<html>
  <head>
    <meta content="text/html; charset=UTF-8" http-equiv="Content-Type">
  </head>
  <body bgcolor="#FFFFFF" text="#000000">
    Dear Wang,<br>
    <br>
    You are right : the Tcool I gave you was equal to 26, not to 24°C.
    Tset value is not important as well, the most important is that you
    understand how to do to define Tset.<br>
    In your model, your heating and cooling advices seem to work fine.
    Your problem comes frome your internal gain : 31 people are defined
    all the time in a room of approximatively 80 m², without schedule. <br>
    Because of your important internal gains, air temperature increases
    until 35°C in winter. Then air temperature is refreshed because
    Tcool = 35°C in winter.<br>
    In summer, air is cooled at 24°C, because this is the temperature
    you define in your cooling advice.<br>
    <br>
    Best regards<br>
    <div class="moz-signature">
      <hr align="LEFT" color="#3300FF" size="2" width="450">
      <table border="0">
        <tbody>
          <tr>
            <td rowspan="3" width="120">
              <center><a href="http://www.itf.biz"><img
                    src="cid:part1.02090304.08050202@itf.biz"
                    alt="www.itf.biz" border="0" height="103" width="66"></a><br>
                <font color=" #0000FF" face="CALIBRI" size="1"><a
                    href="http://www.itf.biz">www.itf.biz</a></font></center>
            </td>
            <td colspan="2"><font color="#000000" face="CALIBRI"
                size="2">Adrien JEZEQUEL<br>
                Simulations Thermiques Dynamiques</font></td>
          </tr>
          <tr>
            <td align="LEFT"> <font color="#0000FF" face="CALIBRI"
                size="4"><b>ITF</b></font><br>
            </td>
            <td><font color="#0000FF" face="CALIBRI" size="2">62, Rue du
                Bolliet<br>
                73230 St Alban Leysse<br>
                FRANCE<br>
              </font></td>
          </tr>
          <tr>
            <td align="LEFT" width="40"><font color="#0000FF"
                face="CALIBRI" size="2"> Phone :<br>
                Fax :<br>
                Mail:<br>
              </font>
            </td>
            <td><font color="#0000FF" face="CALIBRI" size="2"> +33(0)
                479 750 029<br>
                +33(0) 479 852 122<br>
                <a class="moz-txt-link-freetext"
                  href="mailto:a.jezequel@itf.biz">a.jezequel@itf.biz</a>
                ou <a class="moz-txt-link-freetext"
                  href="mailto:aj@itf.biz">aj@itf.biz</a></font></td>
          </tr>
        </tbody>
      </table>
      <i><font color="#008000" face="CALIBRI" size="1">Afin de
          contribuer au respect de l'environnement, merci de n'imprimer
          cet e-mail que si nécessaire<br>
          <font color="#008000" face="CALIBRI" size="1">Please, consider
            our environmental responsability before printing this email<br>
          </font></font></i><font color="#008000" face="CALIBRI"
        size="1"><font color="#008000" face="CALIBRI" size="1">
        </font></font></div>
    <br>
    Le 12/06/2012 18:19, 王洋 a écrit :
    <blockquote
cite="mid:CABF0dEuv7XDvunOjtO5vFoGSzjfBzpGU5QmGPKFG7Az6V+1NRw@mail.gmail.com"
      type="cite"><font size="4">Dear Adrien Jezequel,<br>
        <br>
        Thanks for your quick reply!<br>
      </font><font size="4"><font face="Arial">Tcool = 35 - 9 * Summer </font></font><font
        size="4">means</font><font size="4"> if in summer, Tcool = 26
        °C?<br>
        <br>
        I tried </font><font size="4">to run the simulation based on
        your solution</font><font size="4"><font face="Arial"> Tcool =
          35 - 9 * Summer</font>, the result is also like the last
        Attached.<br>
        Oppositely, </font><font size="4"><font face="Arial">it is not
          my heating system seems to work all the time, it is my cooling</font></font><font
        size="4"><font face="Arial"> system seems to work all the time</font>.<br>
        I set internal gains all the year.<br>
        <br>
        Please see the Attached *.tpf and *.bui files, if you have free
        time , please help me have a look and give me some solutions.<br>
        <br>
        Many thanks in advance!<br>
        <br>
        Br.<br>
        <br>
        wang</font><br>
      <br>
      <br>
      <div class="gmail_quote">2012/6/12 ITF - Adrien JEZEQUEL <span
          dir="ltr"><<a moz-do-not-send="true"
            href="mailto:a.jezequel@itf.biz" target="_blank">a.jezequel@itf.biz</a>></span><br>
        <blockquote class="gmail_quote" style="margin:0 0 0
          .8ex;border-left:1px #ccc solid;padding-left:1ex">
          <div bgcolor="#FFFFFF" text="#000000"> <font size="-1"><font
