<html>
<head>
<meta content="text/html; charset=ISO-8859-1"
http-equiv="Content-Type">
</head>
<body bgcolor="#FFFFFF" text="#000000">
Eva,<br>
Your pump model will have one inlet and one outlet. Just after the
pump, you can use either a combination of Type11s to divert the flow
to the various floors (each Type11 allows for 2 outlets). If you
have the TESS Hydronics Library, you can use Type647, which has one
inlet and up to 100 outputs. In either case, you will probably need
to use some equations to determine what fraction of the pump's total
flow needs to go to each of the flow diverter's outlets. <br>
Regards,<br>
David <br>
<br>
<div class="moz-cite-prefix">On 7/18/2012 20:05, Eva gklezakou
wrote:<br>
</div>
<blockquote
cite="mid:CA+Ci=p9R=C7MGDKBD2phBGSNPCBCnxEejSzRyu7j3+nLty3_1A@mail.gmail.com"
type="cite">Dear Sirs,
<div><br>
</div>
<div>I model a building with underfloor heating which get the
appropriate hot water from solar collectors. The hot water is
stored in a tank and then it is pumped to the building. My query
is how can I distribute the water to each zone, I need a pump
which has one inlet (flow from tank) and six different outlet
(flow to active layer of each zone). Each zone has different
need according to its size and so I want to send the needed
amount of water in order to control their temperatures.</div>
<div>Thank you.</div>
<div><br>
</div>
<div>Regards,</div>
<div>Eva </div>
<br>
<fieldset class="mimeAttachmentHeader"></fieldset>
<br>
<pre wrap="">_______________________________________________
TRNSYS-users mailing list
<a class="moz-txt-link-abbreviated" href="mailto:TRNSYS-users@cae.wisc.edu">TRNSYS-users@cae.wisc.edu</a>
<a class="moz-txt-link-freetext" href="https://mailman.cae.wisc.edu/listinfo/trnsys-users">https://mailman.cae.wisc.edu/listinfo/trnsys-users</a>
</pre>
</blockquote>
<br>
<pre class="moz-signature" cols="72">--
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI 53703 USA
P:+1.608.274.2577
F:+1.608.278.1475
<a class="moz-txt-link-abbreviated" href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.tess-inc.com">http://www.tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.trnsys.com">http://www.trnsys.com</a></pre>
</body>
</html>