    Kostas,<br>
      Pass the Type56 outputs to Type46 for integrating and printing to
    a text file.<br>
    Best,<br>
     david<br>
    <br>
    <br>
    On 6/8/2012 10:11, ts0g . wrote:
    <blockquote cite="mid:DUB109-W1285F744C12BABFF65D5099EAF20@phx.gbl"
      type="cite">
      <style><!--
.hmmessage P
{
margin:0px;
padding:0px
}
body.hmmessage
{
font-size: 10pt;
font-family:Tahoma
}
--></style>
      <div dir="ltr">
        <br>
        <div>Dear TRNSYS users ,<br>
          <br>
          I have imported a 3d model ,from trnsys 3d plug-in for
          sketchup, into the Simulation Studio. I am using Type56 to
          generate my building's air temperature ( TAIR ) ,<br>
           and the sensible heating&cooling demand of airnodes (
          QHEAT-QCOOL ) . I have created 5 different thermal airnodes
          and my question is , which type should I <br>
          use as an output in order to retrieve my results, after
          simulating, in a .txt file so I can process them and compare
          them with some theoretical measurements concerning <br>
          these specific thermal zones.<br>
          Thank you for your help !<br>
          <br>
          Kind regards,<br>
          Kostas <br>
          <br>
          <br>
          <br>
          <br>
          <br>
          --Forwarded Message Attachment--<br>
          From: <a class="moz-txt-link-abbreviated" href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a><br>
          CC: <a class="moz-txt-link-abbreviated" href="mailto:trnsys-users@cae.wisc.edu">trnsys-users@cae.wisc.edu</a><br>
          To: <a class="moz-txt-link-abbreviated" href="mailto:ricardo.palomar@hotmail.com">ricardo.palomar@hotmail.com</a><br>
          Date: Wed, 6 Jun 2012 14:09:13 -0500<br>
          Subject: Re: [TRNSYS-users] Type 1716: ROTARY DESICANT
          DEHUMIDIFIER<br>
          <br>
          Ricardo,<br>
            Without seeing the input file, its hard to know what the
          problem might be. If you can please send your project to me
          (directly, please do not reply to the entire list) then I can
          have a look.<br>
          Kind regards,<br>
           David<br>
          <br>
          <br>
          On 6/6/2012 06:03, Ricardo Palomar Calahorra wrote:
          <blockquote
            cite="mid:SNT135-W4A1A97505AAB2FBA793E2ED0D0@phx.gbl">
            <style>
.ExternalClass .ecxhmmessage P
{padding:0px;}
.ExternalClass body.ecxhmmessage
{font-size:10pt;font-family:Tahoma;}

</style>
            <div dir="ltr"> Hello !!!
              <div><br>
              </div>
              <div>I´m trying to use the type 1716: ROTARY DESICANT
                DEHUMIDIFIER, but I´m having always the same problem,
                when I run the simulation the outputs 8 and 12 (<font
                  size="2">Regeneration air relative humidity,
                  and Condensate flow rate) are "0.00". And the outputs
                  2 and 3 (Process air outlet humidity ratio, and <span
                    style="text-indent:-0.31in;text-align:left">Process</span><span
                    style="text-indent:-0.31in;text-align:left"> air </span><span
                    style="text-indent:-0.31in;text-align:left">outlet</span><span
                    style="text-indent:-0.31in;text-align:left"> </span><span
                    style="text-indent:-0.31in;text-align:left">relative</span><span
                    style="text-indent:-0.31in;text-align:left"> </span><span
                    style="text-indent:-0.31in;text-align:left">humidity)
                    are inconsistent.</span></font></div>
              <div><font size="2"><br>
                </font></div>
              <div><font size="2">Exist any problem running this type?</font></div>
              <div><font size="2"><br>
                </font></div>
              <div><font size="2">Thanks !!!</font></div>
            </div>
            <br>
            <fieldset class="ecxmimeAttachmentHeader"></fieldset>
            <br>
            <pre>_______________________________________________
TRNSYS-users mailing list
<a moz-do-not-send="true" class="ecxmoz-txt-link-abbreviated" href="mailto:TRNSYS-users@cae.wisc.edu">TRNSYS-users@cae.wisc.edu</a>
<a moz-do-not-send="true" class="ecxmoz-txt-link-freetext" href="https://mailman.cae.wisc.edu/listinfo/trnsys-users" target="_blank">https://mailman.cae.wisc.edu/listinfo/trnsys-users</a>
</pre>
          </blockquote>
          <br>
          <pre class="ecxmoz-signature">-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI  53703 USA

