<html>
  <head>
    <meta content="text/html; charset=UTF-8" http-equiv="Content-Type">
  </head>
  <body bgcolor="#FFFFFF" text="#000000">
    Sara,<br>
     There is not a limitation on the number of Type88s that you can
    have in a simulation. I would recommend that if you are trying to
    maintain a particular temperature in the rooms, you use Type108
    instead of Type2. Type2's controls are based on temperature
    differences, not on a specific temperature set point. While Type2
    can be set up in order to maintain a specific temperature Type108 is
    somewhat more intuitive. <br>
    Kind regards,<br>
     David<br>
    <br>
    <br>
    On 5/16/2012 03:20, Guilbert Sara wrote:
    <blockquote
cite="mid:CANAV46xB-ysZBJU=m64bQi5UF4WSfU6SXV5Ba9K_s6e=CHnmng@mail.gmail.com"
      type="cite">
      <p class="MsoNormal"><span style="font-family:"Segoe
          Print"" lang="EN-US">Hi all, </span></p>
      <p class="MsoNormal"><span style="font-family:"Segoe
          Print"" lang="EN-US">I modeled on trnsys
          a chilled water system with two type 88, two fans (type 3),
          two coils (type 52),
          two type 92 and just one pump (type 110) </span></p>
      <p class="MsoNormal"><span style="font-family:"Segoe
          Print"" lang="EN-US">I regulate the room’s
          temperature with a controller (type 2)</span></p>
      <p class="MsoNormal"><span style="font-family:"Segoe
          Print"" lang="EN-US">I don’t know why
          but I change the upper dead band dt for one room like 25 °C
          for the first room
          and 24°C for the other room and when I start the simulation
          the both room are
          going to 25°C, the two rooms have exactly the same behavior.
          The two rooms have
          always the same behavior with different features at the
          beginning. </span></p>
      <p class="MsoNormal"><span style="font-family:"Segoe
          Print"" lang="EN-US">Maybe because I can’t
          use two type 88 in the same project or something like that.</span></p>
      <p class="MsoNormal"><span style="font-family:"Segoe
          Print"" lang="EN-US"> </span></p>
      <p class="MsoNormal"><span style="font-family:"Segoe
          Print"" lang="EN-US">Thank you for your
          help</span></p>
      <p class="MsoNormal"><span style="font-family:"Segoe
          Print"" lang="EN-US">Sara</span></p>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <br>
      <pre wrap="">_______________________________________________
TRNSYS-users mailing list
<a class="moz-txt-link-abbreviated" href="mailto:TRNSYS-users@cae.wisc.edu">TRNSYS-users@cae.wisc.edu</a>
<a class="moz-txt-link-freetext" href="https://mailman.cae.wisc.edu/listinfo/trnsys-users">https://mailman.cae.wisc.edu/listinfo/trnsys-users</a>
</pre>
    </blockquote>
    <br>
    <pre class="moz-signature" cols="72">-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI  53703 USA

P:+1.608.274.2577
F:+1.608.278.1475
<a class="moz-txt-link-abbreviated" href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>

<a class="moz-txt-link-freetext" href="http://www.tess-inc.com">http://www.tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.trnsys.com">http://www.trnsys.com</a></pre>
  </body>
</html>