                face="Arial">Or sorry, I made a mistake in my previous
                mail :<br>
              </font></font>
            <ul>
              <li><font size="-1"><font face="Arial">Tcool = 35 - 9 *
                    Summer (instead of 35*winter  - 9*summer) <br>
                  </font></font></li>
            </ul>
            <font size="-1"><font face="Arial">Regarding your heating
                system it may be something like :<br>
              </font></font>
            <ul>
              <li><font size="-1"><font face="Arial">Theat = 21*Winter</font></font></li>
            </ul>
            <font size="-1"><font face="Arial">Regarding your attached
                picture, your heating system seems to work all the time.
                <br>
                In summer, either you cool at 21°C, either there is no
                internal gains defined, and you heat at 21°C.<br>
                Check your differents inputs.<br>
                You can procede step by step (internal gain = 0,
                ventilation = 0, infiltration rate = 0...) to see the
                influence of each parameters in your model to catch your
                issue.<br>
                <br>
                Best regards<br>
              </font></font>
            <div class="im">
              <div>
                <hr align="LEFT" color="#3300FF" size="2" width="450">
                <table border="0">
                  <tbody>
                    <tr>
                      <td rowspan="3" width="120">
                        <center><a moz-do-not-send="true"
                            href="http://www.itf.biz" target="_blank"><img
                              moz-do-not-send="true" src=""
                              alt="www.itf.biz" border="0" height="103"
                              width="66"></a><br>
                          <font color=" #0000FF" face="CALIBRI" size="1"><a
                              moz-do-not-send="true"
                              href="http://www.itf.biz" target="_blank">www.itf.biz</a></font></center>
                      </td>
                      <td colspan="2"><font color="#000000"
                          face="CALIBRI">Adrien JEZEQUEL<br>
                          Simulations Thermiques Dynamiques</font></td>
                    </tr>
                    <tr>
                      <td align="LEFT"> <font color="#0000FF"
                          face="CALIBRI" size="4"><b>ITF</b></font><br>
                      </td>
                      <td><font color="#0000FF" face="CALIBRI">62, Rue
                          du Bolliet<br>
                          73230 St Alban Leysse<br>
                          FRANCE<br>
                        </font></td>
                    </tr>
                    <tr>
                      <td align="LEFT" width="40"><font color="#0000FF"
                          face="CALIBRI"> Phone :<br>
                          Fax :<br>
                          Mail:<br>
                        </font> </td>
                      <td><font color="#0000FF" face="CALIBRI"> +33(0)
                          479 750 029<br>
                          <a moz-do-not-send="true"
                            href="tel:%2B33%280%29%20479%20852%20122"
                            value="+33479852122" target="_blank">+33(0)
                            479 852 122</a><br>
                          <a moz-do-not-send="true"
                            href="mailto:a.jezequel@itf.biz"
                            target="_blank">a.jezequel@itf.biz</a> ou <a
                            moz-do-not-send="true"
                            href="mailto:aj@itf.biz" target="_blank">aj@itf.biz</a></font></td>
                    </tr>
                  </tbody>
                </table>
                <i><font color="#008000" face="CALIBRI" size="1">Afin de
                    contribuer au respect de l'environnement, merci de
                    n'imprimer cet e-mail que si nécessaire<br>
                    <font color="#008000" face="CALIBRI" size="1">Please,
                      consider our environmental responsability before
                      printing this email<br>
                    </font></font></i><font color="#008000"
                  face="CALIBRI" size="1"><font color="#008000"
                    face="CALIBRI" size="1"> </font></font></div>
              <br>
            </div>
            Le 12/06/2012 17:47, 王洋 a écrit :
            <div>
              <div class="h5">
                <blockquote type="cite"><font size="4">Dear Adrien
                    Jezequel,<br>
                    <br>
                  </font><font color="#000000" size="4">Many thanks!</font><font
                    size="4"><br style="color:rgb(51,51,255)">
                  </font>
