<font size="4">Dear Adrien JEZEQUEL,<br><br>Many thanks for your patient reply and checking for my programs.<br><br>You are right. The problem is indeed Internal Gains. I define a Schedule based on your advice. After running, it seems better than the previous. However, there are some unreasonable situations. Please see the Attached image.<br>
1. Tair and Top are higher than the set point 21 °C in winter all the time. Tair is closed to 23 °C basically, and it is only 21 °C when no occupancy. I guess the reason is the compensation of internal gains and mechanical ventilation.<br>
Do you have some solutions to make sure that the set point is 21 °C in winter?<br><br>2.Tair and Top are lower than the set point 26 °C in summer all the time. The maximal is only 25.4 °C. I guess the reason is due to the influence of mechanical ventilation, and only a few hot days (Toutdoor>26 °C) in summer.<br>
I would like to ensure that the set point is 26 °C in summer. Do you have some solutions to that problem? Only reduce air change rate of mechanical ventilation? Anything else?<br><br>3.Qinf and Qvent are different all over the year although the infiltration rate and ventilation rate settings are the same all over the year. I think Since the weather conditions especially outdoor temperature, wind direction and wind velocity are different all over the year. Am I right?<br>
<br>4. Based on Energy_zone.BAL file, Qcool is 0 all the time. Do you have some ideas? I think it is due to mechanical ventilation and only a few hot days (Toutdoor>26 °C) in summer. Anything else reasons?<br><br>Many thanks in advance!<br>
<br>Br.<br><br>wang</font><br><br><br><br><br><br><br><br><div class="gmail_quote">2012/6/13 ITF - Adrien JEZEQUEL <span dir="ltr"><<a href="mailto:a.jezequel@itf.biz" target="_blank">a.jezequel@itf.biz</a>></span><br>
<blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex">
<div bgcolor="#FFFFFF" text="#000000">
Dear Wang,<div class="im"><br>
<br>
You are right : the Tcool I gave you was equal to 26, not to 24°C.
Tset value is not important as well, the most important is that you
understand how to do to define Tset.<br>
In your model, your heating and cooling advices seem to work fine.
Your problem comes frome your internal gain : 31 people are defined
all the time in a room of approximatively 80 m², without schedule. <br>
Because of your important internal gains, air temperature increases
until 35°C in winter. Then air temperature is refreshed because
Tcool = 35°C in winter.<br></div>
In summer, air is cooled at 24°C, because this is the temperature
you define in your cooling advice.<div class="im"><br>
<br>
Best regards<br>
<div>
<hr color="#3300FF" size="2" width="450" align="LEFT">
<table border="0">
<tbody>
<tr>
<td rowspan="3" width="120">
<center><a href="http://www.itf.biz" target="_blank"><img src="cid:part1.02090304.08050202@itf.biz" alt="www.itf.biz" border="0" height="103" width="66"></a><br>
<font color=" #0000FF" face="CALIBRI" size="1"><a href="http://www.itf.biz" target="_blank">www.itf.biz</a></font></center>
</td>
<td colspan="2"><font color="#000000" face="CALIBRI">Adrien JEZEQUEL<br>
Simulations Thermiques Dynamiques</font></td>
</tr>
<tr>
<td align="LEFT"> <font color="#0000FF" face="CALIBRI" size="4"><b>ITF</b></font><br>
</td>
<td><font color="#0000FF" face="CALIBRI">62, Rue du
Bolliet<br>
73230 St Alban Leysse<br>
FRANCE<br>
</font></td>
