    Eva,<br>
      It isn't entirely clear what you have to change. However, Type56
    thinks that it should be expecting 23 inputs but it is receiving 27.
    There is a discrepancy between your *.b17 file and your Studio
    project that needs to be resolved. I would start by opening TRNBuild
    and making sure that the list of inputs (in the project window) is
    correct. Then save the *.b17 project and exit to the Studio. Right
    click on the Type56 icon and tell it to "update building variable
    list." Last, make any required connection corrections.<br>
    Best,<br>
     David<br>
     <br>
    <br>
    On 5/10/2012 12:03, Eva gklezakou wrote:
    <blockquote
cite="mid:CA+Ci=p9PFRJE8sGMUyNC8ffcLQO3snan28ZGwU9hmh-HBK9fTQ@mail.gmail.com"
      type="cite">
      <div>Dear Sirs,</div>
      <div><br>
      </div>
      <div>when I run my simulation the below message is appeared, what
        do I have to change in order to get results?</div>
      <div>*** Fatal Error at time   :      5000.000000</div>
      <div>    Generated by Unit     :    12</div>
      <div>    Generated by Type     :    56</div>
      <div>    TRNSYS Message    103 : The TRNSYS TYPE checking routine
        has found an inconsistency in the specified component between
        the input file and the information expected by the Type</div>
      <div>    Reported information  : An illegal number of INPUTS has
        been specified for this component. Please check the component
        configuration. 23 INPUTS are required and 27 were specified.</div>
      <div><br>
      </div>
      <div>Thank you.</div>
      <div><br>
      </div>
      <div>Regards,</div>
      <div>Eva</div>
      <div><br>
      </div>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <br>
      <pre wrap="">_______________________________________________
TRNSYS-users mailing list
<a class="moz-txt-link-abbreviated" href="mailto:TRNSYS-users@cae.wisc.edu">TRNSYS-users@cae.wisc.edu</a>
<a class="moz-txt-link-freetext" href="https://mailman.cae.wisc.edu/listinfo/trnsys-users">https://mailman.cae.wisc.edu/listinfo/trnsys-users</a>
</pre>
    </blockquote>
    <br>
    <pre class="moz-signature" cols="72">-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI  53703 USA
P:+1.608.274.2577
F:+1.608.278.1475
<a class="moz-txt-link-abbreviated" href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.tess-inc.com">http://www.tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.trnsys.com">http://www.trnsys.com</a></pre>
  </body>
</html>