                  <p style="color:rgb(51,51,255)"><font size="4">I think
                      you'd better put for cooling temperatures <br>
                    </font> </p>
                  <font size="4"><span style="color:rgb(51,51,255)"> </span></font>
                  <ul style="color:rgb(51,51,255)">
                    <li><font size="4">35°C in winter (no cool) -
                        heating temperature at 21°C<br>
                      </font> </li>
                    <li><font size="4">24°C in summer</font></li>
                  </ul>
                  <font size="4"><span style="color:rgb(51,51,255)">
                      which may be translated in an equation tool by
                      something like :</span><br
                      style="color:rgb(51,51,255)">
                    <span style="color:rgb(51,51,255)"> </span></font>
                  <ul style="color:rgb(51,51,255)">
                    <li><font size="4">summer =
                        GE(TIME,2162)*LT(TIME,6552)</font></li>
                    <li><font size="4">winter = 1 - summer<br>
                      </font> </li>
                    <li><font size="4">Tcool = 35*Winter - 9*Summer</font></li>
                  </ul>
                  <font size="4">For <span style="color:rgb(51,51,255)">Tcool
                      = 35*Winter - 9*Summer</span>, do you mean if in
                    winter, Tcool = 35 °C, so Cooling doesn't work ; if
                    in summer, Tcool = -9°C or 24 °C?<br>
                    <br>
                    Meanwhile, another weird phenomena appear: After
                    running based on your solution in winter, indoor
                    temperature becomes 35 °C also not 21 °C, although I
                    set heating temperature as 21 °C; in summer,
                    however, indoor temperature becomes 21 °C. Please
                    see the Attached On-Line Plotter image.<br>
                    Furthermore, when I create another Tcool equation as
                    <span style="color:rgb(51,51,255)">35*winter+24*summer</span>,
                    the result is also like the Attached On-Line Plotter
                    image.<br>
                    <br>
                    Please give me some solutions or advices! <br>
                    I think the point how to set that Cooling doesn't
                    work in winter? The possible reason of that problem
                    is that I also set a Mechanical Ventilation in
                    winter (Tset=19 °C) and summer </font><font
                    size="4">(Tset=17 °C). I guess Maybe </font><font
                    size="4">the Mechanical Ventilation will influence
                    on Cooling and heating?</font><br>
                  <font size="4"><br>
                    Many thanks in advance!<br>
                    <br>
                    Br.<br>
                    <br>
                    wang  </font><br>
                  <br>
                  <br>
                  <div class="gmail_quote">2012/6/12 <span dir="ltr"><<a
                        moz-do-not-send="true"
                        href="mailto:trnsys-users-request@cae.wisc.edu"
                        target="_blank">trnsys-users-request@cae.wisc.edu</a>></span><br>
                    <blockquote class="gmail_quote" style="margin:0 0 0
                      .8ex;border-left:1px #ccc solid;padding-left:1ex">Send
                      TRNSYS-users mailing list submissions to<br>
                             <a moz-do-not-send="true"
                        href="mailto:trnsys-users@cae.wisc.edu"
                        target="_blank">trnsys-users@cae.wisc.edu</a><br>
                      <br>
                      To subscribe or unsubscribe via the World Wide
                      Web, visit<br>
                             <a moz-do-not-send="true"
                        href="https://mailman.cae.wisc.edu/listinfo/trnsys-users"
                        target="_blank">https://mailman.cae.wisc.edu/listinfo/trnsys-users</a><br>
                      or, via email, send a message with subject or body
                      'help' to<br>
                             <a moz-do-not-send="true"
                        href="mailto:trnsys-users-request@cae.wisc.edu"
                        target="_blank">trnsys-users-request@cae.wisc.edu</a><br>
                      <br>
                      You can reach the person managing the list at<br>
                             <a moz-do-not-send="true"
                        href="mailto:trnsys-users-owner@cae.wisc.edu"
                        target="_blank">trnsys-users-owner@cae.wisc.edu</a><br>
                      <br>
                      When replying, please edit your Subject line so it
                      is more specific<br>
