Dear Group,<br><br>Are there any unspoken rules when using this type (type 23)? I have found the following make it hang or not respond properly:<br>1) giving the controller a zero<br>2) limiting the min max by relatively small numbers (capping the peaks and dips of the natural cycling killed this object for me)<br>
3) inputing a large gain<br>4) too small a I-time input<br><br>This type is really sensitive to the timestep...I'm having to use really small timesteps to get the "tuning" just right. I have tried various tuning techniques suggested on this forum as well as industry known techneques. With x2 controllers, I abandoned the I-D control altogether, as it just wasn't having it and resorted to a pure P-control by setting the I&D inputs to zero. Even then, it gives problems and is highly sensitive.<br>
<br>Regards,<br><br>Jean<br><br><br>