    Dear Cathy <br>
    <br>
    On 12/28/2011 06:41, sun liang wrote:
    <blockquote
      cite="mid:1325076064.12618.YahooMailClassic@web15804.mail.cnb.yahoo.com"
      type="cite">
      <table border="0" cellpadding="0" cellspacing="0">
        <tbody>
          <tr>
            <td style="font: inherit;" valign="top"><br>
              1. I know that when I use the Ventilation to delivery the
              cold and hot air into the controlled zone, the Cooling and
              Heating must be turn off. The temperature of the
              controlled zone is used to adjust the temperature and flow
              rate of the ventilating air. But I also want to obtain the
              cooling load or heating load on this occasion. How can I
              reach my aim?<br>
            </td>
          </tr>
        </tbody>
      </table>
    </blockquote>
    Type56's automatic HEATING and COOLING Types calculate the sensible
    energy required to maintain a predefined set point temperature (also
    called the sensible load). When you change to a controller that is
    trying to maintain the zone temperature by varying the temperature
    and flow of supply air, the "load" is no longer defined; in order to
    define the load, you need to <i>predefine </i>the actual room
    temperature (note that the actual room temperature and the room
    setpoint temperature are not the same thing!). Instead, the concept
    of "load" is replaced by the actual energy that is being adding to
    or removed from the zone. How to see this quantity depends a bit on
    what Types are in your system. If you are heating using a furnace,
    you would look at the output of the furnace that tells how much
    energy it added to the air stream. If you are using heat pumps, you
    would look at the heat pump output that shows how much energy was
    added to the airstream. You could also use a pair of Type33s
    (psychrometrics) to compute the enthalpy of the supply (h_in) and
    return air (h_out), then compute q=mdot*(h_out-h_in).<br>
    <blockquote
      cite="mid:1325076064.12618.YahooMailClassic@web15804.mail.cnb.yahoo.com"
      type="cite">
      <table border="0" cellpadding="0" cellspacing="0">
        <tbody>
          <tr>
            <td style="font: inherit;" valign="top">2. When using
              TRNBuild to design the controlled zone, I am confused by
              defining control strategy and scale in designing the
              Artificial Lighting.<br>
            </td>
          </tr>
        </tbody>
      </table>
    </blockquote>
    The "control strategy" and "scale" fields in the Artificial Lighting
    gain window allow you to adjust the heat gains from lighting that
    the space experiences. Both are typically a value between 0 and 1
    and they act as a multiplier on the base value that you specified
    using the "total heat gain" and "related floor area" fields. As with
    many things in TRNBuild/Type56, you have the option of selecting a
    constant value, scheduling a value, or telling Type56 that the value
    will come from some other Type (or equation) as an INPUT.  <br>
    <br>
    <blockquote
      cite="mid:1325076064.12618.YahooMailClassic@web15804.mail.cnb.yahoo.com"
      type="cite">
      <table border="0" cellpadding="0" cellspacing="0">
        <tbody>
          <tr>
            <td style="font: inherit;" valign="top">3. The TRNSYS
              software I used is Version 16 and was bought from the
              agency of China Mainland. The agency said that I had to
              pay if I want to upgrade my software to Version 17. I want
              to know how the software is upgraded for free. By the way,
              my software does not have a serial number but a Passdog.<br>
            </td>
          </tr>
        </tbody>
      </table>
    </blockquote>
    The update from TRNSYS 16.x to TRNSYS 17.x is a paid update. Within
    each major version number (16, 17, etc.) there are periodic minor
    version updates (16.1, 16.2, 16.3, etc.) which are free. <br>
    <br>
    Kind regards,<br>
     David<br>
    <br>
    <pre class="moz-signature" cols="72">-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI  53703 USA

P:+1.608.274.2577
F:+1.608.278.1475
<a class="moz-txt-link-abbreviated" href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>

<a class="moz-txt-link-freetext" href="http://www.tess-inc.com">http://www.tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.trnsys.com">http://www.trnsys.com</a></pre>