Pauline,<br>
In addition to Adrien's response, the sky temperature model that
is implemented in Type15 (when reading meteonorm files for example)
is the same one that is in the TESS Type575.<br>
Best,<br>
David<br>
<br>
<br>
<div class="moz-cite-prefix">On 8/22/2012 08:22, ITF - Adrien
JEZEQUEL wrote:<br>
</div>
<blockquote cite="mid:5034DD04.2020004@itf.biz" type="cite">
<meta content="text/html; charset=ISO-8859-1"
http-equiv="Content-Type">
<div class="moz-cite-prefix"><font size="-1"><font face="Arial">Hi
Pauline,<br>
<br>
This subject was ever treated in the past :<br>
<a moz-do-not-send="true" class="moz-txt-link-freetext"
href="https://mailman.cae.wisc.edu/pipermail/trnsys-users/2009/004373.html">https://mailman.cae.wisc.edu/pipermail/trnsys-users/2009/004373.html</a><br>
<br>
Different models exist to evaluate sky temperature. </font></font><font
size="-1"><font face="Arial"> That's why you may find
differents values.</font></font><br>
<font size="-1"><font face="Arial">Meteonorm software use
SoDa/ESRA clear sky model.<br>
<br>
In trnsys, you may use :<br>
</font></font>
<ul>
<li>type69a : cloudiness factor is not controled by user<br>
</li>
<li>type69b : cloudiness factor is an input of the type<br>
</li>
<li>type575a and type575b (In TESS library only)</li>
</ul>
<p>If you compare sky temperature given by meteonorm data and
sky temperatures given with type69b with the same cloudiness
factor as meteonorm data, results won't be so different.<br>
</p>
<p>Best regards<br>
</p>
<div class="moz-signature">
<hr align="LEFT" color="#3300FF" size="2" width="450">
<table border="0">
<tbody>
<tr>
<td rowspan="3" width="120">
<center><a moz-do-not-send="true"
href="http://www.itf.biz"><img
src="cid:part2.00030907.01080300@tess-inc.com"
alt="www.itf.biz" border="0" height="103"
width="66"></a><br>
<font color=" #0000FF" face="CALIBRI" size="1"><a
moz-do-not-send="true" href="http://www.itf.biz">www.itf.biz</a></font></center>
</td>
<td colspan="2"><font color="#000000" face="CALIBRI"
size="2">Adrien JEZEQUEL<br>
Simulations Thermiques Dynamiques</font></td>
</tr>
<tr>
<td align="LEFT"> <font color="#0000FF" face="CALIBRI"
size="4"><b>ITF</b></font><br>
</td>
<td><font color="#0000FF" face="CALIBRI" size="2">62,
Rue du Bolliet<br>
73230 St Alban Leysse<br>
FRANCE<br>
</font></td>
</tr>
<tr>
<td align="LEFT" width="40"><font color="#0000FF"
face="CALIBRI" size="2"> Phone :<br>
Fax :<br>
Mail:<br>
</font> </td>
<td><font color="#0000FF" face="CALIBRI" size="2">
+33(0) 479 750 029<br>
+33(0) 479 852 122<br>
<a moz-do-not-send="true"
class="moz-txt-link-freetext"
href="mailto:a.jezequel@itf.biz">a.jezequel@itf.biz</a>
ou <a moz-do-not-send="true"
class="moz-txt-link-freetext"
href="mailto:aj@itf.biz">aj@itf.biz</a></font></td>
</tr>
</tbody>
</table>
<i><font color="#008000" face="CALIBRI" size="1">Afin de
contribuer au respect de l'environnement, merci de
n'imprimer cet e-mail que si nécessaire<br>
<font color="#008000" face="CALIBRI" size="1">Please,
consider our environmental responsability before
printing this email<br>
</font></font></i><font color="#008000" face="CALIBRI"
size="1"><font color="#008000" face="CALIBRI" size="1"> </font></font></div>
Le 22/08/2012 11:17, Pauline GELIN a écrit :<br>
</div>
<blockquote
cite="mid:11E83A53757D4E42BAB9B7808BC3D143546A7B0759@VEV-MES1.KATENE.local"
type="cite">
<meta http-equiv="Content-Type" content="text/html;
charset=ISO-8859-1">
<meta name="Generator" content="Microsoft Word 14 (filtered
medium)">
<!--[if !mso]><style>v\:* {behavior:url(#default#VML);}
o\:* {behavior:url(#default#VML);}
w\:* {behavior:url(#default#VML);}
.shape {behavior:url(#default#VML);}
</style><![endif]-->
<style><!--
/* Font Definitions */
@font-face
{font-family:Calibri;
panose-1:2 15 5 2 2 2 4 3 2 4;}
@font-face
{font-family:Tahoma;
panose-1:2 11 6 4 3 5 4 4 2 4;}
@font-face
{font-family:Consolas;
panose-1:2 11 6 9 2 2 4 3 2 4;}