</tr>
<tr>
<td width="40" align="LEFT"><font color="#0000FF" face="CALIBRI"> Phone :<br>
Fax :<br>
Mail:<br>
</font>
</td>
<td><font color="#0000FF" face="CALIBRI"> +33(0)
479 750 029<br>
<a href="tel:%2B33%280%29%20479%20852%20122" value="+33479852122" target="_blank">+33(0) 479 852 122</a><br>
<a href="mailto:a.jezequel@itf.biz" target="_blank">a.jezequel@itf.biz</a>
ou <a href="mailto:aj@itf.biz" target="_blank">aj@itf.biz</a></font></td>
</tr>
</tbody>
</table>
<i><font color="#008000" face="CALIBRI" size="1">Afin de
contribuer au respect de l'environnement, merci de n'imprimer
cet e-mail que si nécessaire<br>
<font color="#008000" face="CALIBRI" size="1">Please, consider
our environmental responsability before printing this email<br>
</font></font></i><font color="#008000" face="CALIBRI" size="1"><font color="#008000" face="CALIBRI" size="1">
</font></font></div>
<br></div>
Le 12/06/2012 18:19, 王洋 a écrit :
<div><div class="h5"><blockquote type="cite"><font size="4">Dear Adrien Jezequel,<br>
<br>
Thanks for your quick reply!<br>
</font><font size="4"><font face="Arial">Tcool = 35 - 9 * Summer </font></font><font size="4">means</font><font size="4"> if in summer, Tcool = 26
°C?<br>
<br>
I tried </font><font size="4">to run the simulation based on
your solution</font><font size="4"><font face="Arial"> Tcool =
35 - 9 * Summer</font>, the result is also like the last
Attached.<br>
Oppositely, </font><font size="4"><font face="Arial">it is not
my heating system seems to work all the time, it is my cooling</font></font><font size="4"><font face="Arial"> system seems to work all the time</font>.<br>
I set internal gains all the year.<br>
<br>
Please see the Attached *.tpf and *.bui files, if you have free
time , please help me have a look and give me some solutions.<br>
<br>
Many thanks in advance!<br>
<br>
Br.<br>
<br>
wang</font><br>
<br>
<br>
<div class="gmail_quote">2012/6/12 ITF - Adrien JEZEQUEL <span dir="ltr"><<a href="mailto:a.jezequel@itf.biz" target="_blank">a.jezequel@itf.biz</a>></span><br>
<blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex">
<div bgcolor="#FFFFFF" text="#000000"> <font size="-1"><font face="Arial">Or sorry, I made a mistake in my previous
mail :<br>
</font></font>
<ul>
<li><font size="-1"><font face="Arial">Tcool = 35 - 9 *
Summer (instead of 35*winter - 9*summer) <br>
</font></font></li>
</ul>
<font size="-1"><font face="Arial">Regarding your heating
system it may be something like :<br>
</font></font>
<ul>
<li><font size="-1"><font face="Arial">Theat = 21*Winter</font></font></li>
</ul>
<font size="-1"><font face="Arial">Regarding your attached
picture, your heating system seems to work all the time.
<br>
In summer, either you cool at 21°C, either there is no
internal gains defined, and you heat at 21°C.<br>
Check your differents inputs.<br>
You can procede step by step (internal gain = 0,
ventilation = 0, infiltration rate = 0...) to see the
influence of each parameters in your model to catch your
issue.<br>
<br>
Best regards<br>
</font></font>
<div>
<div>
<hr color="#3300FF" size="2" width="450" align="LEFT">
<table border="0">
<tbody>
<tr>
<td rowspan="3" width="120">
<center><a href="http://www.itf.biz" target="_blank"><img src="https://mail.google.com/mail/?ui=2&view=bsp&ver=ohhl4rw8mbn4" alt="www.itf.biz" border="0" height="103" width="66"></a><br>
