Santeri,<br>
I am not sure whether anyone responded to your post. However,
there is a component in the TESS Loads and Structures library that
does exactly this. You have to save the Excel file as text (comma or
tab delimited) and read it into your simulation using Type9. You
then take these loads and pass them to Type682. <br>
<br>
If you do not have access to the component in question, you can
always read the load in using Type9, then use an equation (Tout =
Tin + q/m_dot/Cp) to get the return water temperature. You have to
be a little careful using this equation because there is some inlet
temperature above which you cannot realistically provide cooling.
For example, if Tin is 30C and you are trying to maintain your space
at 20C, there isn't any way you can provide cooling to the space.
Type682 (for Trnsys17) provides that checking automatically.<br>
Best,<br>
David<br>
<br>
<br>
On 4/26/2012 04:31, Santeri Siren wrote:
<blockquote
cite="mid:CAF-s-bLD5VSaK6ZJygw5UgkbF7NrHFuTLQL+2osx5Hb8PsL4fw@mail.gmail.com"
type="cite">Dear all,<br>
<br>
I need to simulate cooling power that chances over time and
affects a water flow. I have the cooling powers that I need to use
in an excel file. So I need a component that reads the powers from
excel as an input and deliveres them to the water flow. The inlet
temperature of the water flow also changes over time. Is there any
simple way to do this?<br>
<br>
It seems that the basic auxiliary cooler cant be used in this case
because it has a rated power that can not be read as a changing
input.<br>
<br>
Best regards. Santeri Siren<br>
<br>
<fieldset class="mimeAttachmentHeader"></fieldset>
<br>
<pre wrap="">_______________________________________________
TRNSYS-users mailing list
<a class="moz-txt-link-abbreviated" href="mailto:TRNSYS-users@cae.wisc.edu">TRNSYS-users@cae.wisc.edu</a>
<a class="moz-txt-link-freetext" href="https://mailman.cae.wisc.edu/listinfo/trnsys-users">https://mailman.cae.wisc.edu/listinfo/trnsys-users</a>
</pre>
</blockquote>
<br>
<pre class="moz-signature" cols="72">--
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI 53703 USA
P:+1.608.274.2577
F:+1.608.278.1475
<a class="moz-txt-link-abbreviated" href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.tess-inc.com">http://www.tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.trnsys.com">http://www.trnsys.com</a></pre>
</body>
</html>