P:+1.608.274.2577
F:+1.608.278.1475
<a moz-do-not-send="true" class="ecxmoz-txt-link-abbreviated" href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>

<a moz-do-not-send="true" class="ecxmoz-txt-link-freetext" href="http://www.tess-inc.com" target="_blank">http://www.tess-inc.com</a>
<a moz-do-not-send="true" class="ecxmoz-txt-link-freetext" href="http://www.trnsys.com" target="_blank">http://www.trnsys.com</a></pre>
          <br>
          <br>
          --Forwarded Message Attachment--<br>
          From: <a class="moz-txt-link-abbreviated" href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a><br>
          CC: <a class="moz-txt-link-abbreviated" href="mailto:trnsys-users@cae.wisc.edu">trnsys-users@cae.wisc.edu</a><br>
          To: <a class="moz-txt-link-abbreviated" href="mailto:mattia.rio@mail.polimi.it">mattia.rio@mail.polimi.it</a><br>
          Date: Wed, 6 Jun 2012 14:14:47 -0500<br>
          Subject: Re: [TRNSYS-users] Shading groups<br>
          <br>
          Mattia,<br>
            I think you will have to be a little creative here. Shading
          devices in Trnsys3D are assumed to be opaque as you know so I
          don't think you can define the shading surface in there. You
          could use Type34, which models simple overhangs and/or
          wingwalls. That model also assumes an opaque shader but it
          gives outputs for various shading fractions and view factors.
          You may be able to use those and the unshaded radiation from
          your weather component to get an estimate of the radiation
          that comes through your not-quite-opaque device. Lastly,
          Type56 allows you to enter a shading factor for any given
          window. You may be able to treat your shaders in that manner.<br>
          <br>
            Unfortunately, there is not a direct way to treat
          semitransparent shaders unless you would care to modify
          Type34.<br>
          Kind regards,<br>
           David<br>
          <br>
          <br>
          On 6/6/2012 10:11, MATTIA ANDREA RIO wrote:
          <blockquote
            cite="mid:20120606171133.11635udywb2jwpc8@webmail-stud.polimi.it">Hi!!!
            i have a little problem with my imported 3d model from
            trnsys 3d plug-in for sketchup. <br>
            <br>
            I have posted a picture that show my 3d model in sketchup;
            so, as you can see, all of the triangular surfaces (into red
            circle), are made in perforated corten steel, and i need to
            give a shading coefficient to their, otherwise the  program
            will do the simulations considering the shading surfaces
            opaque; but actually they are not matt. <br>
            <br>
            if someone have any ideas about how I can do..... <br>
            <br>
            ----------------------------------------------------------------

            <br>
            This message was sent using IMP, the Internet Messaging
            Program. <br>
            <br>
            <br>
            <fieldset class="ecxmimeAttachmentHeader"></fieldset>
            <br>
            <pre>_______________________________________________
TRNSYS-users mailing list
<a moz-do-not-send="true" class="ecxmoz-txt-link-abbreviated" href="mailto:TRNSYS-users@cae.wisc.edu">TRNSYS-users@cae.wisc.edu</a>
<a moz-do-not-send="true" class="ecxmoz-txt-link-freetext" href="https://mailman.cae.wisc.edu/listinfo/trnsys-users" target="_blank">https://mailman.cae.wisc.edu/listinfo/trnsys-users</a>
</pre>
          </blockquote>
          <br>
          <pre class="ecxmoz-signature">-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI  53703 USA

P:+1.608.274.2577
F:+1.608.278.1475
<a moz-do-not-send="true" class="ecxmoz-txt-link-abbreviated" href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>

