<html>
  <head>
    <meta content="text/html; charset=ISO-8859-1"
      http-equiv="Content-Type">
  </head>
  <body bgcolor="#FFFFFF" text="#000000">
    Zhe Li,<br>
      I look at similar energy balances quite often so I suspect there
    is not a systematic problem but something wrong in the simulation.
    There are a few things to look at.<br>
    <br>
    First, make sure that you have some thermal capacitance in the
    liquid loop. This will usually take the form of a buffer tank. The
    tank should have enough volume to store at least one timestep of
    liquid at whatever flow rate your pump is running. <br>
    <br>
    Second, look at the controls on your flow loop. Type941 is basically
    an ON/OFF device; it does not meet a set point temperature but
    simply puts its entire current capacity into cooling down (or
    heating up) the liquid loop. Under low load situations, this can
    dramatically overheat or overcool the liquid loop; the tank above
    should help this a lot.<br>
    <br>
    Third, make sure that you are using a reasonably short timestep (1
    or 5 minutes). this will allow your system to be controller
    appropriately.<br>
    <br>
    When you look at the energy balance, you have to also look at the
    beginning and ending temperature of the liquid loop. If it is
    significantly different than it was at the simulation start, you
    have to account for stored energy in your balance.<br>
    Kind regards,<br>
     David<br>
    <br>
    <br>
    <br>
    <div class="moz-cite-prefix">On 10/16/2012 08:42, Zhe Li wrote:<br>
    </div>
    <blockquote cite="mid:004401cdaba4$1728d2b0$457a7810$%25Li@dit.ie"
      type="cite">
      <meta http-equiv="Content-Type" content="text/html;
        charset=ISO-8859-1">
      <meta name="Generator" content="Microsoft Word 12 (filtered
        medium)">
      <style><!--
/* Font Definitions */
@font-face
        {font-family:Calibri;
        panose-1:2 15 5 2 2 2 4 3 2 4;}
/* Style Definitions */
p.MsoNormal, li.MsoNormal, div.MsoNormal
        {margin:0cm;
        margin-bottom:.0001pt;
        font-size:11.0pt;
        font-family:"Calibri","sans-serif";}
a:link, span.MsoHyperlink
        {mso-style-priority:99;
        color:blue;
        text-decoration:underline;}
a:visited, span.MsoHyperlinkFollowed
        {mso-style-priority:99;
        color:purple;
        text-decoration:underline;}
span.EmailStyle17
        {mso-style-type:personal-compose;
        font-family:"Calibri","sans-serif";
        color:windowtext;}
.MsoChpDefault
        {mso-style-type:export-only;}
@page WordSection1
        {size:612.0pt 792.0pt;
        margin:72.0pt 72.0pt 72.0pt 72.0pt;}
div.WordSection1
        {page:WordSection1;}
--></style><!--[if gte mso 9]><xml>
<o:shapedefaults v:ext="edit" spidmax="1026" />
</xml><![endif]--><!--[if gte mso 9]><xml>
<o:shapelayout v:ext="edit">
<o:idmap v:ext="edit" data="1" />
</o:shapelayout></xml><![endif]-->
      <div class="WordSection1">
        <p class="MsoNormal">Dear TRNSYS users,<o:p></o:p></p>
        <p class="MsoNormal"><o:p> </o:p></p>
        <p class="MsoNormal">Thanks for your time. <o:p></o:p></p>
        <p class="MsoNormal"><o:p> </o:p></p>
        <p class="MsoNormal">I am currently performing a simple
          validation of an air source heat pump system. The air-source
          heat pump is Type941, and I am using a defined thermal load
          (Type682) with an input file (Type9). However, the results I
          am getting for the Total Heat Transfer to Liquid from output
          option in air source heat pump component is between 2 and 3
          times higher than the Heating Load Met from output option in
          thermal load. I cannot think of any reason why the generated
          energy is significantly higher than the load met.  I would
          understand if the generated energy is a bit higher than the
          load met as there might be heat losses from connected pipes. <o:p></o:p></p>
        <p class="MsoNormal"><o:p> </o:p></p>
        <p class="MsoNormal">Could anyone give me some advices? This is
          very important for me to continue my research project.<o:p></o:p></p>
        <p class="MsoNormal"><o:p> </o:p></p>
        <p class="MsoNormal">Thanks very much in advance.<o:p></o:p></p>
        <p class="MsoNormal"><o:p> </o:p></p>
        <p class="MsoNormal">Zhe Li<o:p></o:p></p>
      </div>
      <br clear="all">
      Tá an teachtaireacht seo scanta ó thaobh ábhar agus víreas ag
      Seirbhís Scanta Ríomhphost de chuid Seirbhísí Faisnéise, ITBÁC
      agus meastar í a bheith slán. <a moz-do-not-send="true"
        href="http://www.dit.ie">http://www.dit.ie</a><br>
      This message has been scanned for content and viruses by the DIT
      Information Services E-Mail Scanning Service, and is believed to
      be clean. <a moz-do-not-send="true" href="http://www.dit.ie">http://www.dit.ie</a>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <br>
      <pre wrap="">_______________________________________________
TRNSYS-users mailing list
<a class="moz-txt-link-abbreviated" href="mailto:TRNSYS-users@cae.wisc.edu">TRNSYS-users@cae.wisc.edu</a>
<a class="moz-txt-link-freetext" href="https://mailman.cae.wisc.edu/listinfo/trnsys-users">https://mailman.cae.wisc.edu/listinfo/trnsys-users</a>
</pre>
    </blockquote>
    <br>
    <pre class="moz-signature" cols="72">-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI  53703 USA

P:+1.608.274.2577
F:+1.608.278.1475
<a class="moz-txt-link-abbreviated" href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>

<a class="moz-txt-link-freetext" href="http://www.tess-inc.com">http://www.tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.trnsys.com">http://www.trnsys.com</a></pre>
  </body>
</html>