p>
        <p class="MsoNormal"><span lang="EN-US"><o:p> </o:p></span></p>
        <p class="MsoNormal"><o:p> </o:p></p>
      </div>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <br>
      <pre wrap="">_______________________________________________
TRNSYS-users mailing list
<a class="moz-txt-link-abbreviated" href="mailto:TRNSYS-users@cae.wisc.edu">TRNSYS-users@cae.wisc.edu</a>
<a class="moz-txt-link-freetext" href="https://mailman.cae.wisc.edu/listinfo/trnsys-users">https://mailman.cae.wisc.edu/listinfo/trnsys-users</a>
</pre>
    </blockquote>
    <br>
    <pre class="moz-signature" cols="72">-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI  53703 USA

P:+1.608.274.2577
F:+1.608.278.1475
<a class="moz-txt-link-abbreviated" href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>

<a class="moz-txt-link-freetext" href="http://www.tess-inc.com">http://www.tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.trnsys.com">http://www.trnsys.com</a></pre>
  </body>
</html>