<font color=" #0000FF" face="CALIBRI" size="1"><a href="http://www.itf.biz" target="_blank">www.itf.biz</a></font></center>
</td>
<td colspan="2"><font color="#000000" face="CALIBRI">Adrien JEZEQUEL<br>
Simulations Thermiques Dynamiques</font></td>
</tr>
<tr>
<td align="LEFT"> <font color="#0000FF" face="CALIBRI" size="4"><b>ITF</b></font><br>
</td>
<td><font color="#0000FF" face="CALIBRI">62, Rue
du Bolliet<br>
73230 St Alban Leysse<br>
FRANCE<br>
</font></td>
</tr>
<tr>
<td width="40" align="LEFT"><font color="#0000FF" face="CALIBRI"> Phone :<br>
Fax :<br>
Mail:<br>
</font> </td>
<td><font color="#0000FF" face="CALIBRI"> +33(0)
479 750 029<br>
<a href="tel:%2B33%280%29%20479%20852%20122" value="+33479852122" target="_blank">+33(0)
479 852 122</a><br>
<a href="mailto:a.jezequel@itf.biz" target="_blank">a.jezequel@itf.biz</a> ou <a href="mailto:aj@itf.biz" target="_blank">aj@itf.biz</a></font></td>
</tr>
</tbody>
</table>
<i><font color="#008000" face="CALIBRI" size="1">Afin de
contribuer au respect de l'environnement, merci de
n'imprimer cet e-mail que si nécessaire<br>
<font color="#008000" face="CALIBRI" size="1">Please,
consider our environmental responsability before
printing this email<br>
</font></font></i><font color="#008000" face="CALIBRI" size="1"><font color="#008000" face="CALIBRI" size="1"> </font></font></div>
<br>
</div>
Le 12/06/2012 17:47, 王洋 a écrit :
<div>
<div>
<blockquote type="cite"><font size="4">Dear Adrien
Jezequel,<br>
<br>
</font><font color="#000000" size="4">Many thanks!</font><font size="4"><br style="color:rgb(51,51,255)">
</font>
<p style="color:rgb(51,51,255)"><font size="4">I think
you'd better put for cooling temperatures <br>
</font> </p>
<font size="4"><span style="color:rgb(51,51,255)"> </span></font>
<ul style="color:rgb(51,51,255)">
<li><font size="4">35°C in winter (no cool) -
heating temperature at 21°C<br>
</font> </li>
<li><font size="4">24°C in summer</font></li>
</ul>
<font size="4"><span style="color:rgb(51,51,255)">
which may be translated in an equation tool by
something like :</span><br style="color:rgb(51,51,255)">
<span style="color:rgb(51,51,255)"> </span></font>
<ul style="color:rgb(51,51,255)">
<li><font size="4">summer =
GE(TIME,2162)*LT(TIME,6552)</font></li>
<li><font size="4">winter = 1 - summer<br>
</font> </li>
<li><font size="4">Tcool = 35*Winter - 9*Summer</font></li>
</ul>
<font size="4">For <span style="color:rgb(51,51,255)">Tcool
= 35*Winter - 9*Summer</span>, do you mean if in
winter, Tcool = 35 °C, so Cooling doesn't work ; if
in summer, Tcool = -9°C or 24 °C?<br>
<br>
Meanwhile, another weird phenomena appear: After
running based on your solution in winter, indoor
temperature becomes 35 °C also not 21 °C, although I
set heating temperature as 21 °C; in summer,
however, indoor temperature becomes 21 °C. Please
see the Attached On-Line Plotter image.<br>
Furthermore, when I create another Tcool equation as
<span style="color:rgb(51,51,255)">35*winter+24*summer</span>,
the result is also like the Attached On-Line Plotter
image.<br>
<br>
Please give me some solutions or advices! <br>
I think the point how to set that Cooling doesn't
work in winter? The possible reason of that problem
is that I also set a Mechanical Ventilation in
winter (Tset=19 °C) and summer </font><font size="4">(Tset=17 °C). I guess Maybe </font><font size="4">the Mechanical Ventilation will influence
on Cooling and heating?</font><br>
<font size="4"><br>
Many thanks in advance!<br>
