Juan Francisco,<br>
When you draw your building in Trnsys3D, you will need to perform
either an automatic or a manual surface matching so that the wall
that separates the two zones is listed as ADJACENT in both. Once you
import your *.idf into TRNBuild, you should see the ADJACENT wall
listed in both zones. Go to the wall typemanager and select the
ADJACENT wall type (note, you may want to make a copy of this wall
and give it a new name in case you have more than one type of
adjacent wall in your building). You can now change the layers to be
whatever you like. Note that at the top of the layer list there is
text that says "front/inside." This means that the first layer in
the list is denoted as the "front" of the wall. Lastly, go to the
zone that contains the "front" of the wall, select the ADJACENT wall
in that zone and make sure that the radio button below says "front."
If it says "back," simply change it to "front."<br>
Best,<br>
David<br>
<br>
<br>
On 5/16/2012 02:50, JUAN FRANCISCO BELMONTE TOLEDO wrote:
<blockquote cite="mid:1BEA4308-4F86-4BFB-AEAC-ED0A6B3F4276@mimectl"
type="cite">
<div dir="ltr" id="idOWAReplyText22853">
<div dir="ltr"><font color="#000000" face="Theano Modern"
size="3">hello again.</font></div>
<div dir="ltr"><font face="Theano Modern">i´m sorry my question
was not completely defined, i meant an adjacent wall (or
ceiling) with non-simmetric material layers.</font></div>
<div dir="ltr"><font face="Theano Modern">Regards.</font></div>
<div dir="ltr"> </div>
</div>
<div id="idSignature76323">
<div><font color="#000000" face="Arial">
<div style="MARGIN: 0cm 0cm 0pt" class="MsoNormal"><em><span
style="FONT-STYLE: normal; FONT-FAMILY: 'Comic Sans
MS'; COLOR: blue; FONT-SIZE: 8pt; mso-bidi-font-style:
italic"><font size="1">Juan Francisco Belmonte Toledo</font></span></em><span
style="FONT-FAMILY: 'Comic Sans MS'; COLOR: blue;
FONT-SIZE: 8pt; mso-bidi-font-style: italic"><br>
</span></div>
</font>
<div style="MARGIN: 0cm 0cm 0pt" class="MsoNormal"><font
color="#000000" face="Arial"><span style="FONT-FAMILY:
'Comic Sans MS'; COLOR: blue; FONT-SIZE: 8pt;
mso-bidi-font-style: italic"><font size="1"><em><span
style="FONT-STYLE: normal; FONT-FAMILY: 'Comic
Sans MS'; mso-bidi-font-style: italic">Universidad
de Castilla-La Mancha</span></em><br>
<em><span style="FONT-STYLE: normal; FONT-FAMILY:
'Comic Sans MS'; mso-bidi-font-style: italic">Campus
Universitario. Avda. de España, s/n</span></em><br>
<em><span style="FONT-STYLE: normal; FONT-FAMILY:
'Comic Sans MS'; mso-bidi-font-style: italic">02071
Albacete. Spain </span></em></font></span><span
style="FONT-FAMILY: 'Comic Sans MS'; FONT-SIZE: 8pt"><br>
<br>
</span></font>
<hr tabindex="-1">
<font face="Tahoma" size="2"><b>De:</b> David BRADLEY<br>
<b>Enviado el:</b> Mar 15/05/2012 19:31<br>
<b>Para:</b> JUAN FRANCISCO BELMONTE TOLEDO<br>
<b>CC:</b> <a class="moz-txt-link-abbreviated" href="mailto:trnsys-users@cae.wisc.edu">trnsys-users@cae.wisc.edu</a><br>
<b>Asunto:</b> Re: [TRNSYS-users] NON-SYMMETRIC ADJACENT
WALLS<br>
</font><br>
</div>
</div>
</div>
<div>Juan Francisco,<br>
I may be misinterpreting what you mean by non-symmetric
adjacent walls. However, if it is the case I am imagining, you
have a zone containing one wall that is adjacent to two other
zones (draw a large box with a T-shape in it so that you have
