Thibaut,<br>
You are correct; the assumption that underlies the lumped
capacitance approach is that the entire building (envelope and air)
is at a single temperature. Moving the setpoint requires the HVAC
system to move the temperature of the air and the structure. I have
seen three workarounds to this issue. <br>
<br>
One is to simply limit the heating and cooling capacity of the
system so that the air and structure warm up at a realisitc rate.
You need to use the "temperature level control" version of Type660
and you need to find the peak iteratively instead of letting the
model calculate it for you. <br>
<br>
The second is to model the building as two lumped capacitances,
one for the air and the other for the shell (Type953 is available in
the TESS Loads and Structures library). Unfortunately, this gets
farther away from allowing you to set any "physical" values; for
instance it is hard to know how to appropriately couple the two
capacitances. <br>
<br>
The third is to artificially reduce the capacitance of the
building so that most of what you are accounting for is the air
(with a little bit for the structure and furnishings).<br>
Best,<br>
David<br>
<br>
<br>
On 3/29/2012 09:29, Thibaut VITTE wrote:
<blockquote cite="mid:4F7471BA.7080401@h3c-energies.fr" type="cite">Dear
Trnsys users,
<br>
<br>
I'm using type 660 to modelize "quickly" a simple building. Having
troubles to analyse the results, I've tested it and compared it
with regular type 56.
<br>
<br>
the building is an office building with high internal loads, large
glazed surfaces.
<br>
the heated area is 9200m², with an overall loss coefficient of 0.7
W/m²°C, 69 kJ/K.m3.
<br>
<br>
The annual results seem quite good, since I'm finding diffrences
in annual heating/cooling loads less than 10%.
<br>
<br>
As far as temperatures and free floating building functionning
(see picture attached), it's not that good, but I understand that
a simple capacitance model is limited for that purpose.
<br>
<br>
But the problem is for maximum heating/cooling power. I have
inputed night set back for cooling and heating. And I think that
the whole building capacitance is taken into account when a moving
setpoint is applied! Which implies great instantaneous power. ( 6
times greater than the one calculated by type 56.) (see picture).
The wole building (air + walls) is heated or cooled when a
setpoint changes (as I understand the model), which is not quite
the reality..
<br>
<br>
Am I right? Is there a simple model that can calculate
approximately the instantaneous power with moving setpoint (in
Trnsys type 12, setpoints are only parameters)?
<br>
<br>
Thanks in advance.
<br>
<br>
Thibaut
<br>
<br>
<fieldset class="mimeAttachmentHeader"></fieldset>
<br>
<pre wrap="">_______________________________________________
TRNSYS-users mailing list
<a class="moz-txt-link-abbreviated" href="mailto:TRNSYS-users@cae.wisc.edu">TRNSYS-users@cae.wisc.edu</a>
<a class="moz-txt-link-freetext" href="https://mailman.cae.wisc.edu/listinfo/trnsys-users">https://mailman.cae.wisc.edu/listinfo/trnsys-users</a>
</pre>
</blockquote>
<br>
<pre class="moz-signature" cols="72">--
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI 53703 USA
P:+1.608.274.2577