                      than "Re: Contents of TRNSYS-users digest..."<br>
                      <br>
                      Today's Topics:<br>
                      <br>
                        1. Re: TRNSYS-users Digest, Vol 90, Issue 23<br>
                           (<a moz-do-not-send="true"
                        href="mailto:jose.gonzalez@imdea.org"
                        target="_blank">jose.gonzalez@imdea.org</a>)<br>
                        2. Re: weird Qcool (ITF - Adrien JEZEQUEL)<br>
                        3. Flue gas stack in TRNSYS (Mazen Darwish)<br>
                        4. AutoReply: TRNSYS-users Digest, Vol 90, Issue
                      23<br>
                           (<a moz-do-not-send="true"
                        href="mailto:kelelo1@kelelo.com" target="_blank">kelelo1@kelelo.com</a>)<br>
                      <br>
                      <br>
                      ---------- 已转发邮件 ----------<br>
                      From: <<a moz-do-not-send="true"
                        href="mailto:jose.gonzalez@imdea.org"
                        target="_blank">jose.gonzalez@imdea.org</a>><br>
                      To: <a moz-do-not-send="true"
                        href="mailto:trnsys-users@cae.wisc.edu"
                        target="_blank">trnsys-users@cae.wisc.edu</a><br>
                      Cc: <br>
                      Date: Tue, 12 Jun 2012 14:56:21 +0200 (CEST)<br>
                      Subject: Re: [TRNSYS-users] TRNSYS-users Digest,
                      Vol 90, Issue 23<br>
                      I am out of the office from Monday, June 11 to
                      Friday, June 15 and unable to respond at this
                      time.<br>
                      <br>
                      For any urgent matters, please contact Dr. Manuel
                      Romero (<a moz-do-not-send="true"
                        href="http://manuel.romero_at_imdea.org"
                        target="_blank">manuel.romero_at_imdea.org</a>).<br>
                      <br>
                      Thank you for your understanding.<br>
                      <br>
                      Best regards,<br>
                      <br>
                      José Gonzalez-Aguilar<br>
                      <br>
                      <br>
                      <br>
                      ---------- 已转发邮件 ----------<br>
                      From: ITF - Adrien JEZEQUEL <<a
                        moz-do-not-send="true"
                        href="mailto:a.jezequel@itf.biz" target="_blank">a.jezequel@itf.biz</a>><br>
                      To: <a moz-do-not-send="true"
                        href="mailto:trnsys-users@cae.wisc.edu"
                        target="_blank">trnsys-users@cae.wisc.edu</a><br>
                      Cc: <br>
                      Date: Tue, 12 Jun 2012 15:26:28 +0200<br>
                      Subject: Re: [TRNSYS-users] weird Qcool<br>
                      <div bgcolor="#FFFFFF" text="#000000"> <font
                          size="-1"><font face="Arial">Dear Wang,<br>
                            <br>
                            As far as I understand, the cooling set
                            temperature you define in your model is :<br>
                          </font></font>
                        <ul>
                          <li><font size="-1"><font face="Arial">24°C in
                                summer, which seems to be correct</font></font></li>
                          <li><font size="-1"><font face="Arial">and 0°C
                                in winter... which seems to be wrong,
                                since you don't refresh your thermal
                                zone at 0°C in winter!<br>
                              </font></font></li>
                        </ul>
                        T<font size="-1"><font face="Arial">hat's why
                            you obtain huge cooling loads.<br>
                            BAL_ENERGY is not 0 because you heat and
                            cool in the same time in winter.<br>
                          </font></font>
                        <p>I think you'd better put for cooling
                          temperatures <br>
                        </p>
                        <ul>
                          <li>35°C in winter (no cool) - heating
                            temperature at 21°C<br>
                          </li>
                          <li>24°C in summer</li>
                        </ul>
                        which may be translated in an equation tool by
                        something like :<br>
                        <ul>
                          <li>summer = GE(TIME,2162)*LT(TIME,6552)</li>
                          <li>winter = 1 - summer<br>
                          </li>
                          <li>Tcool = 35*Winter - 9*Summer</li>
