<html><body bgcolor="#FFFFFF"><div>There is a restriction in the thickness of the construction layer containing the active cooling. Try making it 200 mm.<br><br>Sent from my iPhone</div><div><br>On 30.03.2012, at 12:18, "Jan Schneider [BBS INTERNATIONAL]" <<a href="mailto:j.schneider@bbs-international.com">j.schneider@bbs-international.com</a>> wrote:<br><br></div><div></div><blockquote type="cite"><div>

<div class="Section1">

<p class="MsoNormal"><font size="3" color="blue" face="Arial Narrow"><span lang="EN-GB" style="font-size:12.0pt;font-family:"Arial Narrow";color:blue">Hi
Sarah,<o:p></o:p></span></font></p>

<p class="MsoNormal"><font size="3" color="blue" face="Arial Narrow"><span lang="EN-GB" style="font-size:12.0pt;font-family:"Arial Narrow";color:blue">if
the active layer option in the layer type manager is enabled, you have to use
the wall type manager to define active layer.<o:p></o:p></span></font></p>

<p class="MsoNormal"><font size="3" color="blue" face="Arial Narrow"><span lang="EN-GB" style="font-size:12.0pt;font-family:"Arial Narrow";color:blue">Select
the correct wall type and chose “new” in the list of available
layers.<o:p></o:p></span></font></p>

<p class="MsoNormal"><font size="3" color="blue" face="Arial Narrow"><span lang="EN-GB" style="font-size:12.0pt;font-family:"Arial Narrow";color:blue">See
chapter 4 in <a href="http://www.bbs-international.com/webfm_send/446"><a href="http://www.bbs-international.com/webfm_send/446">http://www.bbs-international.com/webfm_send/446</a></a><o:p></o:p></span></font></p>

<p class="MsoNormal"><font size="3" color="blue" face="Arial Narrow"><span lang="EN-GB" style="font-size:12.0pt;font-family:"Arial Narrow";color:blue"><o:p> </o:p></span></font></p>

<div>

<div>

<p class="MsoNormal"><font size="3" color="blue" face="Arial Narrow"><span lang="EN-GB" style="font-size:12.0pt;font-family:"Arial Narrow";color:blue">Best
regards</span></font><font color="blue"><span lang="EN-GB" style="color:blue"><o:p></o:p></span></font></p>

<p class="MsoNormal"><font size="3" color="blue" face="Arial Narrow"><span lang="EN-GB" style="font-size:12.0pt;font-family:"Arial Narrow";color:blue">Jan
Schneider<o:p></o:p></span></font></p>

<p class="MsoNormal"><!--[if gte vml 1]><v:line id="_x0000_s1029" style='position:absolute;
 flip:y;z-index:2' from="-1.5pt,8.3pt" to="215.25pt,8.3pt" /><![endif]--><span style="mso-ignore:vglayout;position:relative;z-index:2;left:-3px;top:10px;
width:291px;height:12px"><image001.gif></span><font color="blue" face="Arial Narrow"><span lang="EN-GB" style="font-family:"Arial Narrow";
color:blue"><o:p> </o:p></span></font></p>

<br style="mso-ignore:vglayout" clear="ALL">

<p class="MsoNormal"><!--[if gte vml 1]><v:shapetype id="_x0000_t75" coordsize="21600,21600" 
 o:spt="75" o:preferrelative="t" path="m@4@5l@4@11@9@11@9@5xe" filled="f" 
 stroked="f">
 <v:stroke joinstyle="miter" />
 <v:formulas>
  <v:f eqn="if lineDrawn pixelLineWidth 0" />
  <v:f eqn="sum @0 1 0" />
  <v:f eqn="sum 0 0 @1" />
  <v:f eqn="prod @2 1 2" />
  <v:f eqn="prod @3 21600 pixelWidth" />
  <v:f eqn="prod @3 21600 pixelHeight" />
  <v:f eqn="sum @0 0 1" />
  <v:f eqn="prod @6 1 2" />
  <v:f eqn="prod @7 21600 pixelWidth" />
  <v:f eqn="sum @8 21600 0" />
  <v:f eqn="prod @7 21600 pixelHeight" />
  <v:f eqn="sum @10 21600 0" />
 </v:formulas>
 <v:path o:extrusionok="f" gradientshapeok="t" o:connecttype="rect" />
 <o:lock v:ext="edit" aspectratio="t" />
</v:shapetype><v:shape id="_x0000_s1028" type="#_x0000_t75" 
 href="http://www.bbs-international.com/" style='position:absolute;
 margin-left:170.25pt;margin-top:3.75pt;width:42.5pt;height:42.5pt;z-index:1;
 mso-position-vertical-relative:line' o:button="t">
 <v:fill o:detectmouseclick="t" />
 <v:imagedata src="cid:image002.jpg@01CD0E6F.03BC8E60" o:title="image004" />
</v:shape><![endif]--><span style="mso-ignore:vglayout;position:
absolute;z-index:1;margin-left:227px;margin-top:5px;width:57px;height:57px"><a href="http://www.bbs-international.com/"><image003.jpg></a></span><font color="gray" face="Arial Narrow"><span lang="EN-GB" style="font-family:"Arial Narrow";
color:gray">BBS INTERNATIONAL - GERMANY</span></font><font color="blue"><span lang="EN-GB" style="color:blue"><o:p></o:p></span></font></p>