one box on top and two smaller boxes underneath). In this case,
you have to break up the wall in the zone on top into two walls,
each one adjacent to a single zone. The zone on top will end up
having 5 walls instead of 4.<br>
Kind regards,<br>
David<br>
<br>
On 5/15/2012 03:12, JUAN FRANCISCO BELMONTE TOLEDO wrote:
<blockquote type="cite">
<div dir="ltr" id="idOWAReplyText70582">
<div dir="ltr"><font color="#000000" face="Theano Modern"
size="3">hello all.</font></div>
<div dir="ltr"> </div>
<div dir="ltr"><font face="Theano Modern">Is there a way to
create non-symmetric adjacent walls in TRNSYS3D or
TRNBUILD?</font></div>
<div dir="ltr"> </div>
<div dir="ltr"><font face="Theano Modern">Regards.</font></div>
<div dir="ltr"> </div>
</div>
<div dir="ltr" id="idSignature84849">
<div><font color="#000000" face="Arial">
<div style="MARGIN: 0cm 0cm 0pt" class="MsoNormal"><em><span
style="FONT-STYLE: normal; FONT-FAMILY: 'Comic
Sans MS'; COLOR: blue; FONT-SIZE: 8pt;
mso-bidi-font-style: italic"><font size="1">Juan
Francisco Belmonte Toledo</font></span></em><span
style="FONT-FAMILY: 'Comic Sans MS'; COLOR: blue;
FONT-SIZE: 8pt; mso-bidi-font-style: italic"><br>
</span></div>
<div style="MARGIN: 0cm 0cm 0pt" class="MsoNormal"><span
style="FONT-FAMILY: 'Comic Sans MS'; COLOR: blue;
FONT-SIZE: 8pt; mso-bidi-font-style: italic"><font
size="1"><em><span style="FONT-STYLE: normal;
FONT-FAMILY: 'Comic Sans MS';
mso-bidi-font-style: italic">Universidad de
Castilla-La Mancha</span></em><br>
<em><span style="FONT-STYLE: normal; FONT-FAMILY:
'Comic Sans MS'; mso-bidi-font-style: italic">Campus
Universitario. Avda. de España, s/n</span></em><br>
<em><span style="FONT-STYLE: normal; FONT-FAMILY:
'Comic Sans MS'; mso-bidi-font-style: italic">02071
Albacete. Spain </span></em></font></span><span
style="FONT-FAMILY: 'Comic Sans MS'; FONT-SIZE: 8pt"><br>
<br>
</span></div>
</font></div>
</div>
<br>
<fieldset class="mimeAttachmentHeader"></fieldset>
<br>
<pre wrap="">_______________________________________________
TRNSYS-users mailing list
<a moz-do-not-send="true" class="moz-txt-link-abbreviated" href="mailto:TRNSYS-users@cae.wisc.edu" target="_blank">TRNSYS-users@cae.wisc.edu</a>
<a moz-do-not-send="true" class="moz-txt-link-freetext" href="https://mailman.cae.wisc.edu/listinfo/trnsys-users" target="_blank">https://mailman.cae.wisc.edu/listinfo/trnsys-users</a>
</pre>
</blockquote>
<br>
<pre class="moz-signature" cols="72">--
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI 53703 USA
P:+1.608.274.2577
F:+1.608.278.1475
<a moz-do-not-send="true" class="moz-txt-link-abbreviated" href="mailto:d.bradley@tess-inc.com" target="_blank">d.bradley@tess-inc.com</a>
<a moz-do-not-send="true" class="moz-txt-link-freetext" href="http://www.tess-inc.com/" target="_blank">http://www.tess-inc.com/</a>
<a moz-do-not-send="true" class="moz-txt-link-freetext" href="http://www.trnsys.com/" target="_blank">http://www.trnsys.com/</a></pre>
</div>
</blockquote>
<br>
<pre class="moz-signature" cols="72">--
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI 53703 USA
P:+1.608.274.2577
F:+1.608.278.1475
<a class="moz-txt-link-abbreviated" href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.tess-inc.com">http://www.tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.trnsys.com">http://www.trnsys.com</a></pre>
</body>
</html>