                        </ul>
                        <p>Best regards<br>
                        </p>
                        <div>
                          <hr align="LEFT" color="#3300FF" size="2"
                            width="450">
                          <table border="0">
                            <tbody>
                              <tr>
                                <td rowspan="3" width="120">
                                  <center><a moz-do-not-send="true"
                                      href="http://www.itf.biz"
                                      target="_blank"><img
                                        moz-do-not-send="true" src=""
                                        alt="www.itf.biz" border="0"
                                        height="103" width="66"></a><br>
                                    <font color=" #0000FF"
                                      face="CALIBRI" size="1"><a
                                        moz-do-not-send="true"
                                        href="http://www.itf.biz"
                                        target="_blank">www.itf.biz</a></font></center>
                                </td>
                                <td colspan="2"><font color="#000000"
                                    face="CALIBRI">Adrien JEZEQUEL<br>
                                    Simulations Thermiques Dynamiques</font></td>
                              </tr>
                              <tr>
                                <td align="LEFT"> <font color="#0000FF"
                                    face="CALIBRI" size="4"><b>ITF</b></font><br>
                                </td>
                                <td><font color="#0000FF" face="CALIBRI">62,
                                    Rue du Bolliet<br>
                                    73230 St Alban Leysse<br>
                                    FRANCE<br>
                                  </font></td>
                              </tr>
                              <tr>
                                <td align="LEFT" width="40"><font
                                    color="#0000FF" face="CALIBRI">
                                    Phone :<br>
                                    Fax :<br>
                                    Mail:<br>
                                  </font> </td>
                                <td><font color="#0000FF" face="CALIBRI">
                                    +33(0) 479 750 029<br>
                                    <a moz-do-not-send="true"
                                      href="tel:%2B33%280%29%20479%20852%20122"
                                      value="+33479852122"
                                      target="_blank">+33(0) 479 852 122</a><br>
                                    <a moz-do-not-send="true"
                                      href="mailto:a.jezequel@itf.biz"
                                      target="_blank">a.jezequel@itf.biz</a>
                                    ou <a moz-do-not-send="true"
                                      href="mailto:aj@itf.biz"
                                      target="_blank">aj@itf.biz</a></font></td>
                              </tr>
                            </tbody>
                          </table>
                          <i><font color="#008000" face="CALIBRI"
                              size="1">Afin de contribuer au respect de
                              l'environnement, merci de n'imprimer cet
                              e-mail que si nécessaire<br>
                              <font color="#008000" face="CALIBRI"
                                size="1">Please, consider our
                                environmental responsability before
                                printing this email<br>
                              </font></font></i><font color="#008000"
                            face="CALIBRI" size="1"><font
                              color="#008000" face="CALIBRI" size="1"> </font></font></div>
                        <br>
                        Le 12/06/2012 14:55, 王洋 a écrit :
                        <blockquote type="cite"><font size="4">Dear all,<br>
                            <br>
                            I make a simulation. The cooling set
                            temperature is 24*Summer schedule (2162 h to
                            6552 h), The heating set temperature is
                            21*Winter schedule (the rest hours). After
                            running, however, it appears WEIRD
                            phenomenon. Please see the ATTACHED
                            Energy_zone.BAL file. During the winter
                            period, there are Qcools and Qcool is very
