<html>
  <head>
    <meta content="text/html; charset=ISO-8859-1"
      http-equiv="Content-Type">
  </head>
  <body bgcolor="#FFFFFF" text="#000000">
    Mattia,<br>
      From the error message it appears as though there is a problem
    with the *.trn file. This file is generated by TRNBuild and contains
    the transfer function coefficients for the walls, floors, ceilings,
    and roofs of your Type56 building. I would recommend that you open
    your building (*.bui, or *.b17) and resave it to make sure that
    there is not an error saying that some of the wall transfer function
    coefficients could not be generated. If you are able to save the
    building file from TRNBuild and the simulation still will not run,
    please send the *.b17 and *.tpf to your distributor for assistance.<br>
    Kind regards,<br>
     David<br>
     <br>
    <br>
    On 6/13/2012 04:34, MATTIA ANDREA RIO wrote:
    <blockquote
      cite="mid:20120613113405.28563h1h8n8py084@webmail-stud.polimi.it"
      type="cite">hi!!!  I'm trying to launch my simulation in
      simulation studio: i would like to export the temperature of air
      node, in this case.
      <br>
      <br>
      however, when i start the simulatuion, this message of error (that
      you can see into link file) appears on my display.
      <br>
      <br>
      how does it mean???
      <br>
      <br>
      Thanks!
      <br>
      <br>
      ----------------------------------------------------------------
      <br>
      This message was sent using IMP, the Internet Messaging Program.
      <br>
      <br>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <br>
      <pre wrap="">_______________________________________________
TRNSYS-users mailing list
<a class="moz-txt-link-abbreviated" href="mailto:TRNSYS-users@cae.wisc.edu">TRNSYS-users@cae.wisc.edu</a>
<a class="moz-txt-link-freetext" href="https://mailman.cae.wisc.edu/listinfo/trnsys-users">https://mailman.cae.wisc.edu/listinfo/trnsys-users</a>
</pre>
    </blockquote>
    <br>
    <pre class="moz-signature" cols="72">-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI  53703 USA

P:+1.608.274.2577
F:+1.608.278.1475
<a class="moz-txt-link-abbreviated" href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>

<a class="moz-txt-link-freetext" href="http://www.tess-inc.com">http://www.tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.trnsys.com">http://www.trnsys.com</a></pre>
  </body>
</html>