/* Style Definitions */
p.MsoNormal, li.MsoNormal, div.MsoNormal
{margin:0cm;
margin-bottom:.0001pt;
font-size:12.0pt;
font-family:"Times New Roman","serif";
color:black;}
a:link, span.MsoHyperlink
{mso-style-priority:99;
color:blue;
text-decoration:underline;}
a:visited, span.MsoHyperlinkFollowed
{mso-style-priority:99;
color:purple;
text-decoration:underline;}
pre
{mso-style-priority:99;
mso-style-link:"Préformaté HTML Car";
margin:0cm;
margin-bottom:.0001pt;
font-size:10.0pt;
font-family:"Courier New";
color:black;}
p.MsoAcetate, li.MsoAcetate, div.MsoAcetate
{mso-style-priority:99;
mso-style-link:"Texte de bulles Car";
margin:0cm;
margin-bottom:.0001pt;
font-size:8.0pt;
font-family:"Tahoma","sans-serif";
color:black;}
p.MsoListParagraph, li.MsoListParagraph, div.MsoListParagraph
{mso-style-priority:34;
margin-top:0cm;
margin-right:0cm;
margin-bottom:0cm;
margin-left:36.0pt;
margin-bottom:.0001pt;
font-size:12.0pt;
font-family:"Times New Roman","serif";
color:black;}
span.PrformatHTMLCar
{mso-style-name:"Préformaté HTML Car";
mso-style-priority:99;
mso-style-link:"Préformaté HTML";
font-family:Consolas;
color:black;}
span.TextedebullesCar
{mso-style-name:"Texte de bulles Car";
mso-style-priority:99;
mso-style-link:"Texte de bulles";
font-family:"Tahoma","sans-serif";
mso-fareast-language:FR;}
span.il
{mso-style-name:il;}
span.EmailStyle23
{mso-style-type:personal;
font-family:"Calibri","sans-serif";
color:#1F497D;}
span.hps
{mso-style-name:hps;}
span.shorttext
{mso-style-name:short_text;}
span.EmailStyle26
{mso-style-type:personal;
font-family:"Calibri","sans-serif";
color:#1F497D;}
span.EmailStyle27
{mso-style-type:personal;
font-family:"Calibri","sans-serif";
color:#1F497D;}
span.EmailStyle28
{mso-style-type:personal;
font-family:"Calibri","sans-serif";
color:#1F497D;}
span.EmailStyle29
{mso-style-type:personal;
font-family:"Calibri","sans-serif";
color:#1F497D;}
span.EmailStyle30
{mso-style-type:personal-reply;
font-family:"Calibri","sans-serif";
color:#1F497D;}
.MsoChpDefault
{mso-style-type:export-only;
font-size:10.0pt;}
@page WordSection1
{size:612.0pt 792.0pt;
margin:70.85pt 70.85pt 70.85pt 70.85pt;}
div.WordSection1
{page:WordSection1;}
--></style><!--[if gte mso 9]><xml>
<o:shapedefaults v:ext="edit" spidmax="1026" />
</xml><![endif]--><!--[if gte mso 9]><xml>
<o:shapelayout v:ext="edit">
<o:idmap v:ext="edit" data="1" />
</o:shapelayout></xml><![endif]-->
<div class="WordSection1">
<p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D">Hello,
<o:p></o:p></span></p>
<p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D"><o:p> </o:p></span></p>
<p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D"
lang="EN-US">For a project I would like to check if the
effective sky temperature done by the weather type 9
(Meteonorm) is the same than the temperature calculated in
the type 69 (with 4 inputs from the type 9). <o:p></o:p></span></p>
<p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D"
lang="EN-US">In fact there are different. <o:p></o:p></span></p>
<p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D"
lang="EN-US">How can we explain that whereas there is the
same descriptions?<o:p></o:p></span></p>
<p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D"
lang="EN-US"><o:p> </o:p></span></p>
<p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D"
lang="EN-US">Thank you very much for your answers. <o:p></o:p></span></p>
<p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D"
lang="EN-US"><o:p> </o:p></span></p>
<p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D"
lang="EN-US">Best regards, <o:p></o:p></span></p>
<p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D"
lang="EN-US"><o:p> </o:p></span></p>
<p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D"
lang="EN-US">Pauline Gelin<o:p></o:p></span></p>
<div>
<p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#7030A0"
lang="EN-US"><o:p> </o:p></span></p>