<p class="MsoNormal"><font size="2" color="gray" face="Arial Narrow"><span style="font-size:10.5pt;font-family:"Arial Narrow";color:gray">Am Forst 27</span></font><font size="2" color="gray"><span style="font-size:10.5pt;color:gray"><o:p></o:p></span></font></p>

<p class="MsoNormal"><font size="2" color="gray" face="Arial Narrow"><span style="font-size:10.5pt;font-family:"Arial Narrow";color:gray">38302
Wolfenbüttel</span></font><font size="2" color="gray"><span style="font-size:10.5pt;
color:gray"><o:p></o:p></span></font></p>

<p class="MsoNormal"><font size="2" color="gray" face="Times New Roman"><span style="font-size:10.5pt;color:gray"> <o:p></o:p></span></font></p>

<p class="MsoNormal"><font size="2" color="gray" face="Arial Narrow"><span style="font-size:10.5pt;font-family:"Arial Narrow";color:gray">Phone:    +49
(0) 5331 – 97 17 25<o:p></o:p></span></font></p>

<p class="MsoNormal"><font size="2" color="gray" face="Arial Narrow"><span style="font-size:10.5pt;font-family:"Arial Narrow";color:gray">Fax:        +49
(0) 5331 – 97 17 17<o:p></o:p></span></font></p>

<p class="MsoNormal"><font size="2" color="gray" face="Arial Narrow"><span lang="EN-GB" style="font-size:10.5pt;font-family:"Arial Narrow";color:gray"><o:p> </o:p></span></font></p>

<p class="MsoNormal"><font size="3" color="gray" face="Arial Narrow"><span lang="EN-GB" style="font-size:12.0pt;font-family:"Arial Narrow";color:gray">BBS
INTERNATIONAL - CHINA</span></font><font color="blue"><span lang="EN-GB" style="color:blue"><o:p></o:p></span></font></p>

<p class="MsoNormal"><font size="2" color="gray" face="Arial Narrow"><span lang="EN-GB" style="font-size:10.5pt;font-family:"Arial Narrow";color:gray">Pavillion
of Innovations<o:p></o:p></span></font></p>

<p class="MsoNormal"><font size="2" color="gray" face="Arial Narrow"><span lang="EN-GB" style="font-size:10.5pt;font-family:"Arial Narrow";color:gray">German
Centre Shanghai</span></font><font size="2" color="gray"><span lang="EN-GB" style="font-size:10.5pt;color:gray"><o:p></o:p></span></font></p>

<p class="MsoNormal"><font size="2" color="gray" face="Arial Narrow"><span lang="EN-GB" style="font-size:10.5pt;font-family:"Arial Narrow";color:gray">88
Keyuan Road<o:p></o:p></span></font></p>

<p class="MsoNormal"><font size="2" color="gray" face="Arial Narrow"><span lang="EN-GB" style="font-size:10.5pt;font-family:"Arial Narrow";color:gray">201203
Shanghai</span></font><font size="2" color="gray"><span lang="EN-GB" style="font-size:10.5pt;color:gray"><o:p></o:p></span></font></p>

<p class="MsoNormal"><font size="2" color="gray" face="Times New Roman"><span lang="EN-GB" style="font-size:10.5pt;color:gray"> <o:p></o:p></span></font></p>

