    Eva,<br>
      Either method will work. I would lean towards drawing the building
    in Trnsys3D and drawing the balconies as shading surfaces. Once you
    get to TRNBuild, make sure to tell it to generate the shading mask.
    Once you do, the building form and the location of the balconies
    will be taken into account as far as shading the windows goes.<br>
    <br>
      For Type34, you would need one instance of Type34 for each shaded
    surface that you want to consider. The surface can be either a wall
    or a window but you must define a new orientation in TRNBuild for
    each surface that is going to receive a different amount of solar
    radiation.<br>
    <br>
      I think Type67 is not appropriate in this case; it was designed to
    deal with objects that shade the building from nearby (like another
    building across the street) and is not set up to deal with objects
    that shade a surface from above (like a balcony does).<br>
    <br>
    Kind regards,<br>
     David<br>
    <br>
    <br>
    <div class="moz-cite-prefix">On 7/3/2012 17:10, Eva gklezakou wrote:<br>
    </div>
    <blockquote
cite="mid:CA+Ci=p9Az13znjbKzeQq3u27opApUVoX7jfGq=CxdaLo2a_zVA@mail.gmail.com"
      type="cite">Dear Sirs,
      <div><br>
      </div>
      <div>I model a two storey building with balconies in all
        elevations so the first floor is shaded by the balconies of the
        above floor. How can I model the balconies? If I model them in
        type 56 does the shading from taken into account? Do I have to
        use type 34 (shading from overhangs)? If yes do I have to use as
        many components of type 34 as the number of the openings (each
        component describe only one opening with overhangs)? Can I
        approach this case with type 67 (shading mask)?</div>
      <div>Thank you.</div>
      <div><br>
      </div>
      <div>Regards,</div>
      <div>Eva</div>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <br>
      <pre wrap="">_______________________________________________
TRNSYS-users mailing list
<a class="moz-txt-link-abbreviated" href="mailto:TRNSYS-users@cae.wisc.edu">TRNSYS-users@cae.wisc.edu</a>
<a class="moz-txt-link-freetext" href="https://mailman.cae.wisc.edu/listinfo/trnsys-users">https://mailman.cae.wisc.edu/listinfo/trnsys-users</a>
</pre>
    </blockquote>
    <br>
    <pre class="moz-signature" cols="72">-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI  53703 USA

P:+1.608.274.2577
F:+1.608.278.1475
<a class="moz-txt-link-abbreviated" href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>

<a class="moz-txt-link-freetext" href="http://www.tess-inc.com">http://www.tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.trnsys.com">http://www.trnsys.com</a></pre>
    <br>
    <br>
  </body>
</html>