<br>
Br.<br>
<br>
wang </font><br>
<br>
<br>
<div class="gmail_quote">2012/6/12 <span dir="ltr"><<a href="mailto:trnsys-users-request@cae.wisc.edu" target="_blank">trnsys-users-request@cae.wisc.edu</a>></span><br>
<blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex">Send
TRNSYS-users mailing list submissions to<br>
<a href="mailto:trnsys-users@cae.wisc.edu" target="_blank">trnsys-users@cae.wisc.edu</a><br>
<br>
To subscribe or unsubscribe via the World Wide
Web, visit<br>
<a href="https://mailman.cae.wisc.edu/listinfo/trnsys-users" target="_blank">https://mailman.cae.wisc.edu/listinfo/trnsys-users</a><br>
or, via email, send a message with subject or body
'help' to<br>
<a href="mailto:trnsys-users-request@cae.wisc.edu" target="_blank">trnsys-users-request@cae.wisc.edu</a><br>
<br>
You can reach the person managing the list at<br>
<a href="mailto:trnsys-users-owner@cae.wisc.edu" target="_blank">trnsys-users-owner@cae.wisc.edu</a><br>
<br>
When replying, please edit your Subject line so it
is more specific<br>
than "Re: Contents of TRNSYS-users digest..."<br>
<br>
Today's Topics:<br>
<br>
1. Re: TRNSYS-users Digest, Vol 90, Issue 23<br>
(<a href="mailto:jose.gonzalez@imdea.org" target="_blank">jose.gonzalez@imdea.org</a>)<br>
2. Re: weird Qcool (ITF - Adrien JEZEQUEL)<br>
3. Flue gas stack in TRNSYS (Mazen Darwish)<br>
4. AutoReply: TRNSYS-users Digest, Vol 90, Issue
23<br>
(<a href="mailto:kelelo1@kelelo.com" target="_blank">kelelo1@kelelo.com</a>)<br>
<br>
<br>
---------- 已转发邮件 ----------<br>
From: <<a href="mailto:jose.gonzalez@imdea.org" target="_blank">jose.gonzalez@imdea.org</a>><br>
To: <a href="mailto:trnsys-users@cae.wisc.edu" target="_blank">trnsys-users@cae.wisc.edu</a><br>
Cc: <br>
Date: Tue, 12 Jun 2012 14:56:21 +0200 (CEST)<br>
Subject: Re: [TRNSYS-users] TRNSYS-users Digest,
Vol 90, Issue 23<br>
I am out of the office from Monday, June 11 to
Friday, June 15 and unable to respond at this
time.<br>
<br>
For any urgent matters, please contact Dr. Manuel
Romero (<a href="http://manuel.romero_at_imdea.org" target="_blank">manuel.romero_at_imdea.org</a>).<br>
<br>
Thank you for your understanding.<br>
<br>
Best regards,<br>
<br>
José Gonzalez-Aguilar<br>
<br>
<br>
<br>
---------- 已转发邮件 ----------<br>
From: ITF - Adrien JEZEQUEL <<a href="mailto:a.jezequel@itf.biz" target="_blank">a.jezequel@itf.biz</a>><br>
To: <a href="mailto:trnsys-users@cae.wisc.edu" target="_blank">trnsys-users@cae.wisc.edu</a><br>
Cc: <br>
Date: Tue, 12 Jun 2012 15:26:28 +0200<br>
Subject: Re: [TRNSYS-users] weird Qcool<br>
<div bgcolor="#FFFFFF" text="#000000"> <font size="-1"><font face="Arial">Dear Wang,<br>
<br>
As far as I understand, the cooling set
temperature you define in your model is :<br>
</font></font>
<ul>
<li><font size="-1"><font face="Arial">24°C in
summer, which seems to be correct</font></font></li>
<li><font size="-1"><font face="Arial">and 0°C
in winter... which seems to be wrong,
since you don't refresh your thermal
zone at 0°C in winter!<br>
</font></font></li>
</ul>
T<font size="-1"><font face="Arial">hat's why
you obtain huge cooling loads.<br>
BAL_ENERGY is not 0 because you heat and
cool in the same time in winter.<br>
</font></font>
<p>I think you'd better put for cooling
temperatures <br>
</p>
<ul>
<li>35°C in winter (no cool) - heating
temperature at 21°C<br>
</li>
<li>24°C in summer</li>
</ul>
which may be translated in an equation tool by