<p class="MsoNormal"><font size="2" color="gray" face="Arial Narrow"><span lang="EN-GB" style="font-size:10.5pt;font-family:"Arial Narrow";color:gray">Phone:    +86
21 – 2898 6466<o:p></o:p></span></font></p>

<p class="MsoNormal"><font size="2" color="gray" face="Arial Narrow"><span lang="EN-GB" style="font-size:10.5pt;font-family:"Arial Narrow";color:gray"><o:p> </o:p></span></font></p>

<p class="MsoNormal"><font size="2" color="gray" face="Arial Narrow"><span lang="EN-GB" style="font-size:10.5pt;font-family:"Arial Narrow";color:gray">E-Mail:
   </span></font><font size="2" color="gray" face="Arial Narrow"><span style="font-size:10.5pt;font-family:"Arial Narrow";color:gray"><a href="mailto:j.schneider@bbs-international.com"><span lang="EN-GB">j.schneider@bbs-international.com</span></a></span></font><font color="blue"><span lang="EN-GB" style="color:blue"><o:p></o:p></span></font></p>

<p class="MsoNormal"><font size="2" color="gray" face="Arial Narrow"><span style="font-size:10.5pt;font-family:"Arial Narrow";color:gray">Web:       <a href="http://www.bbs-international.com"><a href="http://www.bbs-international.com">www.bbs-international.com</a></a></span></font><o:p></o:p></p>

</div>

</div>

<div>

<div class="MsoNormal" align="center" style="text-align:center"><font size="3" face="Times New Roman"><span style="font-size:12.0pt">

<hr size="2" width="100%" align="center" tabindex="-1">

</span></font></div>

<p class="MsoNormal"><b><font size="2" face="Tahoma"><span style="font-size:10.0pt;
font-family:Tahoma;font-weight:bold">Von:</span></font></b><font size="2" face="Tahoma"><span style="font-size:10.0pt;font-family:Tahoma">
<a href="mailto:trnsys-users-bounces@cae.wisc.edu">trnsys-users-bounces@cae.wisc.edu</a> [mailto:trnsys-users-bounces@cae.wisc.edu] <b><span style="font-weight:bold">Im Auftrag von </span></b>Sarah Settler<br>
<b><span style="font-weight:bold">Gesendet:</span></b> Donnerstag, 29. März
2012 14:31<br>
<b><span style="font-weight:bold">An:</span></b> <a href="mailto:trnsys-users@cae.wisc.edu"><a href="mailto:trnsys-users@cae.wisc.edu">trnsys-users@cae.wisc.edu</a></a><br>
<b><span style="font-weight:bold">Betreff:</span></b> [TRNSYS-users] define
active layer</span></font><o:p></o:p></p>

</div>

<p class="MsoNormal"><font size="3" face="Times New Roman"><span style="font-size:
12.0pt"><o:p> </o:p></span></font></p>

<p class="MsoNormal"><font size="2" color="#1f497d" face="Consolas"><span style="font-size:11.0pt;font-family:Consolas;color:#1F497D">Hi all,<o:p></o:p></span></font></p>

<p class="MsoNormal"><font size="2" color="#1f497d" face="Consolas"><span style="font-size:11.0pt;font-family:Consolas;color:#1F497D"><o:p> </o:p></span></font></p>

<p class="MsoNormal"><font size="2" color="#1f497d" face="Consolas"><span lang="EN-US" style="font-size:11.0pt;font-family:Consolas;color:#1F497D">I want to define an
active layer, but the radio button in the layer type manager stays grayed out.
(see attached screenshot)<o:p></o:p></span></font></p>

<p class="MsoNormal"><font size="2" color="#1f497d" face="Consolas"><span lang="EN-US" style="font-size:11.0pt;font-family:Consolas;color:#1F497D"><o:p> </o:p></span></font></p>

<p class="MsoNormal"><font size="2" color="#1f497d" face="Consolas"><span lang="EN-US" style="font-size:11.0pt;font-family:Consolas;color:#1F497D">I can not find an
answer in the multizone building manual, as clicking the radio button seems to
be super-simple.<o:p></o:p></span></font></p>

<p class="MsoNormal"><font size="2" color="#1f497d" face="Consolas"><span lang="EN-US" style="font-size:11.0pt;font-family:Consolas;color:#1F497D"><o:p> </o:p></span></font></p>