                            large up to 47000 kJ. And then it results in
                            wrong BAL_ENERG, it is not 0.<br>
                            <br>
                            Please give me some advices and solutions to
                            that!<br>
                            <br>
                            Many thanks in advance!<br>
                            <br>
                            Br.<br>
                            <br>
                            wang  </font><br>
                          <br>
                          <div class="gmail_quote">2012/6/11 <span
                              dir="ltr"><<a moz-do-not-send="true"
                                href="mailto:trnsys-users-request@cae.wisc.edu"
                                target="_blank">trnsys-users-request@cae.wisc.edu</a>></span><br>
                            <blockquote class="gmail_quote"
                              style="margin:0 0 0 .8ex;border-left:1px
                              #ccc solid;padding-left:1ex">Send
                              TRNSYS-users mailing list submissions to<br>
                                     <a moz-do-not-send="true"
                                href="mailto:trnsys-users@cae.wisc.edu"
                                target="_blank">trnsys-users@cae.wisc.edu</a><br>
                              <br>
                              To subscribe or unsubscribe via the World
                              Wide Web, visit<br>
                                     <a moz-do-not-send="true"
                                href="https://mailman.cae.wisc.edu/listinfo/trnsys-users"
                                target="_blank">https://mailman.cae.wisc.edu/listinfo/trnsys-users</a><br>
                              or, via email, send a message with subject
                              or body 'help' to<br>
                                     <a moz-do-not-send="true"
                                href="mailto:trnsys-users-request@cae.wisc.edu"
                                target="_blank">trnsys-users-request@cae.wisc.edu</a><br>
                              <br>
                              You can reach the person managing the list
                              at<br>
                                     <a moz-do-not-send="true"
                                href="mailto:trnsys-users-owner@cae.wisc.edu"
                                target="_blank">trnsys-users-owner@cae.wisc.edu</a><br>
                              <br>
                              When replying, please edit your Subject
                              line so it is more specific<br>
                              than "Re: Contents of TRNSYS-users
                              digest..."<br>
                              <br>
                              Today's Topics:<br>
                              <br>
                                1. Re: TRNSYS-users Digest, Vol 90,
                              Issue 21<br>
                                   (<a moz-do-not-send="true"
                                href="mailto:jose.gonzalez@imdea.org"
                                target="_blank">jose.gonzalez@imdea.org</a>)<br>
                                2. AutoReply: TRNSYS-users Digest, Vol
                              90, Issue 21<br>
                                   (<a moz-do-not-send="true"
                                href="mailto:kelelo1@kelelo.com"
                                target="_blank">kelelo1@kelelo.com</a>)<br>
                                3. type666 (Andr?s Montero)<br>
                                4. Type 673 heating problem (Santeri
                              Siren)<br>
                              <br>
                              <br>
                              ---------- 已转发邮件 ----------<br>
                              From: <<a moz-do-not-send="true"
                                href="mailto:jose.gonzalez@imdea.org"
                                target="_blank">jose.gonzalez@imdea.org</a>><br>
                              To: <a moz-do-not-send="true"
                                href="mailto:trnsys-users@cae.wisc.edu"
                                target="_blank">trnsys-users@cae.wisc.edu</a><br>
                              Cc: <br>
                              Date: Mon, 11 Jun 2012 16:07:28 +0200
                              (CEST)<br>
                              Subject: Re: [TRNSYS-users] TRNSYS-users
                              Digest, Vol 90, Issue 21<br>
                              I am out of the office from Monday, June
                              11 to Friday, June 15 and unable to
                              respond at this time.<br>
                              <br>
                              For any urgent matters, please contact Dr.
