If you are using 3d sketchup plugin, then look to the virtual partition option. This creates (when imported into trnsbuild x2 airnodes for one zone, in essance 2 zones. bear in mind that there is no air exchange between the two zones...for this you need to use a "coupling". It is basically like two zones, but for the radiation exchanges.<br>
<br><div class="gmail_quote">On 2 July 2012 14:34, Eva gklezakou <span dir="ltr"><<a href="mailto:gklezakoue@gmail.com" target="_blank">gklezakoue@gmail.com</a>></span> wrote:<br><blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex">
Dear Sirs,<div><br></div><div>I model a multi-zone building and there are two adjacent zones which do not have inter-zonal wall between them, because of the geometry and the orientation I decided not to model them as one zone. How can I assign the lack of inter-zonal wall, is it enough if I set an air layer as the only wall's material? Do I have to assign any other parameter in order to be more accurate?</div>

<div>Thank you.</div><div><br></div><div>Regards,</div><div>Eva</div>