<a moz-do-not-send="true" class="ecxmoz-txt-link-freetext" href="http://www.tess-inc.com" target="_blank">http://www.tess-inc.com</a>
<a moz-do-not-send="true" class="ecxmoz-txt-link-freetext" href="http://www.trnsys.com" target="_blank">http://www.trnsys.com</a></pre>
          <br>
          <br>
          --Forwarded Message Attachment--<br>
          From: <a class="moz-txt-link-abbreviated" href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a><br>
          CC: <a class="moz-txt-link-abbreviated" href="mailto:trnsys-users@cae.wisc.edu">trnsys-users@cae.wisc.edu</a><br>
          To: <a class="moz-txt-link-abbreviated" href="mailto:damien.casetta@gmail.com">damien.casetta@gmail.com</a><br>
          Date: Wed, 6 Jun 2012 14:27:41 -0500<br>
          Subject: Re: [TRNSYS-users] Water-to-water heat pump - Heat
          rate to load control<br>
          <br>
          Damien,<br>
            In my experience, there are relatively few heat pumps
          available on the market that can do what you are trying to do.
          Most heat pumps have a fairly fixed capacity (some have
          multiple stages) so that they have an easier time maintaining
          a fixed temperature rise than they do in maintaining a fixed
          temperature outlet. There is at least one notable exception to
          this; an air-to-water heat pump that has a variable speed
          compressor that allows it to modulate and maintain a target
          outlet temperature. <br>
          <br>
            Type927 is a temperature level control device meaning that
          it is looking for inlet water conditions on both sides and for
          a control signal. If you have obtained your heating loads from
          some other software tool, I would recommend that you read them
          into TRNSYS using Type9 and impose them on a water stream
          using Type682 from the TESS Loads and Structures library. I
          would then place a thermostat sensing water return temperature
          in the loop and I would use its output to turn on the loop
          pump and the Type927 heat pump. You will not get a constant
          supply temperature of course but in reality, a single stage
          (or even multi stage) heat pump can't really give you a
          constant supply temperature; it can only give you a supply
          temperature that hovers around a set point.  <br>
          <br>
            If you are using Type56 to generate your building's heating
          demand, I would take it out of energy rate control (ie turn
          OFF the automatic heating and cooling types in TRNBuild), and
          allow the zone temperatures to float. I would then use a
          thermostat watching the zone air temperature and some kind of
          delivery device (a fan coil, radiant floors, etc.) to deliver
          the hot water from the Type927 to the zone.<br>
          <br>
          Kind regards,<br>
           david<br>
          <br>
          <br>
          On 6/6/2012 12:20, Damien Casetta wrote:
          <blockquote
cite="mid:CA+b-pK5xyb7k19Qy-x4a2uFB_4U3kTrP94qs=G4O26Urwy=K2w@mail.gmail.com">Hi, 

            <div><br>
            </div>
            <div>I am trying to handle this problem by controlling the
              temperature. Let me remind you that I want to control the
              heat load of an heat pump in heating mode. </div>
            <div><br>
            </div>
            <div>Here is how I am trying to proceed : </div>
            <div><br>
            </div>
            <div>- I control the temperature exiting the heat pump</div>
            <div>- I fix a temperature set point (with an aquastat -
              heating mode) at 50 C.  </div>
            <div>- I vary the supply temperature (entering the heat
              pump) according to the heating demand. </div>
            <div><br>
            </div>
            <div>The heating demand is based on hourly loads. </div>
            <div><br>
            </div>
            <div>What do you think about it? </div>
            <div><br>
            </div>
            <div>I am not very satisfied but I will give it a try. I am
              sure there is a much simpler way to do it. </div>
            <div><br>
            </div>
            <div><br>
            </div>
            <div>Thanks in advance for your help. </div>
            <div><br>
            </div>
            <div>Best regards,<br>
              <br>
              <div class="ecxgmail_quote">On 1 June 2012 18:10, Damien
                Casetta <span dir="ltr"><<a moz-do-not-send="true"
                    href="mailto:damien.casetta@gmail.com">damien.casetta@gmail.com</a>></span>
                wrote:<br>
                <blockquote class="ecxgmail_quote"
                  style="border-left:1px #ccc solid;padding-left:1ex">Hi, 

                  <div><br>
                  </div>
                  <div>I am modelling a ground-source heat pump system
                    including a water-to-water heat pump (type 927), a
                    borehole heat exchanger (type 557b) and a building
                    demand profile. </div>
                  <div><br>
                  </div>
                  <div>I have read a couple of messages in the archives
                    about this topic but I haven´t understood correctly
                    the few addressing my specific issue. </div>
                  <div><br>
                  </div>
                  <div>Here is my point. I assume the heat pump to meet
                    the building demand. The aim is then to force the
                    heat pump load and observe how the system behaves
                    (COP, ground loop fluid temperatures). </div>
                  <div><br>
                  </div>
                  <div>I would be able to do this with an external
                    MATLAB code (with COP values interpolated from
                    catalog data) but it would be a shame not to harness
                    TRNSYS potential (there is no need to re-invent the
                    wheel as I read in a previous message). </div>
                  <div><br>
                  </div>
                  <div>Let me put in other words: how to control a heat
                    pump load? </div>
                  <div><br>
                  </div>
                  <div>I have read about a trick to handle this, with a
                    "lump" temperature but I don't get the idea behind
                    it. Any other explanations is welcomed. </div>
                  <div><br>
                  </div>
                  <div><br>
                  </div>
                  <div><br>
                  </div>
                  <div>Thanks in advance,</div>
                  <div><br>
                  </div>
                  <div>Best regards,<span class="ecxHOEnZb"><font
                        color="#888888"><br clear="all">
                        <div><br>
                        </div>
                        <div><br>
                        </div>
                        -- <br>
                        <div><font color="#999999"><b>Damien Casetta</b></font></div>
                        <div><br>
                        </div>
                        <div><font color="#009900"><span
                              style="line-height:19px;font-size:13px;font-family:sans-serif"><b>Chalmers

