    Eva,<br>
      They probably won't be very comparable and they shouldn't be but
    they're both still useful in getting at what you're looking for. The
    sensible heating energy output from Type56 is the amount of energy
    that is required by the space in order to maintain temperature. The
    required boiler energy is the amount of source energy that has to be
    purchased in order to run the boiler and provide that amount of
    energy to the zone. The difference between the two is the system
    inefficiency. The required boiler energy must be higher than the
    sensible heating requirement from Type56. If it is, then that is an
    indication that the boiler isn't providing enough energy to keep the
    space heated. The boiler should also have an output that is the
    amount of energy actually transferred to the fluid. This value
    should match the sensible heating demand better; the difference in
    this case is the inefficiency of the pumping and distribution
    systems.   <br>
    Best,<br>
     David<br>
    <br>
    <br>
    <div class="moz-cite-prefix">On 8/25/2012 11:15, Eva gklezakou
      wrote:<br>
    </div>
    <blockquote
cite="mid:CA+Ci=p8oVnMz5O64uZ0bfDgYzQcDt5TJ5qCf2Zyd8cANPsfM=g@mail.gmail.com"
      type="cite">Dear Sirs,
      <div><br>
      </div>
      <div>I model a house with the ideal heating system which is used
        in type 56 and then I integrate to the same house underfloor
        heating with solar panel and boiler (auxiliary heater). The next
        step is to compare the energy consumption between the two cases.
        Does anyone know what is the relation between the two outputs,
        Sensible Heating energy for the first case and Required energy
        boiler input for the second case. How can I make these two
        values comparable?</div>
      <div>Thank you for the help.</div>
      <div><br>
      </div>
      <div>Regards,</div>
      <div>Eva   </div>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <br>
      <pre wrap="">_______________________________________________
TRNSYS-users mailing list
<a class="moz-txt-link-abbreviated" href="mailto:TRNSYS-users@cae.wisc.edu">TRNSYS-users@cae.wisc.edu</a>
<a class="moz-txt-link-freetext" href="https://mailman.cae.wisc.edu/listinfo/trnsys-users">https://mailman.cae.wisc.edu/listinfo/trnsys-users</a>
</pre>
    </blockquote>
    <br>
    <pre class="moz-signature" cols="72">-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI  53703 USA

P:+1.608.274.2577
F:+1.608.278.1475
<a class="moz-txt-link-abbreviated" href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>

<a class="moz-txt-link-freetext" href="http://www.tess-inc.com">http://www.tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.trnsys.com">http://www.trnsys.com</a></pre>
  </body>
</html>