<table class="MsoNormalTable"
style="width:473.25pt;border-collapse:collapse" border="0"
cellpadding="0" cellspacing="0" width="631">
<tbody>
<tr>
<td style="width:104.65pt;border:solid #F79646
2.25pt;border-right:none;padding:0cm 5.4pt 0cm
5.4pt" valign="top" width="140">
<p class="MsoNormal"
style="margin-left:-7.1pt;text-align:center"
align="center"><b><span
style="font-size:8.0pt;font-family:"Tahoma","sans-serif";color:#31849B;mso-fareast-language:EN-US"
lang="EN-US"><o:p> </o:p></span></b></p>
<p class="MsoNormal"
style="margin-left:7.1pt;text-align:center"
align="center"><b><span
style="font-size:14.0pt;font-family:"Tahoma","sans-serif";color:#31849B"><img
id="Image_x0020_5"
src="cid:part7.05040103.00030204@tess-inc.com"
alt="Description :
cid:image007.jpg@01CC9EDB.F49EDC60"
height="70" width="125"></span></b><b><span
style="font-size:14.0pt;font-family:"Tahoma","sans-serif";color:#31849B;mso-fareast-language:EN-US"><o:p></o:p></span></b></p>
<p class="MsoNormal"><b><span
style="font-size:14.0pt;font-family:"Tahoma","sans-serif";color:#31849B"><img
id="Image_x0020_18"
src="cid:part8.09060405.03090307@tess-inc.com"
alt="Description : Description :
Description : Description : Description :
logo Woopa" height="22" width="133"></span></b><b><span
style="font-size:14.0pt;font-family:"Tahoma","sans-serif";color:#31849B;mso-fareast-language:EN-US"><o:p></o:p></span></b></p>
</td>
<td style="width:13.0cm;border:solid #F79646
2.25pt;border-left:none;padding:0cm 5.4pt 0cm 5.4pt"
width="491">
<p class="MsoNormal"><b><span
style="font-size:11.0pt;font-family:"Tahoma","sans-serif";color:#F79646;mso-fareast-language:EN-US">KATENE<o:p></o:p></span></b></p>
<p class="MsoNormal"><b><span
style="font-size:11.0pt;font-family:"Tahoma","sans-serif";color:#F79646;mso-fareast-language:EN-US"><o:p> </o:p></span></b></p>
<p class="MsoNormal"><b><span
style="font-size:11.0pt;font-family:"Tahoma","sans-serif";color:#F79646;mso-fareast-language:EN-US">10
avenue des Canuts – 69120 VAULX EN VELIN<o:p></o:p></span></b></p>
<p class="MsoNormal"
style="mso-margin-top-alt:3.0pt;margin-right:0cm;margin-bottom:0cm;margin-left:1.7pt;margin-bottom:.0001pt"><b><span
style="font-size:11.0pt;font-family:"Tahoma","sans-serif";color:#F79646;mso-fareast-language:EN-US">0437453347</span></b><b><span
style="font-size:11.0pt;font-family:"Tahoma","sans-serif";color:#FFC000;mso-fareast-language:EN-US"><o:p></o:p></span></b></p>
<p class="MsoNormal"><b><span
style="font-size:14.0pt;font-family:"Tahoma","sans-serif";color:#31849B;mso-fareast-language:EN-US"><o:p> </o:p></span></b></p>
</td>
</tr>
</tbody>
</table>
<p class="MsoNormal"><o:p> </o:p></p>
</div>
</div>
<br>
<fieldset class="mimeAttachmentHeader"></fieldset>
<br>
<pre wrap="">_______________________________________________
TRNSYS-users mailing list
<a moz-do-not-send="true" class="moz-txt-link-abbreviated" href="mailto:TRNSYS-users@cae.wisc.edu">TRNSYS-users@cae.wisc.edu</a>
<a moz-do-not-send="true" class="moz-txt-link-freetext" href="https://mailman.cae.wisc.edu/listinfo/trnsys-users">https://mailman.cae.wisc.edu/listinfo/trnsys-users</a>
</pre>
</blockquote>
<br>
<br>
<fieldset class="mimeAttachmentHeader"></fieldset>
<br>
<pre wrap="">_______________________________________________
TRNSYS-users mailing list
<a class="moz-txt-link-abbreviated" href="mailto:TRNSYS-users@cae.wisc.edu">TRNSYS-users@cae.wisc.edu</a>
<a class="moz-txt-link-freetext" href="https://mailman.cae.wisc.edu/listinfo/trnsys-users">https://mailman.cae.wisc.edu/listinfo/trnsys-users</a>
</pre>
</blockquote>
<br>
<pre class="moz-signature" cols="72">--
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI 53703 USA
P:+1.608.274.2577
F:+1.608.278.1475
<a class="moz-txt-link-abbreviated" href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.tess-inc.com">http://www.tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.trnsys.com">http://www.trnsys.com</a></pre>
</body>
</html>