<html>
  <head>
    <meta content="text/html; charset=ISO-8859-1"
      http-equiv="Content-Type">
  </head>
  <body bgcolor="#FFFFFF" text="#000000">
    Nidal,<br>
      I have been using Type344 quite a lot lately and have not had
    trouble with it. I can think of a number of possible causes for the
    behavior that you describe but without seeing the project it is not
    possible to know which one is the trouble. I think the critical
    thing to do is to use a Type65 to look at the values of inputs 15
    and 16 to the pool (of course you will have to look at the outputs
    of whatever Type is connected to those inputs; a pump perhaps or the
    outlet of the solar collector). When you know what the inlet
    temperature and mass flow rate of heating water to the pool are, it
    should be obvious whether such a volume at such a temperature is
    able to change the pool's temperature.<br>
    <br>
    1. it could be that you have so few collectors in comparison to the
    size of the pool that the collector system can't affect the pool.<br>
    2. if could be that the controller that determines when the
    collector system needs to run is not working the way that you expect
    it to.<br>
    3. it could be that the evaporative, convective, and radiative
    thermal losses from the pool are large in comparison to the energy
    input from the heating system and that the pool is completely
    dominated by its surroundings and not by the system.<br>
    <br>
    Another thing to try is to disconnect the solar collector system and
    put in an imaginary source of hot water (just set the inlet
    temperature to a constant value and turn an arbitrary mass flow rate
    on and off with a controller. Verify that the pool temperature is
    affected by those inputs.<br>
    <br>
    Kind regards,<br>
     David<br>
    <br>
    <br>
    <div class="moz-cite-prefix">On 7/15/2012 01:42, Nidal Abdalla
      wrote:<br>
    </div>
    <blockquote
      cite="mid:1342334527.72722.YahooMailNeo@web161605.mail.bf1.yahoo.com"
      type="cite">
      <div style="color:#000; background-color:#fff; font-family:arial,
        helvetica, sans-serif;font-size:14pt">
        <div><font face="Times New Roman" size="3">
          </font><font size="3"><font face="Calibri">Dear All<!--?xml:namespace prefix = o ns = "urn:schemas-microsoft-com:office:office" /--><o:p></o:p></font></font></div>
        <div><font face="Times New Roman" size="3">
          </font></div>
        <div style="margin: 0in 0in 10pt;" class="MsoNormal"><font
            size="3"><font face="Calibri">I am wondering if type 344
              related with outdoor swimming
              pool have been updated or not. In fact, I tried to heat
              the pool using solar
              system by connecting the solar collector via input number
              15 and 16, but I found
              that the temperature of the pool wasn’t raised regardless
              of the collector
              area. Do you any suggestions in this regards?<o:p></o:p></font></font></div>
        <div><font face="Times New Roman" size="3">
          </font></div>
        <div style="margin: 0in 0in 10pt;" class="MsoNormal"><font
            size="3"><font face="Calibri">Best Regards<o:p></o:p></font></font></div>
        <div><font face="Times New Roman" size="3">
          </font><span style="line-height: 115%; font-family:
            "Calibri","sans-serif"; font-size: 11pt;
            mso-ascii-theme-font: minor-latin; mso-fareast-font-family:
            Calibri; mso-fareast-theme-font: minor-latin;
            mso-hansi-theme-font: minor-latin; mso-bidi-font-family:
            Arial; mso-bidi-theme-font: minor-bidi; mso-ansi-language:
            EN-US; mso-fareast-language: EN-US; mso-bidi-language:
            AR-SA;">Nidal Abdalla</span></div>
      </div>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <br>
      <pre wrap="">_______________________________________________
TRNSYS-users mailing list
<a class="moz-txt-link-abbreviated" href="mailto:TRNSYS-users@cae.wisc.edu">TRNSYS-users@cae.wisc.edu</a>
<a class="moz-txt-link-freetext" href="https://mailman.cae.wisc.edu/listinfo/trnsys-users">https://mailman.cae.wisc.edu/listinfo/trnsys-users</a>
</pre>
    </blockquote>
    <br>
    <pre class="moz-signature" cols="72">-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI  53703 USA

P:+1.608.274.2577
F:+1.608.278.1475
<a class="moz-txt-link-abbreviated" href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>

<a class="moz-txt-link-freetext" href="http://www.tess-inc.com">http://www.tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.trnsys.com">http://www.trnsys.com</a></pre>
    <br>
    <br>
  </body>
</html>