something like :<br>
<ul>
<li>summer = GE(TIME,2162)*LT(TIME,6552)</li>
<li>winter = 1 - summer<br>
</li>
<li>Tcool = 35*Winter - 9*Summer</li>
</ul>
<p>Best regards<br>
</p>
<div>
<hr color="#3300FF" size="2" width="450" align="LEFT">
<table border="0">
<tbody>
<tr>
<td rowspan="3" width="120">
<center><a href="http://www.itf.biz" target="_blank"><img src="https://mail.google.com/mail/?ui=2&view=bsp&ver=ohhl4rw8mbn4" alt="www.itf.biz" border="0" height="103" width="66"></a><br>
<font color=" #0000FF" face="CALIBRI" size="1"><a href="http://www.itf.biz" target="_blank">www.itf.biz</a></font></center>
</td>
<td colspan="2"><font color="#000000" face="CALIBRI">Adrien JEZEQUEL<br>
Simulations Thermiques Dynamiques</font></td>
</tr>
<tr>
<td align="LEFT"> <font color="#0000FF" face="CALIBRI" size="4"><b>ITF</b></font><br>
</td>
<td><font color="#0000FF" face="CALIBRI">62,
Rue du Bolliet<br>
73230 St Alban Leysse<br>
FRANCE<br>
</font></td>
</tr>
<tr>
<td width="40" align="LEFT"><font color="#0000FF" face="CALIBRI">
Phone :<br>
Fax :<br>
Mail:<br>
</font> </td>
<td><font color="#0000FF" face="CALIBRI">
<a href="tel:%2B33%280%29%20479%20750%20029" value="+33479750029" target="_blank">+33(0) 479 750 029</a><br>
<a href="tel:%2B33%280%29%20479%20852%20122" value="+33479852122" target="_blank">+33(0) 479 852 122</a><br>
<a href="mailto:a.jezequel@itf.biz" target="_blank">a.jezequel@itf.biz</a>
ou <a href="mailto:aj@itf.biz" target="_blank">aj@itf.biz</a></font></td>
</tr>
</tbody>
</table>
<i><font color="#008000" face="CALIBRI" size="1">Afin de contribuer au respect de
l'environnement, merci de n'imprimer cet
e-mail que si nécessaire<br>
<font color="#008000" face="CALIBRI" size="1">Please, consider our
environmental responsability before
printing this email<br>
</font></font></i><font color="#008000" face="CALIBRI" size="1"><font color="#008000" face="CALIBRI" size="1"> </font></font></div>
<br>
Le 12/06/2012 14:55, 王洋 a écrit :
<blockquote type="cite"><font size="4">Dear all,<br>
<br>
I make a simulation. The cooling set
temperature is 24*Summer schedule (2162 h to
6552 h), The heating set temperature is
21*Winter schedule (the rest hours). After
running, however, it appears WEIRD
phenomenon. Please see the ATTACHED
Energy_zone.BAL file. During the winter
period, there are Qcools and Qcool is very
large up to 47000 kJ. And then it results in
wrong BAL_ENERG, it is not 0.<br>
<br>
Please give me some advices and solutions to
that!<br>
<br>
Many thanks in advance!<br>
<br>
Br.<br>
<br>
wang </font><br>
<br>
<div class="gmail_quote">2012/6/11 <span dir="ltr"><<a href="mailto:trnsys-users-request@cae.wisc.edu" target="_blank">trnsys-users-request@cae.wisc.edu</a>></span><br>
<blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex">Send
TRNSYS-users mailing list submissions to<br>
<a href="mailto:trnsys-users@cae.wisc.edu" target="_blank">trnsys-users@cae.wisc.edu</a><br>
<br>
To subscribe or unsubscribe via the World
Wide Web, visit<br>
<a href="https://mailman.cae.wisc.edu/listinfo/trnsys-users" target="_blank">https://mailman.cae.wisc.edu/listinfo/trnsys-users</a><br>
or, via email, send a message with subject
or body 'help' to<br>
<a href="mailto:trnsys-users-request@cae.wisc.edu" target="_blank">trnsys-users-request@cae.wisc.edu</a><br>
<br>
You can reach the person managing the list
at<br>