<p class="MsoNormal"><font size="2" color="#1f497d" face="Consolas"><span lang="EN-US" style="font-size:11.0pt;font-family:Consolas;color:#1F497D">Thanks in advance,<o:p></o:p></span></font></p>

<p class="MsoNormal"><font size="2" color="#1f497d" face="Consolas"><span lang="EN-US" style="font-size:11.0pt;font-family:Consolas;color:#1F497D"><o:p> </o:p></span></font></p>

<p class="MsoNormal"><font size="2" color="#1f497d" face="Consolas"><span lang="EN-US" style="font-size:11.0pt;font-family:Consolas;color:#1F497D">Sarah<o:p></o:p></span></font></p>

<p class="MsoNormal"><font size="2" color="#1f497d" face="Consolas"><span lang="EN-US" style="font-size:11.0pt;font-family:Consolas;color:#1F497D"><o:p> </o:p></span></font></p>

<p class="MsoNormal"><font size="2" color="#1f497d" face="Consolas"><span lang="EN-US" style="font-size:11.0pt;font-family:Consolas;color:#1F497D"><o:p> </o:p></span></font></p>

<p class="MsoNormal"><font size="2" color="#1f497d" face="Consolas"><span lang="EN-US" style="font-size:11.0pt;font-family:Consolas;color:#1F497D"><o:p> </o:p></span></font></p>

<p class="MsoNormal"><font size="2" color="#1f497d" face="Consolas"><span style="font-size:11.0pt;font-family:Consolas;color:#1F497D">Für Rückfragen
stehe ich Ihnen gerne zur Verfügung.<o:p></o:p></span></font></p>

<p class="MsoNormal"><font size="2" color="#1f497d" face="Consolas"><span style="font-size:11.0pt;font-family:Consolas;color:#1F497D"><o:p> </o:p></span></font></p>

<p class="MsoNormal"><font size="2" color="#1f497d" face="Consolas"><span style="font-size:11.0pt;font-family:Consolas;color:#1F497D">Mit freundlichem
Gruß<o:p></o:p></span></font></p>

<p class="MsoNormal"><font size="2" color="#1f497d" face="Consolas"><span style="font-size:11.0pt;font-family:Consolas;color:#1F497D">Sarah Settler<o:p></o:p></span></font></p>

<p class="MsoNormal"><font size="2" color="#1f497d" face="Consolas"><span style="font-size:11.0pt;font-family:Consolas;color:#1F497D"><o:p> </o:p></span></font></p>

<p class="MsoNormal"><font size="2" color="#1f497d" face="Consolas"><span style="font-size:11.0pt;font-family:Consolas;color:#1F497D">Ökoplan <o:p></o:p></span></font></p>

<p class="MsoNormal"><font size="2" color="#1f497d" face="Consolas"><span style="font-size:11.0pt;font-family:Consolas;color:#1F497D">Büro für zeitgemäße
Energieanwendung <o:p></o:p></span></font></p>

<p class="MsoNormal"><font size="2" color="#1f497d" face="Consolas"><span style="font-size:11.0pt;font-family:Consolas;color:#1F497D">Hummelsbütteler Weg
36 <o:p></o:p></span></font></p>

<p class="MsoNormal"><font size="2" color="#1f497d" face="Consolas"><span style="font-size:11.0pt;font-family:Consolas;color:#1F497D">22339 Hamburg<o:p></o:p></span></font></p>

<p class="MsoNormal"><font size="2" color="#1f497d" face="Consolas"><span style="font-size:11.0pt;font-family:Consolas;color:#1F497D"> <o:p></o:p></span></font></p>

<p class="MsoNormal"><font size="2" color="#1f497d" face="Consolas"><span style="font-size:11.0pt;font-family:Consolas;color:#1F497D">T 040 5394143<o:p></o:p></span></font></p>

</div>




</div></blockquote><blockquote type="cite"><div><span>_______________________________________________</span><br><span>TRNSYS-users mailing list</span><br><span><a href="mailto:TRNSYS-users@cae.wisc.edu">TRNSYS-users@cae.wisc.edu</a></span><br><span><a href="https://mailman.cae.wisc.edu/listinfo/trnsys-users">https://mailman.cae.wisc.edu/listinfo/trnsys-users</a></span><br></div></blockquote></body></html>