<html>
  <head>
    <meta content="text/html; charset=ISO-8859-1"
      http-equiv="Content-Type">
  </head>
  <body bgcolor="#FFFFFF" text="#000000">
    Cathy,<br>
    <br>
    <blockquote
      cite="mid:1326127081.86010.YahooMailClassic@web15807.mail.cnb.yahoo.com"
      type="cite">
      <table border="0" cellpadding="0" cellspacing="0">
        <tbody>
          <tr>
            <td style="font: inherit;" valign="top">
              <div>1. I use the weather data(*.epw) downloaded from the
                webe of Energyplus as the external files of Type15-2.
                When running simulation of the project, there is no
                warning or error. But all the weather data are not read
                out and shown as zero.</div>
            </td>
          </tr>
        </tbody>
      </table>
    </blockquote>
    At one point, the energyplus weather file format changed and so we
    had to change TRNSYS to correspond. Please send me the *.epw file
    that you are trying to read (as well as which version of TRNSYS you
    are running) and I'll take a look at it.<br>
    <blockquote
      cite="mid:1326127081.86010.YahooMailClassic@web15807.mail.cnb.yahoo.com"
      type="cite">
      <table border="0" cellpadding="0" cellspacing="0">
        <tbody>
          <tr>
            <td style="font: inherit;" valign="top">
              <div> 2. In the water circulation, the flow rates of
                Single speed pump( Type114) can be varied when the
                values of the inlet fluid flow rates are different. What
                are the differences between  the Sigle speed
                pump(Type114) and Variable speed pump(Type110)?</div>
            </td>
          </tr>
        </tbody>
      </table>
    </blockquote>
    In TRNSYS almost all of the pump models set the downstream flow
    based on the value of the rated flow rate (a parameter) and the
    control signal (an input). They ignore the amount of flow that is
    coming into the pump from upstream except to do a mass-balance
    check. Type114 is designed to have a control signal of either 0
    (off) or 1 (on). In fact if you give it a control signal of <
    0.5, this is interpreted as 0 (off). If you give it a control signal
    > or = 0.5, this is interpreted as 1 (on). The flowrate out of
    Type114 will always be either zero or the rated flow rate.<br>
    <br>
    With Type110, the rated flow rate (parameter) is multiplied by the
    value of the control signal input (which typically varies between 0
    and 1) to give the outlet flow rate. You have to be a bit careful
    with Type110 because it does not limit the input control signal to a
    maximum value of 1.0. If you specify a control signal of 10, your
    output flow rate will be 10 times the pump's rated flow rate. We do
    not limit the control signal input to a maximum value of 1 because
    there are cases in which pump are intentionally run above their
    rated flow rate.<br>
    <br>
    Kind regards,<br>
     David<br>
    <br>
    <blockquote
      cite="mid:1326127081.86010.YahooMailClassic@web15807.mail.cnb.yahoo.com"
      type="cite">
    </blockquote>
    <pre class="moz-signature" cols="72">-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI  53703 USA

P:+1.608.274.2577
F:+1.608.278.1475
<a class="moz-txt-link-abbreviated" href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>

<a class="moz-txt-link-freetext" href="http://www.tess-inc.com">http://www.tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.trnsys.com">http://www.trnsys.com</a></pre>
  </body>
</html>