<a href="mailto:trnsys-users-owner@cae.wisc.edu" target="_blank">trnsys-users-owner@cae.wisc.edu</a><br>
<br>
When replying, please edit your Subject
line so it is more specific<br>
than "Re: Contents of TRNSYS-users
digest..."<br>
<br>
Today's Topics:<br>
<br>
1. Re: TRNSYS-users Digest, Vol 90,
Issue 21<br>
(<a href="mailto:jose.gonzalez@imdea.org" target="_blank">jose.gonzalez@imdea.org</a>)<br>
2. AutoReply: TRNSYS-users Digest, Vol
90, Issue 21<br>
(<a href="mailto:kelelo1@kelelo.com" target="_blank">kelelo1@kelelo.com</a>)<br>
3. type666 (Andr?s Montero)<br>
4. Type 673 heating problem (Santeri
Siren)<br>
<br>
<br>
---------- 已转发邮件 ----------<br>
From: <<a href="mailto:jose.gonzalez@imdea.org" target="_blank">jose.gonzalez@imdea.org</a>><br>
To: <a href="mailto:trnsys-users@cae.wisc.edu" target="_blank">trnsys-users@cae.wisc.edu</a><br>
Cc: <br>
Date: Mon, 11 Jun 2012 16:07:28 +0200
(CEST)<br>
Subject: Re: [TRNSYS-users] TRNSYS-users
Digest, Vol 90, Issue 21<br>
I am out of the office from Monday, June
11 to Friday, June 15 and unable to
respond at this time.<br>
<br>
For any urgent matters, please contact Dr.
Manuel Romero (<a href="http://manuel.romero_at_imdea.org" target="_blank">manuel.romero_at_imdea.org</a>).<br>
<br>
Thank you for your understanding.<br>
<br>
Best regards,<br>
<br>
José Gonzalez-Aguilar<br>
<br>
<br>
<br>
---------- 已转发邮件 ----------<br>
From: <a href="mailto:kelelo1@kelelo.com" target="_blank">kelelo1@kelelo.com</a><br>
To: <a href="mailto:trnsys-users@cae.wisc.edu" target="_blank">trnsys-users@cae.wisc.edu</a><br>
Cc: <br>
Date: Mon, 11 Jun 2012 14:10:47 GMT<br>
Subject: [TRNSYS-users] AutoReply:
TRNSYS-users Digest, Vol 90, Issue 21<br>
<br>
I will be out of the office from June 8 -
23 on a backpacking trip with my son and
his Venture Crew at Philmont Scout Ranch
in New Mexico. I will not have access to
email or phone service while I am gone,
but I will reply to your message as soon
as possible after I return to the office
on Monday, June 25th.<br>
<br>
Thank you for your patience,<br>
Mark Thornbloom<br>
<br>
<br>
<br>
<br>
---------- 已转发邮件 ----------<br>
From: "Andrés Montero" <<a href="mailto:andresmonteroi@gmail.com" target="_blank">andresmonteroi@gmail.com</a>><br>
To: <a href="mailto:trnsys-users@cae.wisc.edu" target="_blank">trnsys-users@cae.wisc.edu</a><br>
Cc: <br>
Date: Mon, 11 Jun 2012 16:57:30 +0200<br>
Subject: [TRNSYS-users] type666<br>
Dear Trnsys users,
<div><br>
</div>
<div>In order to simulate a water-cooled
chiller, first I need to create the 2
external files for this component. </div>
<div>I'm trying to find some catalogues
with information of a 40 to 45 kW
water-cooled chiller but the web pages I
run into it, ask me to register, but I'm
still waiting the username and pasword.
Does anyone has a catalgoue with this
type of info regarding this cooling
capacity machine?</div>
<div><br>
</div>
<div>Best regards,</div>
<div><br>
</div>
<div>Andrés<br clear="all">
<div><br>
</div>
-- <br>
Andrés Montero I.<br>
<br>
</div>
<br>
<br>
---------- 已转发邮件 ----------<br>
From: Santeri Siren <<a href="mailto:santeri.siren1@gmail.com" target="_blank">santeri.siren1@gmail.com</a>><br>
To: "trnsys käyttäjät" <<a href="mailto:trnsys-users@cae.wisc.edu" target="_blank">trnsys-users@cae.wisc.edu</a>><br>
Cc: <br>
Date: Mon, 11 Jun 2012 19:56:40 +0300<br>
Subject: [TRNSYS-users] Type 673 heating
problem<br>
Dear all,<br>
<br>
I cant make type673 heating mode to work.
