    Paul,<br>
      TRNBuild/Type56 will allow you to set the boundary temperature
    either as a "identical" or as a constant, an input, or a schedule.
    You want to select "userdefined" then click on the little arrow
    button to the left of the constant boundary temperature that pops
    up. Change from "constant" to "input." Go back to the Simulation
    Studio, right click on Type56 and tell it to update the input list.
    Once it does, you should see your the boundary temperature as an
    input. Read in your measured boundary temperature using type9 and
    pass the appropriate output to Type56.<br>
    Best,<br>
     david<br>
    <br>
    <br>
    <div class="moz-cite-prefix">On 7/3/2012 08:48, Paul OSullivan
      wrote:<br>
    </div>
    <blockquote
      cite="mid:9C81D54E1F5A8742A57CD251DCFD30BA02380CD2@CITMAIL.cit.ie"
      type="cite">
      <meta http-equiv="Content-Type" content="text/html;
        charset=ISO-8859-1">
      <meta name="Generator" content="MS Exchange Server version
        6.5.7638.1">
      <title>Use of a varying boundary wall temperature profile - (Paul
        O Sullivan)</title>
      <!-- Converted from text/plain format -->
      <p><font size="2">Hi TRNSYS Users.<br>
          <br>
          I am trying to establish if it is possible to use a measured
          temperature profile as the specified boundary condition for an
          internal boundary wall. I am measuring surface temperatures on
          both sides of the internal walls of the single room being used
          to validate a TRNSYS model. This means I could consider using
          this data as the boundary condition for these walls instead of
          modelling adjacent spaces to the room of interest. Does
          TRNBUILD only accept a single value for this condition or is
          there a way to apply a time varying boundary condition.
          Alternatively I can use an average over the period of analysis
          but this will give some inaccuracy to the model.<br>
          <br>
          Thanks for your help. !<br>
          <br>
          Paul O Sullivan<br>
          Cork Institute of Technology.<br>
          Ireland.<br>
          <br>
        </font>
      </p>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <br>
      <pre wrap="">_______________________________________________
TRNSYS-users mailing list
<a class="moz-txt-link-abbreviated" href="mailto:TRNSYS-users@cae.wisc.edu">TRNSYS-users@cae.wisc.edu</a>
<a class="moz-txt-link-freetext" href="https://mailman.cae.wisc.edu/listinfo/trnsys-users">https://mailman.cae.wisc.edu/listinfo/trnsys-users</a>
</pre>
    </blockquote>
    <br>
    <pre class="moz-signature" cols="72">-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI  53703 USA

P:+1.608.274.2577
F:+1.608.278.1475
<a class="moz-txt-link-abbreviated" href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>

<a class="moz-txt-link-freetext" href="http://www.tess-inc.com">http://www.tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.trnsys.com">http://www.trnsys.com</a></pre>
    <br>
    <br>
  </body>
</html>