                              Manuel Romero (<a moz-do-not-send="true"
                                href="http://manuel.romero_at_imdea.org"
                                target="_blank">manuel.romero_at_imdea.org</a>).<br>
                              <br>
                              Thank you for your understanding.<br>
                              <br>
                              Best regards,<br>
                              <br>
                              José Gonzalez-Aguilar<br>
                              <br>
                              <br>
                              <br>
                              ---------- 已转发邮件 ----------<br>
                              From: <a moz-do-not-send="true"
                                href="mailto:kelelo1@kelelo.com"
                                target="_blank">kelelo1@kelelo.com</a><br>
                              To: <a moz-do-not-send="true"
                                href="mailto:trnsys-users@cae.wisc.edu"
                                target="_blank">trnsys-users@cae.wisc.edu</a><br>
                              Cc: <br>
                              Date: Mon, 11 Jun 2012 14:10:47 GMT<br>
                              Subject: [TRNSYS-users] AutoReply:
                              TRNSYS-users Digest, Vol 90, Issue 21<br>
                              <br>
                              I will be out of the office from June 8 -
                              23 on a backpacking trip with my son and
                              his Venture Crew at Philmont Scout Ranch
                              in New Mexico. I will not have access to
                              email or phone service while I am gone,
                              but I will reply to your message as soon
                              as possible after I return to the office
                              on Monday, June 25th.<br>
                              <br>
                              Thank you for your patience,<br>
                              Mark Thornbloom<br>
                              <br>
                              <br>
                              <br>
                              <br>
                              ---------- 已转发邮件 ----------<br>
                              From: "Andrés Montero" <<a
                                moz-do-not-send="true"
                                href="mailto:andresmonteroi@gmail.com"
                                target="_blank">andresmonteroi@gmail.com</a>><br>
                              To: <a moz-do-not-send="true"
                                href="mailto:trnsys-users@cae.wisc.edu"
                                target="_blank">trnsys-users@cae.wisc.edu</a><br>
                              Cc: <br>
                              Date: Mon, 11 Jun 2012 16:57:30 +0200<br>
                              Subject: [TRNSYS-users] type666<br>
                              Dear Trnsys users,
                              <div><br>
                              </div>
                              <div>In order to simulate a water-cooled
                                chiller, first I need to create the 2
                                external files for this component. </div>
                              <div>I'm trying to find some catalogues
                                with information of a 40 to 45 kW
                                water-cooled chiller but the web pages I
                                run into it, ask me to register, but I'm
                                still waiting the username and pasword.
                                Does anyone has a catalgoue with this
                                type of info regarding this cooling
                                capacity machine?</div>
                              <div><br>
                              </div>
                              <div>Best regards,</div>
                              <div><br>
                              </div>
                              <div>Andrés<br clear="all">
                                <div><br>
                                </div>
                                -- <br>
                                Andrés Montero I.<br>
                                <br>
                              </div>
                              <br>
                              <br>
                              ---------- 已转发邮件 ----------<br>
                              From: Santeri Siren <<a
                                moz-do-not-send="true"
                                href="mailto:santeri.siren1@gmail.com"
                                target="_blank">santeri.siren1@gmail.com</a>><br>
                              To: "trnsys käyttäjät" <<a
                                moz-do-not-send="true"
                                href="mailto:trnsys-users@cae.wisc.edu"
                                target="_blank">trnsys-users@cae.wisc.edu</a>><br>
                              Cc: <br>
                              Date: Mon, 11 Jun 2012 19:56:40 +0300<br>
                              Subject: [TRNSYS-users] Type 673 heating
                              problem<br>
                              Dear all,<br>
                              <br>
                              I cant make type673 heating mode to work.