Cooling mode works just fine but when I
change the cooling control signal to 0 and
heating control signal to 1 it doesnt work
anymore. When the heating mode is used
nothing happens. Does anyone know why?<br>
<br>
Best regards,<br>
Santeri Siren<br>
<br>
_______________________________________________<br>
TRNSYS-users mailing list<br>
<a href="mailto:TRNSYS-users@cae.wisc.edu" target="_blank">TRNSYS-users@cae.wisc.edu</a><br>
<a href="https://mailman.cae.wisc.edu/listinfo/trnsys-users" target="_blank">https://mailman.cae.wisc.edu/listinfo/trnsys-users</a><br>
<br>
</blockquote>
</div>
<br>
<br>
<fieldset></fieldset>
<br>
<pre>_______________________________________________
TRNSYS-users mailing list
<a href="mailto:TRNSYS-users@cae.wisc.edu" target="_blank">TRNSYS-users@cae.wisc.edu</a>
<a href="https://mailman.cae.wisc.edu/listinfo/trnsys-users" target="_blank">https://mailman.cae.wisc.edu/listinfo/trnsys-users</a>
</pre>
</blockquote>
</div>
<br>
<br>
---------- 已转发邮件 ----------<br>
From: Mazen Darwish <<a href="mailto:mazentd@gmail.com" target="_blank">mazentd@gmail.com</a>><br>
To: <a href="mailto:trnsys-users@cae.wisc.edu" target="_blank">trnsys-users@cae.wisc.edu</a><br>
Cc: <br>
Date: Tue, 12 Jun 2012 16:05:51 +0200<br>
Subject: [TRNSYS-users] Flue gas stack in TRNSYS<br>
<div>Hello everyone ,</div>
<div> </div>
<div>Is there a way to model a flue gas stack in
TRNSYS , i need to recirculate hot air and flue
gases from the economizer in an HRSG back to a
solar tower .</div>
<div> </div>
<div>i appreciate your ideas.</div>
<div> </div>
<div>Mazen Darwish</div>
<div>KTH Royal Institute of Technology</div>
<div>Department of Energy Technology </div>
<div>Brinellvägen 68, SE-100 44 Stockholm, Sweden</div>
<div>Mobile: <a href="tel:%2B46-%280%29-723%2008%2018%2093" value="+46723081893" target="_blank">+46-(0)-723
08 18 93</a> </div>
<br>
<br>
---------- 已转发邮件 ----------<br>
From: <a href="mailto:kelelo1@kelelo.com" target="_blank">kelelo1@kelelo.com</a><br>
To: <a href="mailto:trnsys-users@cae.wisc.edu" target="_blank">trnsys-users@cae.wisc.edu</a><br>
Cc: <br>
Date: Tue, 12 Jun 2012 14:23:03 GMT<br>
Subject: [TRNSYS-users] AutoReply: TRNSYS-users
Digest, Vol 90, Issue 23<br>
<br>
I will be out of the office from June 8 - 23 on a
backpacking trip with my son and his Venture Crew
at Philmont Scout Ranch in New Mexico. I will not
have access to email or phone service while I am
gone, but I will reply to your message as soon as
possible after I return to the office on Monday,
June 25th.<br>
<br>
Thank you for your patience,<br>
Mark Thornbloom<br>
<br>
<br>
<br>
_______________________________________________<br>
TRNSYS-users mailing list<br>
<a href="mailto:TRNSYS-users@cae.wisc.edu" target="_blank">TRNSYS-users@cae.wisc.edu</a><br>
<a href="https://mailman.cae.wisc.edu/listinfo/trnsys-users" target="_blank">https://mailman.cae.wisc.edu/listinfo/trnsys-users</a><br>
<br>
</blockquote>
</div>
<br>
</blockquote>
</div>
</div>
</div>
</blockquote>
</div>
<br>
</blockquote>
</div></div></div>
</blockquote></div><br>