<html>
  <head>
    <meta content="text/html; charset=ISO-8859-1"
      http-equiv="Content-Type">
  </head>
  <body bgcolor="#FFFFFF" text="#000000">
    Camilo,<br>
      I am not familiar with the table that is mentioned. The
    documentation notes that values for Kair0 are typically between 7
    and 11 kJ/h.K.m2 and Kair1 are between 14 and 18 (kJ/h.m2)/K/(m/s).
    What I have typically done is to use some basic heat transfer
    equations to calculate the Nusselt number for a few different flow
    rates through the ducts as a function of the Reynolds and Prandtl
    numbers. From the Nusselt number, you can then get the inside
    convection coefficient and fit the values to arrive at Kair0 and
    Kair1. I think my method over predicts the inside convection
    coefficient but I haven't found a better way to do it<br>
    <br>
     One critical thing about earth tubes is to keep the flow turbulent.
    Without knowing what kind of input changes you made in your
    simulation between the cases that do and do not show total energy
    differences across the earth duct it is hard to guess what might be
    happening.<br>
    Best,<br>
     David<br>
    <br>
    <br>
    On 6/24/2012 01:38, Camilo Arias wrote:
    <blockquote
      cite="mid:1340519910.46570.YahooMailNeo@web114706.mail.gq1.yahoo.com"
      type="cite">
      <div style="color:#000; background-color:#fff; font-family:arial,
        helvetica, sans-serif;font-size:10pt">
        <div><font face="arial, helvetica, sans-serif" size="2">Hi, i´m
            working now with the type 460, in the FAQ file sended by
            transsolar, said abaout a table to chose the Kair0 and Kair1
            based in the diameter of the tube, i write to trnsssolar but
            to now an not have a answare, maybe you have this
            information, also, i make some probes share the result the
            total energy (latent and sensible) with
            a psychometric entalphy difference by the same flow mass
            rate, the result are the same in the most parts, but for
            some ones show some differences, do you know the reason of
            this?.</font></div>
        <div style="font-family: arial, helvetica, sans-serif;
          font-size: 10pt; "><br>
        </div>
        <div style="font-family: arial, helvetica, sans-serif;
          font-size: 10pt; ">Thanks</div>
        <div style="font-family: arial, helvetica, sans-serif;
          font-size: 10pt; "><br>
        </div>
        <div style="font-family: arial, helvetica, sans-serif;
          font-size: 10pt; ">Camilo Arias </div>
      </div>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <br>
      <pre wrap="">_______________________________________________
TRNSYS-users mailing list
<a class="moz-txt-link-abbreviated" href="mailto:TRNSYS-users@cae.wisc.edu">TRNSYS-users@cae.wisc.edu</a>
<a class="moz-txt-link-freetext" href="https://mailman.cae.wisc.edu/listinfo/trnsys-users">https://mailman.cae.wisc.edu/listinfo/trnsys-users</a>
</pre>
    </blockquote>
    <br>
    <pre class="moz-signature" cols="72">-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI  53703 USA

P:+1.608.274.2577
F:+1.608.278.1475
<a class="moz-txt-link-abbreviated" href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>

<a class="moz-txt-link-freetext" href="http://www.tess-inc.com">http://www.tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.trnsys.com">http://www.trnsys.com</a></pre>
  </body>
</html>