Mayank,<br>
It is very hard to get matching results between two people using
the same software package, let alone between two different packages;
there are so many assumptions in modeling. Still, what you report is
a quite significant difference in sensitivity. I think the first
place to look is that in your *.bui, you have left the default
thermal capacitance of the zone as <br>
<br>
VOLUME= 3027.33 m3<br>
CAPACITANCE = 3632.79 kJ/K <br>
<br>
this accounts only for the thermal capacitance of the air in the
zone. It neglects the thermal capacitance of the furnishings. A more
typical value would be 18200 kJ/h (approximately 5 times the default
value).<br>
<br>
Kind regards,<br>
David<br>
<br>
On 2/14/2012 01:11, Mayank wrote:
<blockquote cite="mid:4f3a0949.2139440a.48e8.5034@mx.google.com"
type="cite">
<meta http-equiv="Content-Type" content="text/html;
charset=ISO-8859-1">
<meta name="Generator" content="Microsoft Word 12 (filtered
medium)">
<style>
<!--
/* Font Definitions */
@font-face
{font-family:Calibri;
panose-1:2 15 5 2 2 2 4 3 2 4;}
/* Style Definitions */
p.MsoNormal, li.MsoNormal, div.MsoNormal
{margin:0in;
margin-bottom:.0001pt;
font-size:11.0pt;
font-family:"Calibri","sans-serif";}
a:link, span.MsoHyperlink
{mso-style-priority:99;
color:blue;
text-decoration:underline;}
a:visited, span.MsoHyperlinkFollowed
{mso-style-priority:99;
color:purple;
text-decoration:underline;}
span.EmailStyle17
{mso-style-type:personal-compose;
font-family:"Calibri","sans-serif";
color:windowtext;}
.MsoChpDefault
{mso-style-type:export-only;}
@page Section1
{size:8.5in 11.0in;
margin:1.0in 1.0in 1.0in 1.0in;}
div.Section1
{page:Section1;}
-->
</style><!--[if gte mso 9]><xml>
<o:shapedefaults v:ext="edit" spidmax="1026" />
</xml><![endif]--><!--[if gte mso 9]><xml>
<o:shapelayout v:ext="edit">
<o:idmap v:ext="edit" data="1" />
</o:shapelayout></xml><![endif]-->
<div class="Section1">
<p class="MsoNormal">Hello Everyone,<o:p></o:p></p>
<p class="MsoNormal"><o:p> </o:p></p>
<p class="MsoNormal">I have made a simple cooling load
calculation model in
TRNSYS v16 and similar setup in E-quest. There is vast
variation in cooling
load when I put into outdoor air in the room.<o:p></o:p></p>
<p class="MsoNormal">In TRNSYS I used 2800 sqft area building
having 150 person
occupancy and according to ASHRAE 62 (ventilation rate
procedure) I calculated
1150 CFM outdoor air as fresh air. When I taking no outdoor
air the cooling
load is about 10 ton but when I put outdoor air through
ventilation (2.46 ACH)
the cooling load increases and reached at 42 ton.<o:p></o:p></p>
<p class="MsoNormal"><o:p> </o:p></p>
<p class="MsoNormal">And in E-quest it increase only 1 ton.<o:p></o:p></p>
<p class="MsoNormal"> Can anyone help me to find out the reason?
<o:p></o:p></p>
<p class="MsoNormal">I attached bui. File and tpf file.<o:p></o:p></p>
<p class="MsoNormal"><o:p> </o:p></p>
<p class="MsoNormal">Regards <o:p></o:p></p>
<p class="MsoNormal"><o:p> </o:p></p>
<p class="MsoNormal">Mayank <o:p></o:p></p>
</div>
<br>
<fieldset class="mimeAttachmentHeader"></fieldset>
<br>
<pre wrap="">_______________________________________________
TRNSYS-users mailing list
<a class="moz-txt-link-abbreviated" href="mailto:TRNSYS-users@cae.wisc.edu">TRNSYS-users@cae.wisc.edu</a>
<a class="moz-txt-link-freetext" href="https://mailman.cae.wisc.edu/listinfo/trnsys-users">https://mailman.cae.wisc.edu/listinfo/trnsys-users</a>
</pre>
</blockquote>
<br>
<pre class="moz-signature" cols="72">--
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI 53703 USA
P:+1.608.274.2577
F:+1.608.278.1475
<a class="moz-txt-link-abbreviated" href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.tess-inc.com">http://www.tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.trnsys.com">http://www.trnsys.com</a></pre>