                              Cooling mode works just fine but when I
                              change the cooling control signal to 0 and
                              heating control signal to 1 it doesnt work
                              anymore. When the heating mode is used
                              nothing happens. Does anyone know why?<br>
                              <br>
                              Best regards,<br>
                              Santeri Siren<br>
                              <br>
_______________________________________________<br>
                              TRNSYS-users mailing list<br>
                              <a moz-do-not-send="true"
                                href="mailto:TRNSYS-users@cae.wisc.edu"
                                target="_blank">TRNSYS-users@cae.wisc.edu</a><br>
                              <a moz-do-not-send="true"
                                href="https://mailman.cae.wisc.edu/listinfo/trnsys-users"
                                target="_blank">https://mailman.cae.wisc.edu/listinfo/trnsys-users</a><br>
                              <br>
                            </blockquote>
                          </div>
                          <br>
                          <br>
                          <fieldset></fieldset>
                          <br>
                          <pre>_______________________________________________
TRNSYS-users mailing list
<a moz-do-not-send="true" href="mailto:TRNSYS-users@cae.wisc.edu" target="_blank">TRNSYS-users@cae.wisc.edu</a>
<a moz-do-not-send="true" href="https://mailman.cae.wisc.edu/listinfo/trnsys-users" target="_blank">https://mailman.cae.wisc.edu/listinfo/trnsys-users</a>
</pre>
                        </blockquote>
                      </div>
                      <br>
                      <br>
                      ---------- 已转发邮件 ----------<br>
                      From: Mazen Darwish <<a moz-do-not-send="true"
                        href="mailto:mazentd@gmail.com" target="_blank">mazentd@gmail.com</a>><br>
                      To: <a moz-do-not-send="true"
                        href="mailto:trnsys-users@cae.wisc.edu"
                        target="_blank">trnsys-users@cae.wisc.edu</a><br>
                      Cc: <br>
                      Date: Tue, 12 Jun 2012 16:05:51 +0200<br>
                      Subject: [TRNSYS-users] Flue gas stack in TRNSYS<br>
                      <div>Hello everyone ,</div>
                      <div> </div>
                      <div>Is there a way to model a flue gas stack in
                        TRNSYS , i need to recirculate hot air and flue
                        gases from the economizer in an HRSG back to a
                        solar tower .</div>
                      <div> </div>
                      <div>i appreciate your ideas.</div>
                      <div> </div>
                      <div>Mazen Darwish</div>
                      <div>KTH Royal Institute of Technology</div>
                      <div>Department of Energy Technology </div>
                      <div>Brinellvägen 68, SE-100 44 Stockholm, Sweden</div>
                      <div>Mobile: <a moz-do-not-send="true"
                          href="tel:%2B46-%280%29-723%2008%2018%2093"
                          value="+46723081893" target="_blank">+46-(0)-723
                          08 18 93</a> </div>
                      <br>
                      <br>
                      ---------- 已转发邮件 ----------<br>
                      From: <a moz-do-not-send="true"
                        href="mailto:kelelo1@kelelo.com" target="_blank">kelelo1@kelelo.com</a><br>
                      To: <a moz-do-not-send="true"
                        href="mailto:trnsys-users@cae.wisc.edu"
                        target="_blank">trnsys-users@cae.wisc.edu</a><br>
                      Cc: <br>
                      Date: Tue, 12 Jun 2012 14:23:03 GMT<br>
                      Subject: [TRNSYS-users] AutoReply: TRNSYS-users
                      Digest, Vol 90, Issue 23<br>
                      <br>
                      I will be out of the office from June 8 - 23 on a
                      backpacking trip with my son and his Venture Crew
                      at Philmont Scout Ranch in New Mexico. I will not
                      have access to email or phone service while I am
                      gone, but I will reply to your message as soon as
                      possible after I return to the office on Monday,
                      June 25th.<br>
                      <br>
                      Thank you for your patience,<br>
                      Mark Thornbloom<br>
                      <br>
                      <br>
                      <br>
                      _______________________________________________<br>
                      TRNSYS-users mailing list<br>
                      <a moz-do-not-send="true"
                        href="mailto:TRNSYS-users@cae.wisc.edu"
                        target="_blank">TRNSYS-users@cae.wisc.edu</a><br>
                      <a moz-do-not-send="true"
                        href="https://mailman.cae.wisc.edu/listinfo/trnsys-users"
                        target="_blank">https://mailman.cae.wisc.edu/listinfo/trnsys-users</a><br>
                      <br>
                    </blockquote>
                  </div>
                  <br>
                </blockquote>
              </div>
            </div>
          </div>
        </blockquote>
      </div>
      <br>
    </blockquote>
  </body>
</html>