                                University of Technology </b></span>|
                            Energy and Environment</font><span
                            style="color:rgb(153,153,153)"> </span><font
                            color="#999999">| Exchange student</font></div>
                        <div><font color="#3366FF"><b>INSA Lyon</b>
                            Génie Energétique et Environnement</font> <span
                            style="color:rgb(153,153,153)">| Elève
                            ingénieur</span> </div>
                        <div> <span style="color:rgb(153,153,153)"> <br>
                            <a moz-do-not-send="true" target="_blank">+46.7.60.66.31.45</a><br>
                          </span></div>
                        <div><font color="#999999"><a
                              moz-do-not-send="true" target="_blank">+33.6.71.78.03.75</a></font></div>
                        <br>
                      </font></span></div>
                </blockquote>
              </div>
              <br>
              <br clear="all">
              <div><br>
              </div>
              -- <br>
              <div><font color="#999999"><b>Damien Casetta</b></font></div>
              <div><br>
              </div>
              <div><font color="#009900"><span
style="font-family:sans-serif;font-size:13px;line-height:19px;background-color:rgb(255,255,255)"><b>Chalmers

                      University of Technology </b></span>| Energy and
                  Environment</font><span style="color:rgb(153,153,153)"> </span><font
                  color="#999999">| Exchange student</font></div>
              <div><font color="#3366FF"><b>INSA Lyon</b> Génie
                  Energétique et Environnement</font> <span
                  style="color:rgb(153,153,153)">| Elève ingénieur</span> </div>
              <div> <span style="color:rgb(153,153,153)"> <br>
                  +46.7.60.66.31.45<br>
                </span></div>
              <div><font color="#999999">+33.6.71.78.03.75</font></div>
              <br>
            </div>
            <br>
            <fieldset class="ecxmimeAttachmentHeader"></fieldset>
            <br>
            <pre>_______________________________________________
TRNSYS-users mailing list
<a moz-do-not-send="true" class="ecxmoz-txt-link-abbreviated" href="mailto:TRNSYS-users@cae.wisc.edu">TRNSYS-users@cae.wisc.edu</a>
<a moz-do-not-send="true" class="ecxmoz-txt-link-freetext" href="https://mailman.cae.wisc.edu/listinfo/trnsys-users" target="_blank">https://mailman.cae.wisc.edu/listinfo/trnsys-users</a>
</pre>
          </blockquote>
          <br>
          <pre class="ecxmoz-signature">-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI  53703 USA

P:+1.608.274.2577
F:+1.608.278.1475
<a moz-do-not-send="true" class="ecxmoz-txt-link-abbreviated" href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>

<a moz-do-not-send="true" class="ecxmoz-txt-link-freetext" href="http://www.tess-inc.com" target="_blank">http://www.tess-inc.com</a>
<a moz-do-not-send="true" class="ecxmoz-txt-link-freetext" href="http://www.trnsys.com" target="_blank">http://www.trnsys.com</a></pre>
        </div>
      </div>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <br>
      <pre wrap="">_______________________________________________
TRNSYS-users mailing list
<a class="moz-txt-link-abbreviated" href="mailto:TRNSYS-users@cae.wisc.edu">TRNSYS-users@cae.wisc.edu</a>
<a class="moz-txt-link-freetext" href="https://mailman.cae.wisc.edu/listinfo/trnsys-users">https://mailman.cae.wisc.edu/listinfo/trnsys-users</a>
</pre>
    </blockquote>
    <br>
    <pre class="moz-signature" cols="72">-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI  53703 USA

P:+1.608.274.2577
F:+1.608.278.1475
<a class="moz-txt-link-abbreviated" href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>

<a class="moz-txt-link-freetext" href="http://www.tess-inc.com">http://www.tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.trnsys.com">http://www.trnsys.com</a></pre>
  </body>
</html>