    Chou,<br>
      In Type56/TRNBuild the term "VENTILATION" just means a flow of air
    whether it is hot, cold, or neutral. It isn't necessarily tied in
    any way to the HVAC system. The "HEATING" and "COOLING" types are
    used to calculate sensible loads for the space. Those types don't
    have anything to do with how that energy is delivered to the space.<br>
    <br>
      Typically, there are two kinds of simulations that I do with
    Type56:<br>
    <br>
    Early on in a project, I need to determine the peak heating and
    cooling loads for the space and I need to get a very basic idea of
    how much energy the building will consume over the year. In order to
    do this, I use VENTILATION types to put the outdoor (fresh) air
    requirements into the zone. and I use HEATING and COOLING types to
    define set points. I allow the "system" to have unlimited power
    because all I really care about is the maximum hourly value and the
    annual sum. The annual sum gives a very rough idea of how much
    energy is required by the building. You have to do one of two things
    in order to get how much energy is required by the HVAC system:
    either define a simple COP for the heating and cooling system or use
    other TRNSYS models that take heating and cooling load as an input
    and return the power consumed (note, there are very few of these
    components)<br>
    <br>
    The second kind of simulation is much more common and gets at one of
    TRNSYS's strengths. In this, you use the VENTILATION type to deliver
    hot or cold air to the space and you use a thermostat model (such as
    Type108) to turn on and off equipment that controls the flow of air.
    In this case, you disable the HEATING and COOLING types because you
    don't care about loads. The equipment of the system (fans, pumps,
    heat pumps, furnaces, chillers, etc.) will compute their source
    energy requirements as a function of their inlet conditions and the
    building will simply react to the ventilation air that it receives.<br>
    <br>
    Kind regards,<br>
     David<br>
     <br>
    <br>
    On 12/18/2011 05:12, Chou Shen wrote:
    <blockquote
cite="mid:CAP9LdPPQjO5aDKmOMmrPeZ8jBemiP+r6_YpCKs5-WNH2dqQgQg@mail.gmail.com"
      type="cite">Hi<br>
      <br>
      Thanks to David and Matt, you messages have helped me a lot. Now I
      know how to use type 24 & 25 to get monthly summary. <br>
      <br>
      At this time I have some other questions:<br>
      1. When Editing type 56, in the Ventilation lable, the Heating and
      Cooling option can be set up by defining airchange rate and
      temperature & RH of air flow; while in both the Cooling lable
      and Heating lable, the cooling and heating option can be set up by
      defining cooling / heating power (does that mean I need to
      estimate the cooling / heating load before set this block up?),
      and the setpoint temperature & RH. As a result, type 56
      provides two methods to define HVAC system. What's the
      relationships between the two methods?. <br>
      <br>
      2. In addition to adding the information of HVAC in type 56, do I
      need to creat the HVAC system in to get the information of energy
      consumption of HVAC system?<br>
      <br>
      Thanks!<br>
      <br clear="all">
      <br>
      -- <br>
      Chou Shen<br>
      Graduate Research Assistant<br>
      Department of Civil, Architectural & Environmental Engineering<br>
      Missouri University of Science and Technology<br>
      <br>
      <br>
      <br>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <br>
      <pre wrap="">_______________________________________________
TRNSYS-users mailing list
<a class="moz-txt-link-abbreviated" href="mailto:TRNSYS-users@cae.wisc.edu">TRNSYS-users@cae.wisc.edu</a>
<a class="moz-txt-link-freetext" href="https://mailman.cae.wisc.edu/listinfo/trnsys-users">https://mailman.cae.wisc.edu/listinfo/trnsys-users</a>
</pre>
    </blockquote>
    <br>
    <pre class="moz-signature" cols="72">-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI  53703 USA
P:+1.608.274.2577
F:+1.608.278.1475
<a class="moz-txt-link-abbreviated" href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.tess-inc.com">http://www.tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.trnsys.com">http://www.trnsys.com</a></pre>
  </body>
</html>